Old 06-27-2019, 09:54 AM   #21
DocP
Senior Member
 
DocP's Avatar
 
Join Date: Oct 2016
Location: Macedonia
Posts: 217
Quote:
Originally Posted by FSS View Post
I've been using the Yamaha 2400ISHC for 6 years with no issues starting my 13.5K AC. Yamaha made this HC (high current startup) version of the 2400IS specifically to start high load startup motor like the 13.5K AC. Puts out 20 amps for the first 8-10 sec after startup. Really quiet @53db
Same here, but I have 2 of them that can run in parallel. The vast majority of the time I can get by on just one of them, even with the AC running.
__________________
DocP (Michael)
Former: Keystone Cougar 32RLI and 34TBS
Current: 2019 Georgetown GT5 31L5 motorhome
DocP is offline   Reply With Quote
Old 06-27-2019, 10:14 AM   #22
sgrol
Member
 
Join Date: Jun 2011
Location: magnolia,tx
Posts: 34
Look in to this:

https://www.microair.net/collections...nt=30176048267

Then you can run a 2000 or 2200 for your AC. I use my Honda 2000 on idle mode to start and run my 15 k unit with the Micro air and it hasn't "blown up" yet.
__________________
2017 Momentum 388 TH
2017 F350 DRW
sgrol is offline   Reply With Quote
Old 06-27-2019, 10:16 AM   #23
LFord
Member
 
Join Date: Mar 2017
Location: Warne
Posts: 61
Quote:
Originally Posted by nied View Post
My original RV was a 20' Trail Lite with a 13.K AC. The first year I rented a Honda 2000 and it ran the AC but struggled at startup. If you have a good tool rental business in your area with generator rental and sales, contact them and see if you can bring your RV over and try out some of the units.
Let's hope you don't bring one of those "rental center" generators to the RV campsite. Typically, "contractor grade" generators are found at those rental centers, and your campsite neighbors probably won't be happy with the noise especially if run at night while they're trying to sleep!
__________________
Larry J Ford (SWNC)
2016 Passport Ultra Lite Express 199ML
2013 Ford F-150 XLT Supercab, 3.5L V6 ecoBoost (turbo), 3.15 RAR, 8600 lbs. Tow Capacity, Equalizer WDH
LFord is offline   Reply With Quote
Old 06-27-2019, 11:31 AM   #24
Tooth Ferry
Member
 
Join Date: Oct 2016
Location: PellCity,Alabama
Posts: 52
Have you considered the MicroAire Easy Start for your AC?

Reduces starting power needs for your AC . Can run a 15000 on a 2000 Honda. Look it up online.
Tooth Ferry is offline   Reply With Quote
Old 06-27-2019, 12:34 PM   #25
WDPatterson
Senior Member
 
WDPatterson's Avatar
 
Join Date: Jun 2019
Location: Pipe Creek
Posts: 344
Quote:
Originally Posted by sgrol View Post
Look in to this:

https://www.microair.net/collections...nt=30176048267

Then you can run a 2000 or 2200 for your AC. I use my Honda 2000 on idle mode to start and run my 15 k unit with the Micro air and it hasn't "blown up" yet.
I actually have a micro air 364... The soft start module is a very good idea, but you must absolutely have or a true 30 amp power supply available, when you program it...

Keep in mind that the Soft-Start module does not change the running amperage/wattage consumption of your air conditioning system... It only eliminates the heavy Spike on Startup that is required to lock the rotor on the compressor...

It takes what would normally be about a 48 to 52 amp Spike and drops it to something tolerable so that you can run not only your air conditioner, but other accessories on the same generator...
WDPatterson is offline   Reply With Quote
Old 06-27-2019, 12:43 PM   #26
WDPatterson
Senior Member
 
WDPatterson's Avatar
 
Join Date: Jun 2019
Location: Pipe Creek
Posts: 344
Quote:
Originally Posted by BadmanRick View Post
If you want to run the whole camper get a 5500 watt generator.
That would be true except that many 5500 watt generators only have a 20 amp breaker on the 110 volt RV and 120/240 outlets...

Best thing to do is shop around, take a good look at any generator, do not buy unseen...
WDPatterson is offline   Reply With Quote
Old 06-27-2019, 04:28 PM   #27
sonofcy
Senior Member
 
Join Date: Sep 2017
Location: Qualicum Beach
Posts: 555
Add a easy start to the AC and you will have no problems with start up current. Honda 2200 should do it easy.
sonofcy is offline   Reply With Quote
Old 06-28-2019, 01:48 PM   #28
JohnP
Member
 
JohnP's Avatar
 
Join Date: Apr 2018
Location: Waterloo
Posts: 40
Quote:
Originally Posted by Logan X View Post
Hmm, I didn’t think the Honda 2000 watt would run an air conditioner. I’m going to try it when I get home today.
Thats what I thought too. I have a 3,000 watt Firman and there were times it struggled to get going at start up so I don't thing a 2,000 can do it.
JohnP is offline   Reply With Quote
Old 06-28-2019, 02:24 PM   #29
sonofcy
Senior Member
 
Join Date: Sep 2017
Location: Qualicum Beach
Posts: 555
Quote:
Originally Posted by JohnP View Post
Thats what I thought too. I have a 3,000 watt Firman and there were times it struggled to get going at start up so I don't thing a 2,000 can do it.
It depends if the AC is a 15,000 or a 13,500. Also as I said, add the easy start module to the AC and the 2,000 can do it just fine.
sonofcy is offline   Reply With Quote
Old 06-28-2019, 03:57 PM   #30
WDPatterson
Senior Member
 
WDPatterson's Avatar
 
Join Date: Jun 2019
Location: Pipe Creek
Posts: 344
Quote:
Originally Posted by sonofcy View Post
It depends if the AC is a 15,000 or a 13,500. Also as I said, add the easy start module to the AC and the 2,000 can do it just fine.
If the 13.5 KBTU air conditioner requires 2750 watts to lock the rotor, and 1250 watts to run, you're not leaving yourself much room... Many of these so-called 3000 watt generators are only that at peak... That means they will only pull that load for about 5 to 10 seconds... That's their Surge watt rating, and they're only reliable at supplying that wattage when they're in perfect shape...

I have a microair 364... It does work... But I wouldn't trust a generator that runs less than 3500 run-time Watts... It's just not a good idea to max out your generator, if it won't last very long if you do.. You should have twice the runtime wattage as you're going to use all the time...

Like I said, keep in mind that your refrigerator and other appliances are also running on that AC unless you switch them to propane...
WDPatterson is offline   Reply With Quote
Old 07-11-2019, 09:30 AM   #31
duh1
Member
 
Join Date: Oct 2010
Location: Panhandle of Florida
Posts: 75
I tried successively larger generators till got to a champion 3500 which runs the electric.on a 2910 bh Keystone anything smaller won't do it.
duh1 is offline   Reply With Quote
Old 07-11-2019, 10:14 AM   #32
WDPatterson
Senior Member
 
WDPatterson's Avatar
 
Join Date: Jun 2019
Location: Pipe Creek
Posts: 344
Quote:
Originally Posted by duh1 View Post
I tried successively larger generators till got to a champion 3500 which runs the electric.on a 2910 bh Keystone anything smaller won't do it.
That's because wattage / amperage equals voltage...

Conversely, wattage / voltage equals amperage...

3500 watts ÷120 volts = 29.1 amps

That's right at the ragged edge of being able to run everything in a 30-amp service trailer... I guarantee you, after a few uses, if you don't do proper maintenance, you're going to come up short...

Yes, a minimum 3500 watt run time will get you by... It will also wear out that generator a lot faster... Because it's running full load...
WDPatterson is offline   Reply With Quote
Old 07-14-2019, 07:20 PM   #33
Wingerdinger
Member
 
Join Date: Jul 2018
Location: Oak Grove
Posts: 56
My two cents..
I used 2 Champion 2000 Generators, paralleled together, and had my Progressive EMS monitor tell me I had low voltage when running my 15,000 btu A/C and a few small accessories. The wattage never doubles when paralleling 2 generators, and Champion states that you should never exceed 3000 watts with that configuration.
When one of generators gave me trouble, I got a Predator 3500. That unit is awesome. I run my fridge and A/C on econo-mode, and once started, the generator just comes off an idle. The Powerhouse 3500 is the same unit. I was cautiously optimistic, and very pleasantly surprised. It is amazingly quiet.
My only warning is carefully break them in, change oil after 2, 8, and 25 hours. The Chinese don't clean out the case well during manufacturing.
Anybody wanna buy two Champion 2000s with low hours??
__________________
2015 Crossroads Sunset Trail Reserve ST26RB
2005 Ford F-150
Doug, my S/O Patience, and Shelby the mutt
Wingerdinger is offline   Reply With Quote
Old 07-14-2019, 07:24 PM   #34
CaptnJohn
Senior Member
 
Join Date: Dec 2015
Location: Ocean Isle Beach
Posts: 1,431
Where are you located? I could be interested in 1 and parallel kit?
__________________

2022.Montana 3855 BR
2019 F350 6.7 4X4 DRW
CaptnJohn is offline   Reply With Quote
Old 07-14-2019, 07:51 PM   #35
Wingerdinger
Member
 
Join Date: Jul 2018
Location: Oak Grove
Posts: 56
Quote:
Originally Posted by CaptnJohn View Post
Where are you located? I could be interested in 1 and parallel kit?
I'm in the Minneapolis area, Minnesota.
__________________
2015 Crossroads Sunset Trail Reserve ST26RB
2005 Ford F-150
Doug, my S/O Patience, and Shelby the mutt
Wingerdinger is offline   Reply With Quote
Old 07-14-2019, 08:50 PM   #36
CaptnJohn
Senior Member
 
Join Date: Dec 2015
Location: Ocean Isle Beach
Posts: 1,431
Quote:
Originally Posted by Wingerdinger View Post
I'm in the Minneapolis area, Minnesota.


Sorry a bit far from NC. Thanks
__________________

2022.Montana 3855 BR
2019 F350 6.7 4X4 DRW
CaptnJohn is offline   Reply With Quote
Old 07-14-2019, 10:11 PM   #37
WDPatterson
Senior Member
 
WDPatterson's Avatar
 
Join Date: Jun 2019
Location: Pipe Creek
Posts: 344
Quote:
Originally Posted by Wingerdinger View Post
My two cents..
I used 2 Champion 2000 Generators, paralleled together, and had my Progressive EMS monitor tell me I had low voltage when running my 15,000 btu A/C and a few small accessories. The wattage never doubles when paralleling 2 generators, and Champion states that you should never exceed 3000 watts with that configuration.
When one of generators gave me trouble, I got a Predator 3500. That unit is awesome. I run my fridge and A/C on econo-mode, and once started, the generator just comes off an idle. The Powerhouse 3500 is the same unit. I was cautiously optimistic, and very pleasantly surprised. It is amazingly quiet.
My only warning is carefully break them in, change oil after 2, 8, and 25 hours. The Chinese don't clean out the case well during manufacturing.
Anybody wanna buy two Champion 2000s with low hours??
That's some great news!!... It sounds like you found a great combination!!...
WDPatterson is offline   Reply With Quote
Old 07-15-2019, 04:14 AM   #38
Kevin H
Junior Member
 
Join Date: Feb 2018
Location: OLD MONROE
Posts: 21
My 2 cents. I have ran mine on my 2000 watt Honda, However when the wife forgets and wants to warm her coffee in microwave. Bam it's off. Warm a bagel bam it's off. Also it takes more to start a/c after it just shuts off so you may have to wait till pressures equalize before it will restart. I broke down and bought a new 3000 watt Honda and all problems are gone. I also don't like running engines at their max which the 2000 will be doing. Good Luck.
Kevin H is offline   Reply With Quote
Old 07-15-2019, 06:27 AM   #39
sonofcy
Senior Member
 
Join Date: Sep 2017
Location: Qualicum Beach
Posts: 555
Quote:
Originally Posted by Kevin H View Post
My 2 cents. I have ran mine on my 2000 watt Honda, However when the wife forgets and wants to warm her coffee in microwave. Bam it's off. Warm a bagel bam it's off. Also it takes more to start a/c after it just shuts off so you may have to wait till pressures equalize before it will restart. I broke down and bought a new 3000 watt Honda and all problems are gone. I also don't like running engines at their max which the 2000 will be doing. Good Luck.
That's why I bought a pair of the Honda's that can be coupled together (even better now as they are 2200 Watts each). The other things you can do are install a soft start kit in the A/C to stop the initial inrush current, and also a hybrid inverter which can use the battery bank to augment the generator for a second or two. Better is to do both. My old TT was hooked up to a 20A 120V GFCI and we stayed in there with the A/C on during some construction activity. I think the reason it worked was that the A/C was a 13,500 BTU unit not 15,000.
sonofcy is offline   Reply With Quote
Old 07-15-2019, 09:03 AM   #40
WDPatterson
Senior Member
 
WDPatterson's Avatar
 
Join Date: Jun 2019
Location: Pipe Creek
Posts: 344
One thing to keep in mind is that most generators need to be set up for around 63 Hz during no load "idle", and check to make sure they're at 60 hertz, or a little bit over, when under load...
WDPatterson is offline   Reply With Quote
Reply

Tags
generator, newbie

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 12:21 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.