Old 02-20-2021, 02:01 AM   #41
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
Quote:
Originally Posted by Customer1 View Post
If neutral and ground are bonded, it can trip a GFCI even if the individual circuit isn't energized.
Gfi can not trip if the circuit is not energized.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-20-2021, 02:08 AM   #42
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
Quote:
Originally Posted by LHaven View Post
Am I missing something? OP says he plugged his trailer into a GFCI receptacle, meaning a 15A or 20A receptacle, since nothing larger comes in GFCI. That requires an adapter.
I thought it was common knowledge that trailer adapters are just flat not compatible with GFCI outlets. I'm surprised this is news to the storage facility.
I am not aware of this statement. Adaptors (dogbones) are used by almost everyone at some time or another. They do not cause problems with GFI's.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-20-2021, 07:48 AM   #43
nuctrooper
Junior Member
 
Join Date: Dec 2020
Location: Poulsbo
Posts: 26
Quote:
Originally Posted by cavie View Post
I am not aware of this statement. Adaptors (dogbones) are used by almost everyone at some time or another. They do not cause problems with GFI's.
Correct-a dogbone from 15A to 50A works just fine with a gfi. The wishbone style adapters that plug into a 30A for one leg land the 15A for the other leg will not work.
nuctrooper is offline   Reply With Quote
Old 02-20-2021, 09:09 AM   #44
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
Quote:
Originally Posted by nuctrooper View Post
Correct-a dogbone from 15A to 50A works just fine with a gfi. The wishbone style adapters that plug into a 30A for one leg land the 15A for the other leg will not work.
that is correct.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-20-2021, 04:59 PM   #45
Bostongone
Senior Member
 
Join Date: Mar 2017
Location: Ruckersville
Posts: 108
I had the identical problem with the heater element in my trailer several years ago. GFI house breaker would trip every time. Turned off water heater circuit breaker and still had the problem. When I disconnected the neutral feed from the heater element the GFI breaker stopped tripping. The heater circuit was indeed energized from the neutral side and the leakage current from the neutral found its way to ground and the GFI breaker detected the imbalance and tripped. 100 foot extension cord may have aggravated the imbalance?
__________________
2008 Springdale 266RELL
2007 Silverado 2500HD crew cab short bed
Bostongone is offline   Reply With Quote
Old 02-20-2021, 05:06 PM   #46
Steveo57
Senior Member
 
Join Date: Dec 2017
Location: Lisbon
Posts: 551
Quote:
Originally Posted by Bostongone View Post
I had the identical problem with the heater element in my trailer several years ago. GFI house breaker would trip every time. Turned off water heater circuit breaker and still had the problem. When I disconnected the neutral feed from the heater element the GFI breaker stopped tripping. The heater circuit was indeed energized from the neutral side and the leakage current from the neutral found its way to ground and the GFI breaker detected the imbalance and tripped. 100 foot extension cord may have aggravated the imbalance?
Yep. If the element is grounded out then the neutrals and grounds are effectively bonded together in the trailer. So the neutral return path now has a parallel path for some of the current to return on. That causes the GFCI outlet to sense the ground neutral fault and trip even with the breaker to the water heater off.
__________________
2018 Keystone Cougar 22RBS
2020 Ford F-350 XLT SC SRW 6.7l Powerstroke.
Steveo57 is offline   Reply With Quote
Reply

Tags
electrical, electrical problem, electrical problems


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 06:48 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.