30 vrs. 50 amp hook-up
Saturday, when we picked up our new Laredo 325RL it was plugged into a 30amp receptacle with the normal 50/30 dogbone. The 5er is set up for 50 amp service.
The main TV was on and demonstrated to us. All good. Got home and plugged into a 20amp outlet so we could run the lights and TV, nothing more. No power to the TV receptacle and many other receptacles. To me this is understandable as 30 amp service is single phase and 50 amp service is dual phase and the 2 circuits are separated in the panel. (WF 8930/50). Everything was checked with a plug in circuit tester and everything is wired properly.
I am curious how we had TV at the dealer. What happens when you have to take a 30 amp site? Will call in the morning. Any ideas.
|
|
|
03-06-2017, 04:14 PM
|
#2
|
Senior Member
Join Date: Aug 2014
Location: Lincoln, NE
Posts: 423
|
Puzzling. Did the TV breaker pop? Try resetting it.
|
|
|
03-06-2017, 04:19 PM
|
#3
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 16,181
|
What kind of connection do you have to the 20 amp? A regular 120v/50 amp RV adapter or??
A 50/30 amp adapter splits the AC to both legs of the 50 amp plug so "stuff" works. Sounds like the hookup you have does not do that.
|
|
|
03-06-2017, 04:27 PM
|
#4
|
Senior Member
Join Date: Feb 2017
Location: Dade City
Posts: 1,039
|
Quote:
Originally Posted by sourdough
What kind of connection do you have to the 20 amp? A regular 120v/50 amp RV adapter or??
A 50/30 amp adapter splits the AC to both legs of the 50 amp plug so "stuff" works. Sounds like the hookup you have does not do that.
|
The 50/30 adapter is used and plugged into the 30/20 adapter that plugs into the house receptacle.
Thank You for your knowledge, I will check this out tomorrow.
|
|
|
03-06-2017, 04:29 PM
|
#5
|
Site Team | Emeritus
Join Date: Jan 2014
Location: Western PA
Posts: 2,733
|
X2 .. as stated your need a cable or combination of cables that is going to take your 20 amp source and have it applied to both legs of the 50 amp service into your 50 amp rig. However you have it connected now, you are only feeding one leg of he 50 amp service into your rig. Basically you only feeding half the 110v breakers in you rig.
|
|
|
03-06-2017, 04:52 PM
|
#6
|
Site Team | Emeritus
Join Date: Jan 2014
Location: Western PA
Posts: 2,733
|
Quote:
Originally Posted by Frank G
The 50/30 adapter is used and plugged into the 30/20 adapter that plugs into the house receptacle.
Thank You for your knowledge, I will check this out tomorrow.
|
If you used the same cables used at the dealer, assume they were yours, then unplug the 30 amp cable from there 30 amp receptacle and put the 30 to 20 adapter on that end. Then your 20 amp extension cord goes on there. Done
20 to 30 amp adapter is merely converting a 30 amp plug layout to a 20 amp plug layout, now that 30 to 50 amp doggone is taking the single leg and applying it to both legs of the 50 amp cable going into you 50 amp rig.
So if you did this not sure why it is not working for you. Should be feeding both legs in your rig
|
|
|
03-06-2017, 04:58 PM
|
#7
|
Senior Member
Join Date: Oct 2016
Location: "Murvil, TN
Posts: 2,135
|
Quote:
Originally Posted by Frank G
Saturday, when we picked up our new Laredo 325RL it was plugged into a 30amp receptacle with the normal 50/30 dogbone. The 5er is set up for 50 amp service.
The main TV was on and demonstrated to us. All good. Got home and plugged into a 20amp outlet so we could run the lights and TV, nothing more. No power to the TV receptacle and many other receptacles. To me this is understandable as 30 amp service is single phase and 50 amp service is dual phase and the 2 circuits are separated in the panel. (WF 8930/50). Everything was checked with a plug in circuit tester and everything is wired properly.
I am curious how we had TV at the dealer. What happens when you have to take a 30 amp site? Will call in the morning. Any ideas. 
|
Plug your cord into a different outlet.....and keep trying different outlets until you find one that is on the same side of the line as your TV etc.
__________________
2016 F350 King Ranch Crew Cab Dually Diesel 4x4
2018 Grand Design Momentum 394M
2019 Can Am Spyder RT Limited (Phoenix Orange)
Excessive payload capacity is a wonderful thing
"If it ain't Fast....It ain't Fun"
|
|
|
03-06-2017, 05:32 PM
|
#8
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 16,181
|
It sounds like your setup should work but...... If you have access to a place that sells them just get a 120v/50A adapter and use that. I use a 12 ga. 25' extension cord and plug it into the 50A pigtail that plugs into the trailer and all is well.....unless I try to pull more than 20A
|
|
|
03-06-2017, 05:35 PM
|
#9
|
Site Team
Join Date: Mar 2011
Location: Gaylord
Posts: 25,219
|
Some dealerships use a "service department" power cable (so the customer's new cable stays clean and stowed). If your dealership did this, you could have a faulty power cable. One other possibility (if there's no power to anything in your trailer) is that your home outlet that you're plugging into is wired backwards and you're not getting power to the "hot side" of your trailer electrical breaker box....
__________________
John
2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
|
|
|
03-06-2017, 05:44 PM
|
#10
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 16,181
|
Your going from a 20A (120VAC) to 30A adapter....where is that located? Then you're going from the 30A adapter to a 50A...where is that located? In theory you should be getting 120v from the 120v plug and it runs on one conductor through the 30A adapter then splits to both 120V legs of the 50A plug inside the 30/50 adapter. Take a meter and read what should be the 2 hot legs in the 50A plug. I'm thinking you don't have AC on one of them. Maybe a bad 30/50 adapter? Here is a link that shows where your hot legs should be:
https://www.google.com/search?q=wiri...w2tXNmzX0mBqM:
|
|
|
03-07-2017, 03:29 AM
|
#11
|
Senior Member
Join Date: Nov 2016
Location: Austin
Posts: 296
|
30 amp vs 50 amp
I have 330RL (travel trailer version of your rig). When we brought ours home and plugged in to our 30 amp outlet - Nothing worked in the entertainment slide out. Turned out to be the circuit was tripped on the outlet inside the outdoor kitchen. Reset the button and all is good. Be sure to check that outlet. This has happened a couple of times since. Not sure why it trips.
__________________
'19 Chevy 3500 High Country DRW
'18 Montana 3921FB Aggie ‘77
In the sticks near Austin TX
Aussie Gus+Texas Heeler Jimmy
|
|
|
03-07-2017, 07:10 AM
|
#12
|
Site Team | Emeritus
Join Date: Jan 2014
Location: Western PA
Posts: 2,733
|
The majority of posts have identified the electrical components and how they need to be connected to power a 50 amp rig from a extension cord connecting the rig to a house receptacle. The OP is requested to inform us as to exactly what electrical cables/adapters he is currently using.
|
|
|
03-07-2017, 07:19 AM
|
#13
|
Site Team | Emeritus
Join Date: Jan 2014
Location: Western PA
Posts: 2,733
|
Quote:
Originally Posted by Mikendebbie
I have 330RL (travel trailer version of your rig). When we brought ours home and plugged in to our 30 amp outlet - Nothing worked in the entertainment slide out. Turned out to be the circuit was tripped on the outlet inside the outdoor kitchen. Reset the button and all is good. Be sure to check that outlet. This has happened a couple of times since. Not sure why it trips.
|
That GFI breaker that you are resetting is designed to be sensitive to electrical faults. That GFI also feeds/protects other plugs down stream from it. I would see if you can relate the tripping to other occurrences such as rain (moisture I'm outside plug), that side movement (possible power cable rubbing on frame), use of a faulty device/extension cable, etc
|
|
|
03-07-2017, 07:35 AM
|
#14
|
Senior Member
Join Date: Feb 2017
Location: Dade City
Posts: 1,039
|
Quote:
Originally Posted by PARAPTOR
The majority of posts have identified the electrical components and how they need to be connected to power a 50 amp rig from a extension cord connecting the rig to a house receptacle. The OP is requested to inform us as to exactly what electrical cables/adapters he is currently using.
|
1) The 50amp cable was supplied with the unit and was the same one used at the dealership.
2) The 50/30 Dogbone was the one supplied by the dealer and the one used at the dealership.
3) The 30amp/110V adapter is the standard one sold at every RV dealer
4) The extension cord is a short 12ga
5) The house outlet is 20 amp circuit (new and inspected in 2015) and when a plug in type tester is plugged into it it shows to be properly wired.
6) The end of the 110 volt extension cord, when tested, show to be properly wired
7) The working receptacles in the RV show to be properly wired.
I am at work at the time so it will be later in the afternoon before I can continue the search. I do appreciate everyone's input. I am thinking that there is a tripped GFI receptacle that I am missing or, are they using GFI circuit breakers. none of the breakers appear to be tripped. Every receptacle in the unit has a protected by GFI sticker on them.
Later
|
|
|
03-07-2017, 08:08 AM
|
#15
|
Site Team | Emeritus
Join Date: Jan 2014
Location: Western PA
Posts: 2,733
|
Thanks, sounds like you have the correct components and connected accordingly and other than the 30 to 20 amp adapter the same as tested at the dealer. As a quick check I would check in the power distribution panel to ensure you are getting 110v Ac on both legs.
If yes then all that cabling from house to rig is okay. If not I would start by checking the end of your 50 amp shore power cable (diagram provided in previous post). Based on results I would work my way back to the plug in the hose.
I am not aware of GFI circuit breakers being used in these rigs. Concerns me that you say ALL plugs labeled as GFI protected. I would look for multiple GFI plugs and to ensure there are not tripped. Would test each with trip/reset buttons.
We have had posts identifying loose wires on these GFI devices mainly on the output side (that feeding down stream protected plugs.
Please keep us informed when you have a chance to look at it again
|
|
|
03-07-2017, 08:23 AM
|
#16
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 16,181
|
When you get home do the following: get a multi meter and take the plug that plugs into the trailer. Put the common lead of the meter on the ground leg of the 50A plug and the red lead on one of the hot legs as shown in the diagram (one of the plugs on the sides) and see if you have 120V. Do the same for the other hot lead. If you have 120V on each leg THEN start looking for tripped or blown fuses, GFCI plugs etc. No need to start chasing anything until you know you are actually good at the trailer plug.
If everything worked at the trailer when at the dealer, and now it doesn't at your house, logic says it's something in the way it is hooked up. However, if you have the 120v on both legs the trailer is getting what it needs for all of your "stuff" to work, which then points at the distribution panel, fuse, breaker or GFCI circuit. I've not had to pull or work on a ground fault plug in a trailer but in a house you can have outlets wired past the initial plug that will go "dark" if the original GFCI plug is tripped. Good luck and let us know.
|
|
|
03-07-2017, 08:52 AM
|
#17
|
Site Team | Emeritus
Join Date: Jan 2014
Location: Western PA
Posts: 2,733
|
Quote:
Originally Posted by sourdough
When you get home do the following: get a multi meter and take the plug that plugs into the trailer. Put the common lead of the meter on the ground leg of the 50A plug and the red lead on one of the hot legs as shown in the diagram (one of the plugs on the sides) and see if you have 120V. Do the same for the other hot lead. If you have 120V on each leg THEN start looking for tripped or blown fuses, GFCI plugs etc. No need to start chasing anything until you know you are actually good at the trailer plug.
If everything worked at the trailer when at the dealer, and now it doesn't at your house, logic says it's something in the way it is hooked up. However, if you have the 120v on both legs the trailer is getting what it needs for all of your "stuff" to work, which then points at the distribution panel, fuse, breaker or GFCI circuit. I've not had to pull or work on a ground fault plug in a trailer but in a house you can have outlets wired past the initial plug that will go "dark" if the original GFCI plug is tripped. Good luck and let us know.
|
Daisy chaining RV outlets off a single GFI, usually in located in the bathroom, is common practice. That GFI protects its own plugs as as well those plugs daisy chained down stream of it (connected to the output terminals of that GFI). A fault in any of these plugs will trip the breaker and open power to all of them. As noted in previous posts(search) it was found that the wires on the identified output terminal were loose or disconnected. If I recall some GFI terminations where push in terminals. Also noted were faulty GFI's. A search of these posts will provide methods used to check these GFI devices.
As noted by many ensuring that both legs in the power distribution panel have power is the place to start.
__________________
2013 RAPTOR 300MP w/Rear Patio Deck NO Folding Side Ladder 
2013 Silverado 3500HD LTZ CC LB 4X4 DRW
Duramax 6.6L Turbo Diesel; Allison Trans
Reese 20K; Carlisle Radial Trail RH/HD; TPMS (12 Tires)
Veteran

PSU (GO LIONS)
|
|
|
03-08-2017, 03:51 PM
|
#18
|
Senior Member
Join Date: Feb 2017
Location: Dade City
Posts: 1,039
|
Sorry for the delay. Found the tripped GFI receptacle in the bathroom. Would you believe almost all of the receptacles are daisy chained off of one GFI. (about 8 0r 9) The exception being the Washer/Dryer outlet and the BR TV.
The only other Issue is the lack of a handy outlet for a C-pap machine.
Thanks everyone for your input, a lot was learned.
|
|
|
03-08-2017, 04:04 PM
|
#19
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 16,181
|
Great! I'm glad you found the problem. You might try to think back at the sequence of events to try to figure out what blew it; just as an fyi for yourself. Then again, it could have just tripped being plugged in but you might just think through it.
|
|
|
03-08-2017, 04:21 PM
|
#20
|
Senior Member
Join Date: Feb 2014
Location: radium hot springs bc
Posts: 2,007
|
Having GFCI controlling all other receptacles is not unusual. Had a house in Phoenix built in 2008 it had all of the receptacles ran off of the master bathroom GFCI. This was code at the time. So not surprised that RVs are using this system.