I have attempted with all breakers off and it still trips.
If you have turned off all of the breakers in the trailer including the main breakers and you've also tried different cords then that would point to a problem with the receptacle on the trailer or the wiring from the receptacle to the breaker panel. Did you try just plugging in the dog bone by itself?
__________________
2018 Keystone Cougar 22RBS
2020 Ford F-350 XLT SC SRW 6.7l Powerstroke.
Steveo57 is offline   Reply With Quote
Old 02-04-2021, 08:53 PM   #22
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,981
Agree. If all the power center breakers INCLUDING THE MAIN BREAKER are turned off and the problem still exists, it's either the shore power cord, the twist lock connector on the trailer or the outlet you're plugging into.

I'd first use a "plain extension cord" and plug into the outlet just to see if it will trip the GFCI.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is online now   Reply With Quote
Old 02-05-2021, 11:16 AM   #23
BAMA4K
Junior Member
 
Join Date: Nov 2020
Location: Troy
Posts: 17
So problem solved. I had to disconnect all the wiring off the water heater element. As soon as I did I was able to connect up with breakers on and GFI did not trip. Thanks to everyone for all the help and feed back.
BAMA4K is offline   Reply With Quote
Old 02-05-2021, 12:09 PM   #24
sourdough
Site Team
 
Join Date: Feb 2014
Location: W. Texas
Posts: 17,671
Quote:
Originally Posted by BAMA4K View Post
So problem solved. I had to disconnect all the wiring off the water heater element. As soon as I did I was able to connect up with breakers on and GFI did not trip. Thanks to everyone for all the help and feed back.

Thanks for posting your progress but I think I'm confused. In your first post you said all the breakers were off and the wiring was disconnected from the water heater?? The solution was to disconnect the wiring from the heating element? That heating element should be controlled by a breaker eliminating the need to unwire it. What kind of configuration do you have that requires unwiring the heating element in a water heater in addition to throwing all breakers?
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
sourdough is offline   Reply With Quote
Old 02-05-2021, 12:31 PM   #25
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
It is a well-known fact that some GFI outlets don't play nice if plugged in series with another GFI outlet. Trip all the GFI outlet's within your RV. Or turn off the circuit breakers labeled GFI in the breaker box. Then plug in a see what happens. Let us know.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-05-2021, 01:17 PM   #26
BAMA4K
Junior Member
 
Join Date: Nov 2020
Location: Troy
Posts: 17
All breakers were off. Apparently the heating element grounds out the plug. Not sure if this is all trailers but it is the case with my Avalanche. I have new element ordered and will change out tomorrow and let y’all know it issue in 100% fixed.
BAMA4K is offline   Reply With Quote
Old 02-05-2021, 01:31 PM   #27
LHaven
Senior Member
 
LHaven's Avatar
 
Join Date: Feb 2019
Location: Wickenburg
Posts: 3,304
Quote:
Originally Posted by BAMA4K View Post
All breakers were off. Apparently the heating element grounds out the plug. Not sure if this is all trailers but it is the case with my Avalanche. I have new element ordered and will change out tomorrow and let y’all know it issue in 100% fixed.
If your heating element leaks shore power with all breakers off, you have a serious and potentially dangerous wiring problem. Hie thee to an electrician. Your problem is not in the element, it's in whatever is routing power to the element despite the breaker being off.
__________________
2019 Cougar 26RBSWE
2019 Ford F-250
LHaven is offline   Reply With Quote
Old 02-05-2021, 02:17 PM   #28
ChuckS
Senior Member
 
ChuckS's Avatar
 
Join Date: Mar 2014
Location: Mountain Home, Idaho
Posts: 3,009
Looking at what Trekwood shows for water heater yours is Suburban with INSIDE switch (12 volt relay) that is inside the junction box for the 120 VAC power to the heating element.

If you haven’t looked inside that junction box Id suggest taking the time to at least take a peak... a shorted (unusual) heating element shouldn’t have caused that issue... very rare for element to short out..usual fail is it Opens Up...

If you don’t have an inside switch for electric mode on your water heater than I’m still quite puzzled at your fail issue

https://www.trekwood.com/products/12...ay-Single-Pack
Attached Thumbnails
Click image for larger version

Name:	DB156703-97F8-4AF3-9812-079EA7BFD80D.jpeg
Views:	104
Size:	52.2 KB
ID:	31861  
__________________


2007 GMC Classic club cab 4x4 Duramax LBZ
2014 Alpine 3010 RE. 34 foot fifth wheel
ChuckS is offline   Reply With Quote
Old 02-05-2021, 03:18 PM   #29
sourdough
Site Team
 
Join Date: Feb 2014
Location: W. Texas
Posts: 17,671
Quote:
Originally Posted by BAMA4K View Post
All breakers were off. Apparently the heating element grounds out the plug. Not sure if this is all trailers but it is the case with my Avalanche. I have new element ordered and will change out tomorrow and let y’all know it issue in 100% fixed.
As others have said, something is definitely wrong. I have the 12 gal. Suburban water heater as I assume you do. That element should never be hot with the breaker thrown...and then you have the switch on the heater that is another "failsafe". With the element disconnected take a meter and read both sides on the ohm scale. Should be in the 10 ohm range as I recall, I figure yours is good. If not it's open and bad which I doubt. Then on the ohm scale read between one post of the element and ground; it should read nothing, which I figure it will. If those things read like that there is something seriously wrong, if not you will have to investigate further.

This is from memory but that switch on the side of the heater only controls the power to the element; the breaker controls the power to that switch via the relay ChuckS mentioned. My 120vac fried going to the water heater. Fried the switch (check it, mine was welded together) but still had no power - I am sure it is the relay Chuck mentioned but I'm letting warranty cover it when I get back. I turned off the breaker and there is no power at all to the water heater or element and I just run on LP.

Look into that closely because that element should not be throwing a breaker, gfci or not, with the trailer breaker off that feeds the water heater.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
sourdough is offline   Reply With Quote
Old 02-05-2021, 04:59 PM   #30
Customer1
Senior Member
 
Join Date: May 2019
Location: NE Ohio
Posts: 503
If neutral and ground are bonded, it can trip a GFCI even if the individual circuit isn't energized.
__________________
2018 Cougar 26RBS
2016 Chevrolet 3500DRW D/A
Customer1 is offline   Reply With Quote
Old 02-05-2021, 07:43 PM   #31
LHaven
Senior Member
 
LHaven's Avatar
 
Join Date: Feb 2019
Location: Wickenburg
Posts: 3,304
Quote:
Originally Posted by Customer1 View Post
If neutral and ground are bonded, it can trip a GFCI even if the individual circuit isn't energized.
That's true... if power is present to return over those conductors. If no power is being drawn anywhere in the rig (which is what you should see when all the interior breakers are off), the GFCI shouldn't even be able to detect that short. I agree that if any breaker, anywhere in the rig, is energized, and a neutral-ground are bonded anywhere else in the rig, you'll see it pop. But that could be anywhere in the rig, just checking the water heater won't necessarily find it.
__________________
2019 Cougar 26RBSWE
2019 Ford F-250
LHaven is offline   Reply With Quote
Old 02-06-2021, 04:06 PM   #32
Frank G
Senior Member
 
Frank G's Avatar
 
Join Date: Feb 2017
Location: Dade City
Posts: 1,039
The electrical panel in a RV is considered a sub-panel, there is no neutral to ground bonding in this panel. The bonding is done at the shore power panel.

If the power is off to a compromised water heater element there is the possibility that a bonding has occurred between the neutral side and the case ground thus creating a unbalance to the shore power GFIC.
__________________
2021 Surveyor Legend 19rble
2017 Laredo 325RL
Travelers Rest Resort
www.travelersrestresort.com
Frank G is offline   Reply With Quote
Old 02-06-2021, 04:44 PM   #33
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
Quote:
Originally Posted by Frank G View Post
The electrical panel in a RV is considered a sub-panel, there is no neutral to ground bonding in this panel. The bonding is done at the shore power panel.

If the power is off to a compromised water heater element there is the possibility that a bonding has occurred between the neutral side and the case ground thus creating a unbalance to the shore power GFIC.

the shore power Ped is also a sub panel. The bonding is done at the park service entrance panel.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-11-2021, 08:20 AM   #34
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
It is a well-known fact that some GFI outlets do not play nice with 2 GFI's in series. Go into your RV and turn off the one or two GFI circuits that are there. Come back and tell us the results.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-11-2021, 09:01 AM   #35
Steveo57
Senior Member
 
Join Date: Dec 2017
Location: Lisbon
Posts: 551
Quote:
Originally Posted by cavie View Post
It is a well-known fact that some GFI outlets do not play nice with 2 GFI's in series. Go into your RV and turn off the one or two GFI circuits that are there. Come back and tell us the results.
It's a well known fact that that well known fact is in fact not a fact.
__________________
2018 Keystone Cougar 22RBS
2020 Ford F-350 XLT SC SRW 6.7l Powerstroke.
Steveo57 is offline   Reply With Quote
Old 02-11-2021, 10:01 AM   #36
cavie
Senior Member
 
cavie's Avatar
 
Join Date: Oct 2020
Location: Port Charlotte
Posts: 240
Quote:
Originally Posted by Steveo57 View Post
It's a well known fact that that well known fact is in fact not a fact.
I am a master electrician. I own two trailers. 9 years different is age. I proved it to myself with them sitting side by side.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 02-11-2021, 10:38 AM   #37
Yvon Royer
Junior Member
 
Join Date: Apr 2016
Location: Delta, BC
Posts: 10
Quote:
Originally Posted by BAMA4K View Post
I have a 2020 Keystone Avalanche. When I plugged into GFI it trips. I have turned off all breakers, disconnected batteries and unhooked wiring to water heater and it still trips breaker. Electrician came out and checked circuit and said all is good. Any suggestions or additional things I can check before hauling it to a dealer? Oh and I tried different cords from trailer to Plug.
Your first step should be to locate your fuse panel and to turn all AC breakers off then check if the GFCI still trips. If it does not, you can switch them on one at a time until you find the culprit circuit. A common one is the water heater especially if you forgot to fill it with water before turning the electrical heater on; that one is guaranteed to trip a GFCI because the heater element has cracked and live parts are exposed to the water.

If you still trip the GFCI with all circuit breakers off, you can start looking upstream of your AC panel towards the plug.
__________________
Yvon Royer

2005 Cougar 285 EFS Fifth Wheel
2012 RAM 3500 Diesel 6.7 L
Andersen Ultimate Hitch
Yvon Royer is offline   Reply With Quote
Old 02-11-2021, 12:03 PM   #38
bigrockk
Member
 
Join Date: Jul 2010
Location: Wpg
Posts: 51
Quote:
Originally Posted by BAMA4K View Post
So problem solved. I had to disconnect all the wiring off the water heater element. As soon as I did I was able to connect up with breakers on and GFI did not trip. Thanks to everyone for all the help and feed back.
Despite all the feedback to the contrary you nailed it and found your problem. You will have to replace your water heater element and make sure it is turned off until the tank is full to avoid a repeat of this problem.

The GFCI tripping even though you had the breaker off is quite normal if the water heater electric element has shorted to ground. Shutting the breaker off only isolates the "hot" wire from the element but not the "neutral" wire.

Grounds and neutrals must be isolated from each other, if not it will cause the GFCI to trip and this is normal. The GFCI was just doing it's job, glad you got it figured out!
bigrockk is offline   Reply With Quote
Old 02-11-2021, 04:34 PM   #39
rburckhart
Member
 
Join Date: Dec 2009
Location: Williston
Posts: 32
Bet you have a short

I had this same problem with an older 5th wheel we had; as soon as I plugged it in, the GFCI tripped. Pulled my hair out until I found out the water heater electric element was shorted. Disconnected the wires and that solved the problem.
__________________
Dick & Vicki
Williston, FL
Cougar 28 SGS
2013 F-250 SD 6.2 gas
Siberian Husky named "Willow"
rburckhart is offline   Reply With Quote
Old 02-19-2021, 10:33 PM   #40
monitormix
Junior Member
 
monitormix's Avatar
 
Join Date: Jan 2016
Location: Sacramento, CA
Posts: 24
Quote:
Originally Posted by LHaven View Post
Am I missing something? OP says he plugged his trailer into a GFCI receptacle, meaning a 15A or 20A receptacle, since nothing larger comes in GFCI. That requires an adapter.
I thought it was common knowledge that trailer adapters are just flat not compatible with GFCI outlets. I'm surprised this is news to the storage facility.
Most newer commercial spaces have GFP listed breakers on the main disconnect. They are typically between 25-100ma based on the electrical engineers call out. You can purchase GFCI listed breakers to 50A single phase. Usually for hot tubs. All residential GFCI are listed to trip at 6ma. It doesn't take much to fault out.
__________________
2016 Cougar X-Lite 26RLS
2006 Ram 2500 5.9Cummins QCLB w/MODS
monitormix is offline   Reply With Quote
Reply

Tags
electrical, electrical problem, electrical problems


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 07:22 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.