Quote:
Originally Posted by brandonmangan
I appreciate the soft start recommendations and have considered them in the past, but we have two 15K ACs, and they both push north of 15 AMPS full-time while the compressor is on. I decided I wasn't going to spend $600 on something that would give me razor-thin margins (if it worked at all). The screenshots from my EMS were with nothing but ACs running while using the adapter. They use the same amount of power when running off standard 50 AMP.
|
Keep in mind that it isn't the running amps that you have to worry about, it is the starting amps that is the issue. Depending on your AC, your fan and compressor can start at the same time and easily draw close to 28A. Multiply that times 2 units and you could easily unintentionally stress/overload something. Unfortunately, that something is often the electronics in the AC unit.
With a soft start, my 15k Furrion starts the air circulation fan first, which draws 3.4A, then the condenser fan starts adding another 3.4A, then the compressor kicks in with a total system draw peaking at about 15A (compared to almost 29A without the soft start) before settling down to a running draw of 14.3A continuous for all three components running together. I am not trying to sell you a soft start, but it costs a heck of a lot less than a major AC repair.