Ac cycles, trips generator

Just bought a westinghouse igen 4500 for our 28 foot Hideout with a 13.5k ac. Generator will run the air just fine for 15 minutes or so then the ac sounds like it shuts off then comes back on and when it does that it trips the overload on the generator. Temperature has not come down to thermostat setting yet so not sure why it turns off then right back on. Anyone else seen this issue? What would be some possible fixes?
RNTFREE is offline   Reply With Quote
Old 07-30-2021, 05:16 PM   #2
NH_Bulldog
Senior Member
 
NH_Bulldog's Avatar
 
Join Date: Apr 2019
Location: Henniker
Posts: 1,978
That 4,500 watt generator runs3,700 watts continuous, but should be plenty if you have a 13.5 AC. I read about Westinghouse issues when I was generator shopping so I bought a Generac 3,000i and it powers mine just fine (13.5k Dometic Brisk Aire II) with no issues. Make sure you have all other loads off like water heater, fridge, etc. Also factors like ambient temperature, and altitude come into play. If it continues to be an issue, a soft start for the AC unit might help
__________________
Rob & Amy
2019 Passport 240BH SL (current)
2024 Cougar 29BHL (on order, due early May)
2022 Ford F250 7.3L Godzilla Crew Cab 4x4
NH_Bulldog is offline   Reply With Quote
Old 07-30-2021, 05:17 PM   #3
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,772
Does the A/C do the same thing on shore power?

It may be the heat causing the A/C compressor to overload and it simply can't keep up with the pressure requirement to push the refrigerant without overheating and when it cycles, the head pressure is just too great so the amp demand to start the compressor "kicks the generator out".

If it works on shore power, focus on the generator. if it does the same on generator and shore power, focus on the air conditioner.....

Page, AZ is around 4100' altitude. That's about 600' higher than the "maximum full power altitude" for most generators.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 07-30-2021, 05:24 PM   #4
RNTFREE
Junior Member
 
RNTFREE's Avatar
 
Join Date: Jul 2021
Location: Page
Posts: 7
Quote:
Originally Posted by JRTJH View Post
Does the A/C do the same thing on shore power?

It may be the heat causing the A/C compressor to overload and it simply can't keep up with the pressure requirement to push the refrigerant without overheating and when it cycles, the head pressure is just too great so the amp demand to start the compressor "kicks the generator out".

If it works on shore power, focus on the generator. if it does the same on generator and shore power, focus on the air conditioner.....

Page, AZ is around 4100' altitude. That's about 600' higher than the "maximum full power altitude" for most generators.
It does do the same cycling thing on shore power but never has popped a breaker, even on a 30 Amp hookup. It just cycles and keeps working. I was thinking the same thing, restarting against pressure would spike the amps, not sure why it cycles though.
RNTFREE is offline   Reply With Quote
Old 07-30-2021, 05:39 PM   #5
chuckster57
Site Team
 
chuckster57's Avatar
 
Join Date: Jul 2014
Location: Modesto
Posts: 20,203
Could be the heat. Try running the AC late night/early morning when ambient temps are below about 90 and see if it does the same thing.
__________________

2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.

Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
chuckster57 is offline   Reply With Quote
Old 07-30-2021, 05:54 PM   #6
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,772
Quote:
Originally Posted by RNTFREE View Post
It does do the same cycling thing on shore power but never has popped a breaker, even on a 30 Amp hookup. It just cycles and keeps working. I was thinking the same thing, restarting against pressure would spike the amps, not sure why it cycles though.
The Air Conditioner is on its own 20 amp circuit breaker, so that "should" open before the campground 30 amp breaker (depending on what other loads you have drawing power inside the trailer)...

The compressor has a thermal overload built into it. If that thermal device senses the compressor overheating, it will "cycle off" until the compressor cools and the thermal overload resets. So, the cycling may be a symptom of the compressor overheating and shutting down to protect itself from burning up. Then, when it does "cycle on again" the head pressure is just too great for the "surge wattage in the generator"...

I'd guess that if the air conditioner is not tripping its 20 amp breaker and it's working on 30 amps from shore power, then your generator may be "sensing a pending load above the continuous rating and shutting down to protect itself... That would probably be normal, not a "failure of the generator"...

My "long distance guess" is an overworked 13.5K a/c that has a compressor that's giving it's heart to try to keep you cool and just can't keep up with the temperature.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 07-30-2021, 06:27 PM   #7
jasin1
Senior Member
 
jasin1's Avatar
 
Join Date: Aug 2020
Location: Upper Chesapeake Bay
Posts: 4,792
Quote:
Originally Posted by RNTFREE View Post
It does do the same cycling thing on shore power but never has popped a breaker, even on a 30 Amp hookup. It just cycles and keeps working. I was thinking the same thing, restarting against pressure would spike the amps, not sure why it cycles though.
How old is the trailer? Have you ever cleaned the air conditioning condenser coil on the roof? Maybe watch a YouTube video on cleaning the coil.
You may try running the fan on high all the time and see if that helps with the generator kicking out..the fan motor is only minimal amps but even 1 amp may be the one pushing it over the edge..one less motor that has to start from a dead stop
__________________
2020 Cougar 315 RLS
2020 Ram 3500 6.7HO 4.10 Dually Aisin
jasin1 is offline   Reply With Quote
Old 07-30-2021, 07:14 PM   #8
RNTFREE
Junior Member
 
RNTFREE's Avatar
 
Join Date: Jul 2021
Location: Page
Posts: 7
Quote:
Originally Posted by jasin1 View Post
How old is the trailer? Have you ever cleaned the air conditioning condenser coil on the roof? Maybe watch a YouTube video on cleaning the coil.
You may try running the fan on high all the time and see if that helps with the generator kicking out..the fan motor is only minimal amps but even 1 amp may be the one pushing it over the edge..one less motor that has to start from a dead stop
Trailer is a 2020, had been sitting in a dirt storage lot on Nellis air force base when we got it so it's possible there's dirt/ sand in things. I'll check that out next time I'm up there.
RNTFREE is offline   Reply With Quote
Reply

Tags
generator

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 01:01 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.