Ok. If you removed the thermostat and the furnaces keeps running you need to locate the wiring at the furnace.
Refer to above, and locate the two thermostat wires. Disconnect one or the other, if the furnace still runs then you probably need a new control board. If the furnace stops, then you probably have a “short” in the thermostat wiring.
You should have 12VDC on 1 of the thermostat wires and the other shouldnt. When you operate the thermostat the “circuit” is completed sending 12V to the furnace control board. When the set temp is reached, that 12V “signal” is broken.