30 Amp Backyard Post

Tried to search this subject, but I could not find anything. If it has already been discussed sorry in advance.

I am thinking about setting up a 30 amp power post in the backyard, one I am tired of pulling over 80 feet of cords across the lawn, which leaves a dead section of grass snaking across the grass, and I also hate to pass it through the open basement window! Which has its own set of unique problems, one creepy crawlies get into the basement, and there is the human creepy crawlies that may migrate through that open window!

I have already planned to do this in the past, when I wired in the "Man Cave" a couple of years ago I put in a 30 amp breaker in preparation! I am not afraid of big electrical projects, the little ones I generally have to farm out to buddies and such.

Has anyone done this? If so what were your costs, and what if any equipment was used.
__________________


2014 Dodge 3500 Laramie 6.7 Cummins, Exhaust Brake.

2013 Cougar High Country 315RES
Rusty is offline   Reply With Quote
Old 07-02-2013, 06:15 AM   #2
Htfiremedic
Senior Member
 
Htfiremedic's Avatar
 
Join Date: Oct 2012
Location: Hickory Taver SC
Posts: 381
I have and the biggest cost was the wire. Conduit was fairly chrap(the gray cpvc). The outlet was around $7.
My latest was a 50amp and it was less than $200 for a 40' run.
Htfiremedic is offline   Reply With Quote
Old 07-02-2013, 06:18 AM   #3
Rusty
Senior Member
 
Join Date: Feb 2013
Location: Airdrie Alberta
Posts: 166
I believe the run would be in the 80 foot range?

If you buried the PVC did you use a Trencher? Or did you just use the old elbow grease method?
__________________


2014 Dodge 3500 Laramie 6.7 Cummins, Exhaust Brake.

2013 Cougar High Country 315RES
Rusty is offline   Reply With Quote
Old 07-02-2013, 08:15 AM   #4
mikell
Senior Member
 
Join Date: Dec 2010
Location: SW Michigan
Posts: 806
http://www.csgnetwork.com/wiresizecalc.html

Easy with #10 wire on 30 amp circut. Really don't need conduit but some people use it
mikell is offline   Reply With Quote
Old 07-02-2013, 08:46 AM   #5
azlee56
Senior Member
 
Join Date: Mar 2012
Location: Tucson AZ
Posts: 616
I was wondering about this also, but for a 50 amp and what kind of pedestal do you need going to your house for the lot line electric?
__________________
"just ride away into the black and white sunset"
azlee56 is offline   Reply With Quote
Old 07-02-2013, 08:55 AM   #6
hankpage
Site Team
 
hankpage's Avatar
 
Join Date: Jun 2009
Location: Venice
Posts: 5,346
Check local codes as many areas no longer allow direct burial wiring. Conduit is cheap and more than pays for itself if you ever want to upgrade to 50 amp you don't have to dig everything back up .... just fish the new wires through the conduit and change the breaker and outlet. Be sure to use long sweeps for your turns and wires will pull easily.
__________________
Hank & Lynn
2007 Cougar 290RKS, E-Z Flex, 16" XPS RIBs ( SOLD .. Gonna miss her ... looking for new 5r)
2004.5 Dodge 2500 QC, LB, 5.9HO, WestTach gauges, Ride-Rite
hankpage is offline   Reply With Quote
Old 07-02-2013, 09:22 AM   #7
Rusty
Senior Member
 
Join Date: Feb 2013
Location: Airdrie Alberta
Posts: 166
If I read right the only stipulations on burying the cable is, 1) depth of the conduit, and 2) use of a wood 2 x 4 to cover the cable along its length if it is closer to the surface.
__________________


2014 Dodge 3500 Laramie 6.7 Cummins, Exhaust Brake.

2013 Cougar High Country 315RES
Rusty is offline   Reply With Quote
Old 07-02-2013, 09:55 AM   #8
hankpage
Site Team
 
hankpage's Avatar
 
Join Date: Jun 2009
Location: Venice
Posts: 5,346
I have never heard of the 2x4 thing.(Even pressure treated will eventually rot) In the States trench depth is specified and may even be deeper if under a driveway. Follow your local codes and you should be fine.
__________________
Hank & Lynn
2007 Cougar 290RKS, E-Z Flex, 16" XPS RIBs ( SOLD .. Gonna miss her ... looking for new 5r)
2004.5 Dodge 2500 QC, LB, 5.9HO, WestTach gauges, Ride-Rite
hankpage is offline   Reply With Quote
Old 07-03-2013, 03:08 AM   #9
mikell
Senior Member
 
Join Date: Dec 2010
Location: SW Michigan
Posts: 806
I'm finishing up mine tonight . About 40 feet of #10 and a $30 box from Lowes. Mines on the side of my shop for the motorhome. The 5er has a 50 amp on a post both enough to fully run each unit
mikell is offline   Reply With Quote
Old 07-03-2013, 03:48 AM   #10
therink
Senior Member
 
Join Date: May 2010
Location: Rochester, NY
Posts: 1,605
I ran direct burial romex from dedicated 30amp breaker in my garage to a post in backyard at my rv pad and installed a 30amp rv outlet I purchased from Lowes.
__________________
Steve Rinker
Rochester, NY
2013 Outback Sydney 340FBH (12,280 lbs loaded-scale)

2015 GMC Sierra Denali 3500HD, SRW, Duramax, CC, SB (payload 3700)

https://i1109.photobucket.com/albums/...65/340FBH1.jpg
therink is offline   Reply With Quote
Old 07-03-2013, 06:01 AM   #11
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,979
Here is one of a number of posts about installing underground conduit/romex to supply an RV power pole in the yard. While the actual wiring is a bit different, the concept of trenching/installing the outlet box is very similar.

http://www.keystonerv.org/forums/sho...extension+cord

One thing to remember (ETCH IT IN STONE) 30 Amp RV service is wired as 115VAC it is not wired like a home dryer or stove plug !!!!!!!!! If you accidentally wire it as 230 VAC you will destroy much of your RV's electrical system the moment you plug it in.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 07-03-2013, 06:24 AM   #12
byrdr1
Senior Member
 
byrdr1's Avatar
 
Join Date: Sep 2009
Location: North Carolina
Posts: 1,037
Quote:
Originally Posted by JRTJH View Post
One thing to remember (ETCH IT IN STONE) 30 Amp RV service is wired as 115VAC it is not wired like a home dryer or stove plug !!!!!!!!! If you accidentally wire it as 230 VAC you will destroy much of your RV's electrical system the moment you plug it in.
Hot is one 30 amp breaker for 115VAC and the then you have a netrual wire and then a ground wire.
10/2 with copper ground wire is best for 30amp. I used ground burial wire but mine was run through my carport so it is inside conduit from house to 30amp plug box.
With my 5er NOW I use a 50amp female locking ring plug on camper side with a 30 plug on the box side.Marinco brand.
randy
PS one day I may upgrade to a 50 amp service which is still 120vac each leg, but then I am draggin that large and heavy and expensive cord out and around..
__________________

Randy "Camp On"
2011 Cougar 327RES
2014 Ford F-350, 6.7L 4X4, CC, SRW
byrdr1 is offline   Reply With Quote
Old 07-03-2013, 11:08 AM   #13
diugo
Permanent User Ban
 
Join Date: Apr 2013
Location: Imperial Dam LTVA (Yuma, AZ)
Posts: 258
Quote:
Originally Posted by mikell View Post
http://www.csgnetwork.com/wiresizecalc.html

Easy with #10 wire on 30 amp circut. Really don't need conduit but some people use it
Actually, #6 is the recommended wire size. Remember that an 80-foot extension cord carries two conductors, so 80 feet---not 40---represents half the circuit length (the question asked by the calculator).
diugo is offline   Reply With Quote
Old 07-04-2013, 04:26 PM   #14
tileman
Senior Member
 
Join Date: May 2012
Location: Fla
Posts: 351
I ran 50 amp to my 5th wheel was about 300' wire and box was around 1,000
and I did the work myself.

Here's some good info http://www.myrv.us/electric/index.htm
__________________
2012 Fuzion 310 Toy hauler
2010 Dodge DRW 4x4 3500
tileman is offline   Reply With Quote
Old 07-05-2013, 06:42 AM   #15
K4BEV
Member
 
Join Date: Mar 2013
Location: SWTN
Posts: 32
TAKE PICTURES - Draw up a map
You may really want to know where that conduit is buried several years from now.
__________________
'07 Laredo
'05 F-250 Diesel TT
K4BEV is offline   Reply With Quote
Old 07-05-2013, 09:54 AM   #16
labs4life
Senior Member
 
labs4life's Avatar
 
Join Date: Dec 2012
Location: Woodstock, GA
Posts: 405
Quote:
Originally Posted by K4BEV View Post
TAKE PICTURES - Draw up a map
You may really want to know where that conduit is buried several years from now.
^^^^^^^this. You might want an afterthought water line there as well and it would suck to cut your wire. Better to have and not need than need and not have!!!! Truest words my Grandpa ever spoke!
labs4life is offline   Reply With Quote
Old 07-05-2013, 11:18 AM   #17
Htfiremedic
Senior Member
 
Htfiremedic's Avatar
 
Join Date: Oct 2012
Location: Hickory Taver SC
Posts: 381
Quote:
Originally Posted by Rusty View Post
I believe the run would be in the 80 foot range?

If you buried the PVC did you use a Trencher? Or did you just use the old elbow grease method?
I buried it under DW's flower bed, seriously. Black paper and rubber mulch. I'm lazy...lol
Htfiremedic is offline   Reply With Quote
Old 07-05-2013, 01:35 PM   #18
labs4life
Senior Member
 
labs4life's Avatar
 
Join Date: Dec 2012
Location: Woodstock, GA
Posts: 405
^^^^^as I say sometimes, work smarter not harder!!
labs4life is offline   Reply With Quote
Old 07-05-2013, 06:00 PM   #19
cabinfever
Senior Member
 
Join Date: Feb 2013
Location: Erie, PA
Posts: 441
Added an RV breaker 30 AMP service at the house today. I used 10/2 and total wire run was about 80 feet. Voltage at RV plug is 118 volts.
__________________

2007 Silverado 2500HD 4X4
2013 Springdale 303BHSSR
cabinfever is offline   Reply With Quote
Old 07-05-2013, 10:29 PM   #20
bigcitypopo
Member
 
Join Date: Jul 2013
Location: Ventura Co. - CA
Posts: 39
I'd pull wire for 50A if I did mine over... Wire the 30A and save the other as a future... Then it's just a breaker and outlet swap. Be sure you use conduit. Schedule 40 should be fine. Some places require EMT. Please wire a proper ground. Some codes allow the EMT to be used a ground... I never liked that.

Get a good outdoor box, and then it's easy as pie..
__________________
2012 F150 screw lariat ecoboost
2014 Springdale 294BHSSRWE
bigcitypopo is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 06:21 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.