|
|
04-11-2023, 04:37 PM
|
#21
|
Junior Member
Join Date: Mar 2023
Location: Colora
Posts: 15
|
Quote:
Originally Posted by jasin1
may be a loose neutral wire ….for instance if you touch the pos lead of tester on the breaker hot wire and touch the other on the neutral buss and hit a loose wire for that breaker you may be pushing it tighter and voila you have a good hot and neutral connection now for that circuit..that would explain the spark also
make sure the breaker is snapped in tight also to the buss bar
|
I checked all the wires I did find a couple loose on the negative bus tightened everything replaced the breaker same results I am going to try and attach a photo so y’all can see what I mean red lead on breaker black lead on negative bus and I have power
|
|
|
04-11-2023, 04:54 PM
|
#22
|
Senior Member
Join Date: Aug 2020
Location: Upper Chesapeake Bay
Posts: 4,841
|
Quote:
Originally Posted by Jmclain21917
I checked all the wires I did find a couple loose on the negative bus tightened everything replaced the breaker same results I am going to try and attach a photo so y’all can see what I mean red lead on breaker black lead on negative bus and I have power
|
i think the black lead is not doing anything..i agree with bad breaker. i think pushing on the breaker terminal is making a connection inside the bad breaker by pressure… i think a reverse polarity issue would trip the pedestal breaker…so ruling that out…replace the breaker or swap it with another one of the same amperage inside the panel just to check it
__________________
2020 Cougar 315 RLS
2020 Ram 3500 6.7HO 4.10 Dually Aisin
|
|
|
04-11-2023, 05:29 PM
|
#23
|
Senior Member
Join Date: Jul 2013
Location: Box Elder
Posts: 2,910
|
That bus bar is your ground bus, and should not be a current carrying bar. I see the black insulated wire and the bare portion attached to the bar appears to have been hot, the blackened copper wire. It really looks like things may have been wired incorrectly.
__________________
Bob & Becky
2012 3402 Montana
2012 Chevy 2500HD D/A CC
|
|
|
04-11-2023, 05:42 PM
|
#24
|
Junior Member
Join Date: Mar 2023
Location: Colora
Posts: 15
|
Quote:
Originally Posted by bobbecky
That bus bar is your ground bus, and should not be a current carrying bar. I see the black insulated wire and the bare portion attached to the bar appears to have been hot, the blackened copper wire. It really looks like things may have been wired incorrectly.
|
The way it is wired is how it was when I purchased the trailer, everything was working properly until the battery ne night no changes the power went out , so I am at a complete loss
|
|
|
04-11-2023, 05:43 PM
|
#25
|
Junior Member
Join Date: Mar 2023
Location: Colora
Posts: 15
|
Quote:
Originally Posted by jasin1
i think the black lead is not doing anything..i agree with bad breaker. i think pushing on the breaker terminal is making a connection inside the bad breaker by pressure… i think a reverse polarity issue would trip the pedestal breaker…so ruling that out…replace the breaker or swap it with another one of the same amperage inside the panel just to check it
|
If I take the he black lead off power goes out.
|
|
|
04-11-2023, 05:48 PM
|
#26
|
Junior Member
Join Date: Mar 2023
Location: Colora
Posts: 15
|
Quote:
Originally Posted by bobbecky
That bus bar is your ground bus, and should not be a current carrying bar. I see the black insulated wire and the bare portion attached to the bar appears to have been hot, the blackened copper wire. It really looks like things may have been wired incorrectly.
|
I don’t see a blackened copper wire.
|
|
|
04-11-2023, 05:50 PM
|
#27
|
Junior Member
Join Date: Mar 2023
Location: Colora
Posts: 15
|
Quote:
Originally Posted by bobbecky
That bus bar is your ground bus, and should not be a current carrying bar. I see the black insulated wire and the bare portion attached to the bar appears to have been hot, the blackened copper wire. It really looks like things may have been wired incorrectly.
|
I see it in the pic now, that’s a shadow none of the copper is blackened.
|
|
|
04-11-2023, 05:51 PM
|
#28
|
Senior Member
Join Date: Aug 2020
Location: Upper Chesapeake Bay
Posts: 4,841
|
i’d call an electrician..i wouldn’t try and figure it out anymore…what you describe doesn’t really make sense… you shouldn’t be able to complete a circuit with the meter set on voltage or you would short out the meter when doing a voltage test (meaning that you would be sending 120 volts to ground if that were the case)
__________________
2020 Cougar 315 RLS
2020 Ram 3500 6.7HO 4.10 Dually Aisin
|
|
|
04-11-2023, 05:54 PM
|
#29
|
Junior Member
Join Date: Mar 2023
Location: Colora
Posts: 15
|
Quote:
Originally Posted by jasin1
i’d call an electrician..i wouldn’t try and figure it out anymore…what you describe doesn’t really make sense… you shouldn’t be able to complete a circuit with the meter set on voltage or you would short out the meter when doing a voltage test
|
It makes no sense at all
|
|
|
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Threads |
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
|
All times are GMT -8. The time now is 07:01 PM.