No generator power transfering 2018 Raptor
Good morning I am new to the forum idea but after reading I see everyone is super helpful so thank you in advance. Keeping it simple I have a new 2018 raptor tow hauler. Generator starts with no issue. Generator makes power not problem. Transfer switch transfers no problem. Power leaves transfer switch no problem. PROBLEM once the power leaves the transfer switch it is lost. I do not have any power getting to anything in the camper. Upon delivery they ran the generator but I assumed it was good but I never actually checked if powered anything up. I noticed it right away once home. The dealer came to my house and changed the transfer switch but this did not work. Does anyone have any idea what is going on. Camper is at dealer currently and they seem to be lost as well. Thank you
|
|
|
03-12-2019, 06:22 AM
|
#2
|
Site Team
Join Date: Jul 2014
Location: Modesto
Posts: 20,339
|
Welcome to the forum!
How did you verify voltage is in fact getting to the transfer switch and is in fact coming from the transfer switch to the breaker panel?
__________________
2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.
Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
|
|
|
03-12-2019, 06:43 AM
|
#3
|
Junior Member
Join Date: Mar 2019
Location: wappingers falls
Posts: 14
|
I used my electrical meter and checked on the line voltage in on the transfer switch. I also checked the load side leaving. Both have power. I shut the generator off and I lose the power. When I open up the circuit breaker panel the line side in to the main breaker has not power when I have power on load side of transfer switch. I almost feel like there is another switch somewhere that is off?
|
|
|
03-12-2019, 08:17 AM
|
#4
|
Site Team
Join Date: Mar 2011
Location: Gaylord
Posts: 26,995
|
Do you have an EMS inline from the transfer switch to the circuit breaker panel? If so, if the generator has a "floating ground" the EMS may not be allowing power to pass through to the circuit breakers.
__________________
John
2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
|
|
|
03-12-2019, 08:32 AM
|
#5
|
Junior Member
Join Date: Mar 2019
Location: wappingers falls
Posts: 14
|
Done mind me but EMS? What is that. When I trace the wires out, the wires from the generator go direct to transfer switch. When leaving switch they disappear into the finished part of the camper. I have been unsuccessful in getting any information from Keystone on anything in between. I have been thinking that a bad ground may be the issue just have not found one
|
|
|
03-12-2019, 08:44 AM
|
#6
|
Senior Member
Join Date: Oct 2016
Location: Sherman
Posts: 326
|
If you have 50 amp shore power then the wiring from the output of the transfer switch to the panel is good. Do you have a 30 amp generator? If so then it is possibly powering only half of the breaker panel.
__________________
2017 Alpine 3401RS,Titan Disc brakes,Morryde SRE 4000, 2016 Ram 3500HD Laramie SRW,LWB,4X4, Aisin transmission
|
|
|
03-12-2019, 09:59 AM
|
#7
|
Junior Member
Join Date: Mar 2019
Location: wappingers falls
Posts: 14
|
I so have shore power. Generator is 50 amps as well. I checked each circuit out of the panel as I thought maybe the same thing. Dealer is having the same issue trying to figure it all out.
|
|
|
03-12-2019, 10:07 AM
|
#8
|
Member
Join Date: Jan 2016
Location: Jerome
Posts: 61
|
On our Carbon, shore power will is 120/240 volts. (Measuring 240 volt across the main breaker) When on generator power, it is 120 volt only. (Main breaker has 120 volt to both sides of main breaker measuring to neutral wire)
Are you measuring between lines to the main breaker? If so, measure from each wire of main breaker to neutral (or ground) and see if you get 120 volts.
Hope this helps!
__________________
2020 Voltage 3635
2018 Ford F-350 DRW
Lots of toys!
|
|
|
03-12-2019, 10:20 AM
|
#9
|
Junior Member
Join Date: Mar 2019
Location: wappingers falls
Posts: 14
|
I will take a look at that thank you for the input
|
|
|
03-12-2019, 10:20 AM
|
#10
|
Senior Member
Join Date: Oct 2016
Location: Sherman
Posts: 326
|
It sounds like you have an EMS between the transfer switch and the breaker panel. The EMS is passing power when on shore power but for some reason it does not like the generator and is shutting the power off.
__________________
2017 Alpine 3401RS,Titan Disc brakes,Morryde SRE 4000, 2016 Ram 3500HD Laramie SRW,LWB,4X4, Aisin transmission
|
|
|
03-12-2019, 11:10 AM
|
#11
|
Site Team
Join Date: Mar 2011
Location: Gaylord
Posts: 26,995
|
Quote:
Originally Posted by Ddubya
It sounds like you have an EMS between the transfer switch and the breaker panel. The EMS is passing power when on shore power but for some reason it does not like the generator and is shutting the power off.
|
That would likely be a "floating ground" on the generator output.....
__________________
John
2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
|
|
|
03-12-2019, 11:35 AM
|
#12
|
Junior Member
Join Date: Mar 2019
Location: wappingers falls
Posts: 14
|
Excuse my ignorance in this What is a EMS
|
|
|
03-12-2019, 11:46 AM
|
#13
|
Senior Member
Join Date: May 2018
Location: Rochester, NY
Posts: 286
|
Quote:
Originally Posted by Raptor 18
Excuse my ignorance in this What is a EMS
|
Electrical Management System
__________________
2018 Springdale Summerland Series 3030BH
2018 Ram 2500 HD 6.4L Hemi Big Horn 4x4
|
|
|
03-12-2019, 12:00 PM
|
#14
|
Site Team
Join Date: Mar 2011
Location: Gaylord
Posts: 26,995
|
Quote:
Originally Posted by Raptor 18
Excuse my ignorance in this What is a EMS
|
Go here to read about one brand of EMS: https://www.progressiveindustries.net/ems-lchw50
Most are comparable in what they monitor/protect and how they do it.
If you have a floating ground or phase reversed input, AND an EMS, chances are with shore power correctly phased and grounded, that part will work (as yours does) but with a problem in how the generator is connected to the trailer input, the EMS would "shut it down" (as yours does) .....
__________________
John
2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
|
|
|
03-13-2019, 06:25 AM
|
#15
|
Senior Member
Join Date: Aug 2017
Location: Lafayette
Posts: 1,068
|
I doubt especially since the OP didn't know what an EMS was that he had requested one to be installed, they don't come standard on the Raptors anyway. It sounds to me like one breaker is tripped somewhere, maybe on the gen itself or in the panel. GFI Could be bad also though not sure how many 110 circuits actually run through it. Are you not getting any 110 power, microwave or outlets??
__________________
2015 Ram,3500,Dually,B&W,4.10s,Aisin,Limited,Silver
2018 Raptor,428SP w/full body paint
2012 Harley, Ultra Limited
|
|
|
03-13-2019, 06:33 AM
|
#16
|
Senior Member
Join Date: Nov 2017
Location: Mico, TX
Posts: 7,462
|
The appliances won't be on the GFI circuit which is normally 15A and only supports ONE circuit where the outlets supported by the GFI outlet are run in series. One goes, they all go. The microwave will have its own breaker and an outlet up in the box where the microwave is located or right next to it but hidden. Don't know if the refrigerator is on the GFI circuit as well but it might be as I can't recall off the top of my head.
__________________
wiredgeorge Mico TX
2006 F350 CC 4WD 6.0L
2002 Keystone Cougar 278
2006 GL1800 Roadsmith Trike
|
|
|
|