Furnace with air conditioner covered?

I have a Bullet 248RKS. The AC shroud has a cover on it for winter. The system is ducted. I turned on the furnace and it was not getting hot but it was blowing out of the ducts. I went outside and checked the shroud and it was “sucked in.” So, is it not proper to run the furnace with the AC shroud covered???
__________________
Skids
2019 Bullet 248RKS
skids is offline   Reply With Quote
Old 10-11-2019, 10:01 AM   #2
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,741
What style thermostat? If you have a "manual" stat with a fan switch that says "on" or "high" and "low" and "off" that controls the air conditioner fan and should be in the "off" position when you switch from "cool" to "heat".
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 10-11-2019, 11:15 AM   #3
skids
Senior Member
 
skids's Avatar
 
Join Date: Sep 2019
Location: Florissant
Posts: 698
Quote:
Originally Posted by flybouy View Post
What style thermostat? If you have a "manual" stat with a fan switch that says "on" or "high" and "low" and "off" that controls the air conditioner fan and should be in the "off" position when you switch from "cool" to "heat".
It is a green touch screen and it has heat set point (62F) and air conditioning set point (75F) and yes also fan speed was set to High. I will set fan speed to off if it has that setting and try the heat again.
__________________
Skids
2019 Bullet 248RKS
skids is offline   Reply With Quote
Old 10-11-2019, 11:26 AM   #4
nied
Member
 
Join Date: Nov 2016
Location: Dayton
Posts: 68
I have a 248. The AC vents through the ceiling while the furnace vents from floor registers. Only one can operate at a time.
nied is offline   Reply With Quote
Old 10-11-2019, 11:51 AM   #5
skids
Senior Member
 
skids's Avatar
 
Join Date: Sep 2019
Location: Florissant
Posts: 698
Flybouy, you hit the nail on the head. The fan shown on the thermostat needs to be off when running the furnace. Yes Nied, the cold air is through the ceiling vents and the furnace through the lower ones.
__________________
Skids
2019 Bullet 248RKS
skids is offline   Reply With Quote
Old 10-12-2019, 03:30 AM   #6
Schbobby
Member
 
Join Date: Jul 2019
Location: Wareham
Posts: 40
I got the In-Control system in my 2019 Cougar! Turned on heat this morning due to waking up to 40’s outside. Turned to Heat, Gas, Fan off and got Heat, gas fan on! Seems the system will run the fan as the heater is on in mine as well.
Schbobby is offline   Reply With Quote
Old 10-12-2019, 04:14 AM   #7
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,741
That's correct. The '"fan" control only controls the fan on the air conditioner. The camper's heat and air conditioner are 2 separate pieces of equipment. I guess if you have the heat stripin the a/c the fan should be in the "off" position.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 10-20-2019, 10:08 AM   #8
6.2 Superduty
Member
 
Join Date: Jun 2018
Location: ofallon
Posts: 41
Quote:
Originally Posted by skids View Post
Flybouy, you hit the nail on the head. The fan shown on the thermostat needs to be off when running the furnace. Yes Nied, the cold air is through the ceiling vents and the furnace through the lower ones.
I have a 2018 bullet 269rls that has a touch screen thermostat. Every bullet I have seen made after 2018 has the same thermostat. The fan settings are high ,low and auto. To operate furnace it is set to auto. If yours has an fan off setting it is different from everything I have seen
I hope it is a new model to update the troublesome thermostat previously used. Florissant Mo or Co?
6.2 Superduty is offline   Reply With Quote
Old 10-20-2019, 02:58 PM   #9
skids
Senior Member
 
skids's Avatar
 
Join Date: Sep 2019
Location: Florissant
Posts: 698
It is Florissant, Colorado. As I think back, I thought the fan setting was touched repeatedly until nothing showed (off?) but I could be wrong about that. I do know that neither the high or low settings were wanted for winter air movement!
__________________
Skids
2019 Bullet 248RKS
skids is offline   Reply With Quote
Old 10-20-2019, 06:26 PM   #10
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,741
I think it may be "auto" 'high" 'low", point is if it's in "high" or "low" mode it's in a manual, always on state regardless of whether it's set for heat or cool. In auto mode the fan will only run if in cooling mode and the unit is calling for the compressor to run.
At least that's how most of them are set up that I'm familiar with.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 10-21-2019, 03:24 AM   #11
Schbobby
Member
 
Join Date: Jul 2019
Location: Wareham
Posts: 40
When I put the fan into Auto on my 2019 Cougar the heat vents were on and the AC fan was off!
Schbobby is offline   Reply With Quote
Old 10-24-2019, 10:28 PM   #12
Frosty46
Member
 
Join Date: Aug 2019
Location: St. Charles
Posts: 38
Quote:
Originally Posted by skids View Post
I have a Bullet 248RKS. The AC shroud has a cover on it for winter. The system is ducted. I turned on the furnace and it was not getting hot but it was blowing out of the ducts. I went outside and checked the shroud and it was “sucked in.” So, is it not proper to run the furnace with the AC shroud covered???
The AC and the onboard furnace share few aspects. The blower for the furnace forces air though the ducting system in your trailer. To use your furnace raise the t-stat set point to your wished for temp. fan switch in auto and all is well. No need to turn off your ac/t-stat blower switch for furnace use. Now as to your "covering" your AC rooftop unit---very, very bad idea in the first place-----open invitation to rodents in the extreme!
Frosty46 is offline   Reply With Quote
Old 10-25-2019, 08:14 AM   #13
travelin texans
Senior Member
 
travelin texans's Avatar
 
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
Quote:
Originally Posted by Frosty46 View Post
The AC and the onboard furnace share few aspects. The blower for the furnace forces air though the ducting system in your trailer. To use your furnace raise the t-stat set point to your wished for temp. fan switch in auto and all is well. No need to turn off your ac/t-stat blower switch for furnace use. Now as to your "covering" your AC rooftop unit---very, very bad idea in the first place-----open invitation to rodents in the extreme!
That's a new one for me!
Never ever heard of any critter gaining access through the rooftop ac, but guess stranger things have happened.
Have met several that will not leave the stinky slinky connected for rear of critters crawling from the sewer into the RV. Have yet to figure what kind of critters or other than into the tank where they'd go, baby alligators I guess????
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
travelin texans is offline   Reply With Quote
Old 10-25-2019, 09:11 AM   #14
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,741
The ac shroud cover can become a heaven mice. I've seen it happen in the storage lots I've used over the years. It'
s not so much of them getting into the trailer as it is them nesting and chewing the wire insulation. They can creat total havoc on wiring.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 10-25-2019, 10:07 AM   #15
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,979
If you think about it, it's much more "comfortable" camping in a tent rather than camping outdoors in the rain... Mice are, I'm sure, also inclined to take up residence in a "nice toasty, warm tent rather than in the "next door trailer's A/C shroud that's filled with slots and holes and doesn't block the wind or rain"....

It's not so much about "using the A/C as an entry point" as it is about "the A/C tent makes a perfect place to spend the winter and destroy the wiring, foam insulation and possibly store enough "food reserves" to keep them wet and increase corrosion from the "wet food stores"... Not to mention the "overall, general mess" they make "under the tent and in the squirrel cage blower assembly as they gnaw on the soy based insulation in the motor windings, all while toasty warm in their "human provided tent".........
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 10-25-2019, 05:37 PM   #16
blubuckaroo
Gone Traveling
 
Join Date: May 2019
Location: Ridgefield WA
Posts: 190
Turn the breaker off!
We leave our TT in a covered storage with a 20 amp circuit for battery maintenance. I always open the breaker for the A/C here. Reason? what if the goofy electronic thermostat were to malfunction?
blubuckaroo is offline   Reply With Quote
Reply

Tags
air conditioner, cover, furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 01:33 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.