Quote:
Originally Posted by onfire
3000is Honda 24 amp continuous, 30 map peak gen.
With every breaker turned off, all lights off....nothing but the 14 amp AC unit running...when the compressor activates, the converter shuts the power off.
Generator starts and runs the ac fine direct wired...with room to spare..
Worst case I can wire the ac directly to one of the generators extra 20 amp plugs and bypass the converter.
|
is the 3000 in eco mode when the AC starts?? if so it may not be recovering fast enough and the voltage sags on startup. Also the 3000 is 23A rated continous, 25A max, not 30A max. That only gives you a spare 8A or so once the AC starts, and really not much at all to spare when the AC is trying to start.
Also, if every breaker is turned off, then the converter is also off, since it is tied to one of the breakers. I still believe that the converter is charging the batteries, and/or supplying power to other 12V loads enough to make the 3000is struggle. Or, even if not supplying any load, it sees the power go below 105V and shuts off. Inrush current for the AC is not 14A, it can be as high as 50-60A for a second or so, especially at higher temperatures. That plus any other load is causing the generator to momentarily come close to overload. that is why the generator voltage is dropping to 104V. These inverter generators are not very forgiving for overload, nor are they very good for supplying surge current needs for motor loads. the output voltage drops like a rock as you get anywhere near max rated load. And if the 3000is is like other hondas, the 25A peak is for a second or less, not the 30 minutes honda claims.
when you stay "direct wired" what do you mean??
and when you say the converter "shuts down all power" for 30 seconds, what happens. If the converter output goes to 0, the trailer batteries should easily supply keep all 12V accessories running and you shouldn't even notice the converter momentarily shutting down.
Like I mentioned in the previous post, I have honda 2000's paralleled. they can provide more current than a 3000is, for continous(27A) and max (33). Starting the AC at high temps with any other signficant load (>5A) if the generators are not in eco mode will cause the voltage to sag down below 105V momentarily until the throttle catches up. In fact it will trip out my EMS system in eco mode even with no other loads if I don't bypass the EMS.
If they are not in eco mode, then voltage stays up and the EMS doesn't trip out even with a few other small loads.