Why a propane regulator here?

I have a Cougar 5th wheel, and had issues with the automatic switchover for propane. Assuming that it was the switching unit, I replaced it. Still doesn't work! After some more checking, it appears that I get no propane from the driver side line. I'm guessing that the regulator that is mounted onto the iron pipe going across the camper is broke.

But why is there a regulator there to begin with? The propane switching unit has an integrated regulator, and the tank on the passenger side doesn't have a separate regulator. If the connection from one side to the other was a hose, maybe to reduce flow in case of a cut. But this is an iron pipe! I'm thinking of connecting the propane hose directly to the iron pipe and just do away with the regulator, but thought to seek some opinions on here first. So what do you think?
Old Bear is offline   Reply With Quote
Old 08-13-2015, 08:54 AM   #2
SteveC7010
Senior Member
 
SteveC7010's Avatar
 
Join Date: Sep 2011
Location: Northville NY in the Adirondacks
Posts: 2,128
Quote:
Originally Posted by Old Bear View Post
I have a Cougar 5th wheel, and had issues with the automatic switchover for propane. Assuming that it was the switching unit, I replaced it. Still doesn't work! After some more checking, it appears that I get no propane from the driver side line. I'm guessing that the regulator that is mounted onto the iron pipe going across the camper is broke.

But why is there a regulator there to begin with? The propane switching unit has an integrated regulator, and the tank on the passenger side doesn't have a separate regulator. If the connection from one side to the other was a hose, maybe to reduce flow in case of a cut. But this is an iron pipe! I'm thinking of connecting the propane hose directly to the iron pipe and just do away with the regulator, but thought to seek some opinions on here first. So what do you think?
The regulator significantly lowers the pressure of the propane in your system. Removing it is highly dangerous.

In my rig, the tank change valve and the regulator are a one-piece unit. Perhaps you could post pics of what you are describing.

I am not sure what the real problem might be, but some things to verify:

Before anything, make sure there's propane in both tanks.

First, for the switchover to take place, the tanks have to be fully turned on. Opening the valve just partway may cause the propane to leak out at the valve, so all the way open or all the way shut.

Second, the connection to the tank on the end of the pigtail needs to be fully seated and the knob fully rotated. It's a bit awkward getting your hand up in there to connect the tank so if the pigtail is not fully tight, it will either leak dry or the check valve will shut off.

Third, while you're in there, make sure that both pigtails are not kinked. That'll shut off a tank quite efficiently.
__________________

'11 Cougar 326MKS loaded with mods
'12 Ford F250 SuperCab 6.7 PowerStroke Diesel
Amateur Radio: KD2IAT (146.520) GMRS: WQPG808 (462.675 TPL 141.3)
SteveC7010 is offline   Reply With Quote
Old 08-13-2015, 10:55 AM   #3
Old Bear
Junior Member
 
Join Date: Mar 2014
Location: Tennessee
Posts: 28
Quote:
Originally Posted by SteveC7010 View Post
The regulator significantly lowers the pressure of the propane in your system. Removing it is highly dangerous.

In my rig, the tank change valve and the regulator are a one-piece unit. Perhaps you could post pics of what you are describing.

I am not sure what the real problem might be, but some things to verify:

Before anything, make sure there's propane in both tanks.

First, for the switchover to take place, the tanks have to be fully turned on. Opening the valve just partway may cause the propane to leak out at the valve, so all the way open or all the way shut.

Second, the connection to the tank on the end of the pigtail needs to be fully seated and the knob fully rotated. It's a bit awkward getting your hand up in there to connect the tank so if the pigtail is not fully tight, it will either leak dry or the check valve will shut off.

Third, while you're in there, make sure that both pigtails are not kinked. That'll shut off a tank quite efficiently.
I had just refilled both tanks, and was intentionally testing the new changeover (http://www.campingworld.com/shopping...egulator/24030). Yes, it has an integrated two-stage regulator. What I find odd is that the tank that is in the compartment with the changeover connects directly to the changeover (side A), but the tank on the other side of the camper connects to a regulator on that side, which is connected to an iron pipe coming into the compartment with the changeover, which in turn is connected to a hose that is connected to the other side of the changeover (side B). Both A and B connections are going through the integrated two-stage regulator, so I'm not seeing where reducing the pressure to go 7 feet through an iron pipe is accomplishing anything. An abundance of caution? Oversupply of regulators? I'll look more closely this afternoon, finally cooled off a bit here.
Old Bear is offline   Reply With Quote
Old 08-13-2015, 11:46 AM   #4
Ken / Claudia
Senior Member
 
Join Date: Nov 2012
Location: Fruitland
Posts: 3,357
Sounds strange to me, until someone corrects me, I do not think any trailer should have 2 regulators. But, just reading thru this, You filled both tanks and tested the auto switch over. It switches over when the tank you picked to run first is near empty. How are you attempting it to switch from a full tank to a full tank by itself. If you can list the trailer new/used and post photos of what your describing.
__________________
2013 24RKSWE (27ft TT) Cougar 1/2 ton series SOLD 10-2021
2013 Ford F350 4x4 CC 6.7 engine, 8 ft bed, 3.55 rear end, lariat package
Retired from Oregon State Police in 2011 than worked another 9.5 years as a small town traffic cop:
As of 05-2020, I am all done with 39 years total police work. No more uniforms for me.
Ken / Claudia is offline   Reply With Quote
Old 08-13-2015, 11:54 AM   #5
chuckster57
Site Team
 
chuckster57's Avatar
 
Join Date: Jul 2014
Location: Modesto
Posts: 20,323
On fivers with two tanks, one on each side, the one without the switchover valve will have a regulator. This is pretty much standard and not a Keystone only thing. What the reason is I don't know but seeing as it's on all newer brands it must be a safety thing.
__________________

2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.

Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
chuckster57 is offline   Reply With Quote
Old 08-13-2015, 01:03 PM   #6
SteveC7010
Senior Member
 
SteveC7010's Avatar
 
Join Date: Sep 2011
Location: Northville NY in the Adirondacks
Posts: 2,128
Quote:
Originally Posted by chuckster57 View Post
On fivers with two tanks, one on each side, the one without the switchover valve will have a regulator. This is pretty much standard and not a Keystone only thing. What the reason is I don't know but seeing as it's on all newer brands it must be a safety thing.
I just went out and pulled the curbside tank, and sure enough, there is a little tiny regulator in the line. It's almost buried by the wall and if you did not know it was there, you might never notice it. I keep learning....

I am thinking that maybe the changeover/regulator actually regulates only one side of the valve. Would be interesting to know for sure.

OK, for the OP, the regulator on the curbside is there and clearly necessary. I'd suggest you run through some of the other things that I mentioned in my first post.
__________________

'11 Cougar 326MKS loaded with mods
'12 Ford F250 SuperCab 6.7 PowerStroke Diesel
Amateur Radio: KD2IAT (146.520) GMRS: WQPG808 (462.675 TPL 141.3)
SteveC7010 is offline   Reply With Quote
Old 08-13-2015, 01:42 PM   #7
Ken / Claudia
Senior Member
 
Join Date: Nov 2012
Location: Fruitland
Posts: 3,357
Thanks guys for finding that there really are 2 regulators. Question remains why? And with 2 full tanks can you check the auto switch over? I have turned mine many times to use the 2nd tank before 1st is empty but, that's not auto.
__________________
2013 24RKSWE (27ft TT) Cougar 1/2 ton series SOLD 10-2021
2013 Ford F350 4x4 CC 6.7 engine, 8 ft bed, 3.55 rear end, lariat package
Retired from Oregon State Police in 2011 than worked another 9.5 years as a small town traffic cop:
As of 05-2020, I am all done with 39 years total police work. No more uniforms for me.
Ken / Claudia is offline   Reply With Quote
Old 08-13-2015, 02:20 PM   #8
jsmith948
Senior Member
 
Join Date: Jan 2012
Location: Central San Joaguin Valley, CA
Posts: 2,117
On our Cougar, we had issues with the auto change-over. Could not get gas from the driver's side tank. Turned out to be a faulty 'pig-tail'. The safety valve that limits gas flow if there is a ruptured line would not reset. Ended up replacing both of the 'pigtails'. No problems since. Also, if you turn the tank valves on too fast, you will trigger the safety valve. If that happens, you simply have to disconnect the hose from the tank, wait a bit, then reconnect.
If you do a forum search, there is a thread that explains, in detail, how to properly open the valves of the gas system.
__________________

Jack & Marty
2018 Laredo 298 SRL
2011 F-250 SB Crew Cab 4x4 6.7L
jsmith948 is offline   Reply With Quote
Old 08-13-2015, 02:59 PM   #9
hankaye
Senior Member
 
Join Date: Apr 2011
Location: Arrey,
Posts: 2,368
Howdy All;

The Driver's side regulator is for reducing the pressure to an acceptable
level for the Black iron pipe. It gets reduced to IIRC 30 psi. They are just
like the regulators on a household tank and function for the same reason,
Should the transport line (black iron pipe), rupture the full pressure won't
cause a massive leak but allow the rapid flow mechanism in the pigtail to
shut off the flow.

OP, ... When you opened the valve to the driver's side did you open it
s...l...o...w...l...y? If not then you triggered the shut off function in the pig
tail. turn it off, remove the pig tail from the tank, then re attach it, the
removing allows the pressure to dissipate. Hook it back up and try it
again.

hankaye
__________________
Striving for a less complicated life since 1949 ...

Home: 2008 Cougar 278 RKS
T.V.: 2004 F-250 4X4, Level III BulletProofed , Detroit Tru-Track Differential (915A550)
Dog: 2006 Border Collie (Rascal) aka Maximum fur dispersal unit. (08/04/2006 - 12/16/2017) RIP.
hankaye is offline   Reply With Quote
Old 08-13-2015, 05:21 PM   #10
shiggs68
Member
 
Join Date: Jul 2012
Location: Pataskala
Posts: 70
On a two tank system where the tanks are on each side of a fifth wheel, the far side tank requires a small regulator if the run to the main regulator is more than 2 ft. This is standard propane regulations.

That regulator reduces the pressure to something like 30 inches water column and the main regulator reduces the distribution pressure to 11 inches water column.


Sent from my iPad using Tapatalk
shiggs68 is offline   Reply With Quote
Old 08-13-2015, 10:27 PM   #11
bobbecky
Senior Member
 
bobbecky's Avatar
 
Join Date: Jul 2013
Location: Box Elder
Posts: 2,907
This is an answer to the same question on a different brand RV forum.

The main reason for the regulator is to make sure that once the propane leaves the tank as a vapor that it stays a vapor. Propane regulators in trailers do not regulate liquid only vapor. If the regulator was not there the pressure in the hose would be the same as the tank. This could lead to the vapor condensening back into a liquid. With a reduction in the pressure from the regulator to the other side of the coach this will greatly reduce the possibility of the vapor in the crossover hose turning back into a liquid. This is all based on propanes vapor/pressure saturation points. the lower the pressure the lower the temperature to turn it back into a liquid.

Hope that answers the question.
__________________
Bob & Becky
2012 3402 Montana
2012 Chevy 2500HD D/A CC
bobbecky is offline   Reply With Quote
Old 08-14-2015, 06:40 AM   #12
Old Bear
Junior Member
 
Join Date: Mar 2014
Location: Tennessee
Posts: 28
Quote:
Originally Posted by bobbecky View Post
This is an answer to the same question on a different brand RV forum.

The main reason for the regulator is to make sure that once the propane leaves the tank as a vapor that it stays a vapor. Propane regulators in trailers do not regulate liquid only vapor. If the regulator was not there the pressure in the hose would be the same as the tank. This could lead to the vapor condensening back into a liquid. With a reduction in the pressure from the regulator to the other side of the coach this will greatly reduce the possibility of the vapor in the crossover hose turning back into a liquid. This is all based on propanes vapor/pressure saturation points. the lower the pressure the lower the temperature to turn it back into a liquid.

Hope that answers the question.
Why yes ... yes, it does!
Old Bear is offline   Reply With Quote
Old 04-16-2016, 05:29 PM   #13
shiggs68
Member
 
Join Date: Jul 2012
Location: Pataskala
Posts: 70
Why a propane regulator here?

Propane vaporizes at any temperature above -44 degrees. The regulator has nothing to do with that process other then because of the high tank pressure resulting from the vaporization, it is a safety factor to distribute a lower pressure than the high tank pressure.

Likewise, as I stated above, it is propane code the an intermediate regulator be used on the far tank because of the distance. High pressure tank hoses are not allowed longer then 2 feet.


TravelingRVDoctor -Sent from my iPad using Tapatalk
shiggs68 is offline   Reply With Quote
Old 04-16-2016, 05:51 PM   #14
Bob Landry
Senior Member
 
Join Date: Jan 2011
Location: Austin, Tx
Posts: 1,910
I've read several threads pertaining to the propane line "locking u" because of opening the valve too fast. I've been cranking mine open since I've had a trailer and have not once had the high pressure valve kick in. It's very possible that is something that someone posted on the Internet and it just got parroted. The pressure in the propane line is the same when you slightly crack the valve as it is when it's wide open.
The High pressure valve in the pigtail is designed to kick in in the event of a rupture or break in the gas line which would cause an immediate and rapid loss of pressure. If just opening the tank too fast caused that, there would be thousands of unhappy people out there babying their propane tank valves and I don't hear of that happening. If this phenomenon in fact does happen, disconnecting the hose from the tank would be unnecessary as the pressure could be released simply by turning on a stove burner or your grill.

I'm not saying that it is an impossibility for it to happen, but I would like to see some substantiating evidence that it happens other than something that someone's brother's uncle wrote it on the Internet.
__________________
2011 Outback 277RL
2013 F250 XLT Crew Cab 6.2L

Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Old 04-17-2016, 05:07 AM   #15
Pull Toy
Senior Member
 
Pull Toy's Avatar
 
Join Date: Mar 2015
Location: Southeastern Connectiut
Posts: 1,306
To check the auto change over function just turn off the tank that you want to change from and use up the propane in the system. A safe way to do this is to light your stove. The auto change over should happen when the pressure drops enough to call for it.

I usually prefer not to keep both tank valves open at the same time. From past experience I have learned that by manually starting the second tank when the first one is empty, I have time to refill the first tank without being totally out of gas in the middle of the night.
__________________

Pull Toy

Steve & Jan, Ava & Emma (Mini Schnauzers):
2016 F350 Lariat 4X4 Powerstroke CC/SB "PULLTOY V"
2013 Alpine 3535RE "MAGIC CARPET IV"
Proud Navy Vet!
Pull Toy is offline   Reply With Quote
Old 04-17-2016, 06:21 AM   #16
chuckster57
Site Team
 
chuckster57's Avatar
 
Join Date: Jul 2014
Location: Modesto
Posts: 20,323
I have had a couple of customers come in with no L/P flow, and found the high pressure valve kicked in. Albeit rare, it can and does happen.
__________________

2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.

Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
chuckster57 is offline   Reply With Quote
Old 04-21-2016, 05:11 PM   #17
shiggs68
Member
 
Join Date: Jul 2012
Location: Pataskala
Posts: 70
Quote:
Originally Posted by Bob Landry View Post
I've read several threads pertaining to the propane line "locking u" because of opening the valve too fast. I've been cranking mine open since I've had a trailer and have not once had the high pressure valve kick in. It's very possible that is something that someone posted on the Internet and it just got parroted. The pressure in the propane line is the same when you slightly crack the valve as it is when it's wide open.

The High pressure valve in the pigtail is designed to kick in in the event of a rupture or break in the gas line which would cause an immediate and rapid loss of pressure. If just opening the tank too fast caused that, there would be thousands of unhappy people out there babying their propane tank valves and I don't hear of that happening. If this phenomenon in fact does happen, disconnecting the hose from the tank would be unnecessary as the pressure could be released simply by turning on a stove burner or your grill.



I'm not saying that it is an impossibility for it to happen, but I would like to see some substantiating evidence that it happens other than something that someone's brother's uncle wrote it on the Internet.


The evidence is Federal Law. Just google search OPD propane valves. The are require on all 20, 30, and 40 pound DOT Propane tanks. Not hear say, it does happen and is designed to shut down if high flow is detected to protect against hot pressure tank hose failure.
shiggs68 is offline   Reply With Quote
Old 04-21-2016, 07:27 PM   #18
Bob Landry
Senior Member
 
Join Date: Jan 2011
Location: Austin, Tx
Posts: 1,910
No argument about it being Federal law. No one has said anything about any law. The intent of the shut off is to stop the flow of propane in the event of a break in any part of the propane system that suddenly releases the pressure in the line.
__________________
2011 Outback 277RL
2013 F250 XLT Crew Cab 6.2L

Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 09:03 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.