AC/Vent Smell

Did a search on here but came up empty so here goes my Q...2020 Outback 291UBH, 9 months old and full timing since new. after a long wet winter I turned on the ventilation fan and then the air conditioner a few days ago. both are exhibiting a mildew odor (like cat urine - I dont have a cat). removed the Coleman Mach ceiling cover and had a look to see if there was any obvious mold or mildew but found none and the screens are clean (didnt see a filter per se but if there is one that would be my next step). Over the winter i did see some condensation dripping from around the fan on occasion so i know there has been moisture in that area. tried spraying some fabreeze up there and into the ducts but that didnt last long. next tried some clorox mildew eliminator in the same cavities above the cover, the ducting and around the evaporator but again the fix was short lived. the evap fins are clean. went up on the roof and removed the cover; no dead animals, plugged drain holes in the condenser drip pan nor evidence of pooled water. the condenser fins are immaculately clean. I'm stumped but guessing there is mildew somewhere around the evap or in the ducting (or a dirty filter that i am not seeing). there is no way to access the ducting to clean it. the smell is not from my roof vent or the fridge. gut feeling is the usual "it's not gonna go away on it's own" the more i run the system. temps are already in the high 80's. any ideas?
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 05-29-2020, 08:04 PM   #2
Bob R
Senior Member
 
Join Date: Jan 2020
Location: Pahrump
Posts: 129
Is it urine or more of a vinegar smell? Whatever smell it is it is possibly some mold build up in the duct work. It happens quite a bit with newer cars and the A/C in them. Different ways to try and get rid of the smell such as an auto AC duct cleaner (enzamatic cleaner) or sometimes an ozone generator but I don't know how that would work with an RV. Absolutely best way is to isolate the duct and replace it, which in an RV is not an easy task. Others may have different suggestions so try them all, easiest to hardest. A good cleaning of your AC unit(s) should also be in order also.

bob
__________________
2019 Raptor 356 with iFlex Smartryde Suspension
2022 F350 CC DRW 409CI Diesel
Bob R is offline   Reply With Quote
Old 05-30-2020, 05:08 AM   #3
+Ruff Rider
Gone Traveling
 
Join Date: Apr 2015
Location: United States
Posts: 171
I would take it to the dealer and find out how water got in the ductwork. Mold is BAD. You dont want to breath that stuff. This is not something you want to tackle yourself. Sure you can spray junk in there bit there is the problem of how the mold got there in the first place. your RV isn't even a year old yet.
+Ruff Rider is offline   Reply With Quote
Old 06-25-2020, 03:53 PM   #4
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
Quote:
Originally Posted by +Ruff Rider View Post
I would take it to the dealer and find out how water got in the ductwork. Mold is BAD. You dont want to breath that stuff. This is not something you want to tackle yourself. Sure you can spray junk in there bit there is the problem of how the mold got there in the first place. your RV isn't even a year old yet.
This smell is exactly like cat urine but I know darn well its mildew. I finally found the problem. This is Part 1 from a couple weeks ago while investigating for moisture in the evaporator plenum from inside the trailer via the vent cover on the ceiling. I've seen a bit of moisture in the fan cavity a few times in the past - probably from condensation or an outside water leak forming on the aluminum plate behind the fan and steel fan shaft itself which then dripped down onto the aluminum framework bolted directly to the ceiling. while the moisture was very minor it was obviously wet enough at times to occasionally drip thru one of the screwholes holding the vent cover framework to the ceiling. it's happened half a dozen times over the last 9 months and usually lasts only for a very short time while running the fan or AC (15 minutes or less @ one drop per minute so not a heap of water but still wet nonetheless). I do not see a way to prevent condensation forming on these metal surfaces other than better dehumidifying during the winter months (IF condensation is the actual source). I run a dehumidifier and several EvaDry desiccants and Damp Rid placed strategically throughout the trailer but really i need a bigger dehumidifier irregardless. my theory is this water was flung around by the fan onto the fabric insulation coverings inside the plenum itself. the plenum has foam and cloth-like material attached to it. some of it looks similar to fiberglass (obviously not fiberglass in 2020 but definitely some sort of insulation). i noticed a slight green tinge to it (see photo) as well as some discoloration of the foam material. so im wondering if these materials have absorbed moisture and thus the mildew smell. I do not see any black mold anywhere nor have i ever found it in the wrig; occasionally i see very minute amounts of mildew along the baseboards, under the couch in the slideout on the carpet at the baseboards, around the bunkbed mattresses and in the window sills - but again, it is always very minor and i clean these areas daily to prevent any buildup. im thinking there is a leak somewhere on the roof letting a small amount water in; but its just a theory. maybe its just condensation from the cool Oregon winter despite venting. Will be going up on the roof a second time and taking apart the plenum for a much closer look. Part 2 to follow soon...
Attached Thumbnails
Click image for larger version

Name:	20200531_104615.jpg
Views:	217
Size:	112.0 KB
ID:	28278   Click image for larger version

Name:	20200531_104641.jpg
Views:	202
Size:	51.0 KB
ID:	28279   Click image for larger version

Name:	20200531_104651.jpg
Views:	223
Size:	45.3 KB
ID:	28280   Click image for larger version

Name:	20200531_104748.jpg
Views:	236
Size:	78.1 KB
ID:	28281  
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 06-25-2020, 03:58 PM   #5
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
more pics..................
Attached Thumbnails
Click image for larger version

Name:	20200531_104801.jpg
Views:	204
Size:	86.6 KB
ID:	28282   Click image for larger version

Name:	20200531_104812.jpg
Views:	223
Size:	81.7 KB
ID:	28283   Click image for larger version

Name:	20200531_104831.jpg
Views:	210
Size:	69.0 KB
ID:	28284   Click image for larger version

Name:	20200531_104840.jpg
Views:	226
Size:	98.2 KB
ID:	28285  
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 06-25-2020, 04:02 PM   #6
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
and a few more............
Attached Thumbnails
Click image for larger version

Name:	20200531_104853.jpg
Views:	224
Size:	103.5 KB
ID:	28286   Click image for larger version

Name:	20200531_135007.jpg
Views:	232
Size:	64.1 KB
ID:	28287  
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 06-25-2020, 04:15 PM   #7
Northofu1
Senior Member
 
Northofu1's Avatar
 
Join Date: May 2018
Location: Markham, Ontario
Posts: 1,942
I'm pretty sure if you clean your coils and clean out the condensate tray yearly, it would pretty much eliminate that smell. The same in your car, some people run it on Max AC and that doesn't allow the condensate to flush out the line, collects dust and crap and starts to smell. I found in my last rig that if you close vents and open the AC dump into the main cabin until it starts to dry it out and get cold enough it keeps moisture from forming in vents.
__________________
Dan & Serena

2019 GMC SIERRA 2500 HD SLE
2015 Cougar X-Lite 29 RET
Northofu1 is offline   Reply With Quote
Old 06-25-2020, 06:23 PM   #8
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
Quote:
Originally Posted by Northofu1 View Post
I'm pretty sure if you clean your coils and clean out the condensate tray yearly, it would pretty much eliminate that smell. The same in your car, some people run it on Max AC and that doesn't allow the condensate to flush out the line, collects dust and crap and starts to smell. I found in my last rig that if you close vents and open the AC dump into the main cabin until it starts to dry it out and get cold enough it keeps moisture from forming in vents.
Much appreciated Northofu1 for the input and I totally agree with you . but if you look at the evap and condenser coils you will see they are sparkling clean after only 10 months of full timing even before i scrubbed both with clorox mildew remover and a brush (although that doesnt mean they didnt have mildew on them from appearance alone). same for the condenser drip tray. this ac unit has less than 25 hours on it from new. your advice is certainly good annual maintenance that i will surely do every year...but you will see why it wont help when i post part 2 and reveal where the mildew is actually coming from...stay tuned!
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 06-25-2020, 11:37 PM   #9
Northofu1
Senior Member
 
Northofu1's Avatar
 
Join Date: May 2018
Location: Markham, Ontario
Posts: 1,942
What is the exterior condensate flow like from the unit?
It should drip off of the trailer gutters quite steadily. Maybe the condensate has nowhere to go or maybe backing up?
On larger commercial air handling units I have seen water infiltration if the condensate pan isn't draining freely.
__________________
Dan & Serena

2019 GMC SIERRA 2500 HD SLE
2015 Cougar X-Lite 29 RET
Northofu1 is offline   Reply With Quote
Old 06-26-2020, 05:26 AM   #10
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,714
I would caution the OP on the "i scrubbed both with clorox mildew remover and a brush" operation. Those coils are aluminum ad very thin. They also don't play well with some chemicals. I would suggest an aerosol can of foam A/C coil cleaner and a very soft nylon brush, nothing stiffer than a paint brush.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 06-26-2020, 01:58 PM   #11
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
PART 2: Sorry for the lengthy posts but I'm an old mechanic and think it prudent to explain the problem and what i found for others who may have the same issue...afterall, that's the entire purpose of these forums. And the problem I found can happen to ANYONE with an RV...

Went back up on the roof and disassembled the sheet metal evaporator plenum and there it was...the plenum on the inlet side of the evap has insulating material on the top and side plates and that material was full of mildew with the majority along the seams where the top and sides screw together. the factory applied two little 2"x2" pieces of ducting tape on the front corners of the plenum where the top and sides screw together but NOTHING along the rest of the seams. I removed the fouled insulation (still a bit more to scrape off yet as you can see in the photos) and cleaned the plenum with mildew remover. went to Home Depot and Lowes for some new insulation but they only carry big rolls so will have to find another solution (maybe reflectix or foam board). I taped all the seams thoroughly. The smell is now pretty much gone but the question remains: why was there moisture there in the first place? was it from condensation over the long wet winter or did rainwater seep into the plenum during travel via the seams that werent taped up? as previously mentioned i did see moisture on the metal fan plate on the downside of the evap as well as the fan shaft itself and there was some minor dripping from the ceiling vent when the ac was on (this happened beginning the first week of ownership). could condensation other than what drips into the drip pan be forming inside the plenum while the unit is running? could this be a lack of ventilation in the plenum? as for the condensate drip pans, they were sparkling clean with no evidence of standing water anywhere and the drains were not clogged (i even watched during operation and they are draining as designed). as for cleaning the evap fins with clorox, too late now Marshall - whats done is done. thoughts? hate to see this happen again. tx in advance for any input - anything is appreciated
Attached Thumbnails
Click image for larger version

Name:	20200625_153113.jpg
Views:	199
Size:	376.2 KB
ID:	28297   Click image for larger version

Name:	20200625_153109.jpg
Views:	210
Size:	501.5 KB
ID:	28298   Click image for larger version

Name:	20200625_153131.jpg
Views:	219
Size:	450.2 KB
ID:	28299   Click image for larger version

Name:	20200625_153136.jpg
Views:	220
Size:	355.2 KB
ID:	28300  
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 06-26-2020, 01:59 PM   #12
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
a few more pics
Attached Thumbnails
Click image for larger version

Name:	20200625_150504.jpg
Views:	182
Size:	283.3 KB
ID:	28301   Click image for larger version

Name:	20200625_150517.jpg
Views:	232
Size:	392.3 KB
ID:	28302   Click image for larger version

Name:	20200625_150545.jpg
Views:	218
Size:	231.0 KB
ID:	28303  
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Old 06-27-2020, 05:24 AM   #13
Lee
Senior Member
 
Join Date: Feb 2013
Location: Lacey, WA
Posts: 499
Rodgebone, just a note of thanks for the follow up to your problem.

Many times, on various forums, Folks post questions concerning their problem, get replies,... then never post the solution.

As a fellow member living in the Great North-Wet, I do not believe that your problem is a result of our high humidity and/or condensation. If this was the case there would be thousands of Posts like yours.

I feel that you had/have a water intrusion issue into the A/C unit ....possibly as you described in the lack of Duct tape or something else.

Again, thanks for the follow-up!!!!
__________________
Lee

1970 F250 Highboy 4x4
2013 Cougar 21RBSWE
Lee is offline   Reply With Quote
Old 07-25-2020, 10:55 AM   #14
rodgebone
Senior Member
 
Join Date: Nov 2019
Location: Portland, OR
Posts: 114
The fix (part 3):

Went back to Home Depot and found (in the AC/Ducting aisle this time) insulation for the plenum and some very malleable ducting tape. cost about $23 for both the tape and insulation (enough to do the job 4x). So once again took apart the plenum on the roof and scraped off the remaining mildew-infested insulation from the sheet metal. Installed new fresh stuff and thoroughly sealed the seams on the plenum. took about an hour to do and was pretty straight forward. forgot to take pics but here a few from after the install from an inside view while I was removing and replacing the inlet/outlet partition below the evaporator that is probably mildew infested as well. Used foam board and sealed it with the tape to make a replacement. And while I was at it I found a lot of the factory ducting tape had not been applied correctly and more than half of it had peeled loose around the wiring cuts, the ducts and the plenum to ceiling. so resealed those areas with new tape while it was apart. the factory did a pretty sloppy job IMHO as there were gaps all over from poor tape insulation installation that came loose after less than a year so airflow was not going everywhere it is supposed to. not only will the mildew be gone but now the airflow path thru the ceiling ducting be much more direct and efficient.

Basically, I just got some aluminum foil faced 1/2" thick insulation and taped it onto every inch i could access and removed or retaped all the loose factory stuff. Then replaced the cloth material partition. Seems to have done the trick after a couple of hot days of testing.
Attached Thumbnails
Click image for larger version

Name:	20200703_151502.jpg
Views:	220
Size:	234.9 KB
ID:	28840   Click image for larger version

Name:	20200703_151508.jpg
Views:	230
Size:	296.0 KB
ID:	28841   Click image for larger version

Name:	20200703_151523.jpg
Views:	201
Size:	295.1 KB
ID:	28842   Click image for larger version

Name:	20200703_151533.jpg
Views:	189
Size:	263.7 KB
ID:	28843  
__________________
2020 291UBH Outback Ultra Lite
2019 Ram 1500 5.7L Laramie 4x4
rodgebone is offline   Reply With Quote
Reply

Tags
vent

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 10:37 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.