An Open Letter To Keystone

I also sent this to their customer no-service department via the link on their website:

I recently completed the addition of a second 30A service to my 277RL, the purpose being to better balance the loads and get an even distribution of power utilizing a splitter on a 50A outlet. Since I'm a marine electrician and air conditioner service center, this was quite an easy project, only made difficult by two factors. One, the unorthodox method of randomly ganging appliances on a circuit breaker that shows no indication of everything that is attached to it. I found wall outlets serviced by circuit breakers that I would have never suspected or thought to look for.The other is the almost impossibility of separating the circuits that needed to be re-routed to the appropriate circuit breaker due to all of the connections and terminations being done in the ceiling.

I can certainly understand why one would not want all of the wall outlets to be fed by one common circuit breaker marked."Outlets" That practice would certainly reduce confusion for the knowledgeable DIYer as well as providing a margin of safety in the event of the need to kill power in a critical situation and in general, just make too much sense.
I do find it interesting that you refuse to release any electrical information or diagrams, citing a concern for customer safety, but you seem to be perfectly at ease in the doing electrical installations in a manner that is confusing to owners and creates possible hazardous conditions, however remote, by increasing the time it may take to shut off power to a device or outlet in an emergency situation.
As an enhancement to customer safety, you might consider labeling these "rogue" outlets as to which breaker actually controls them.
If your policy is in fact based on customer safety and not just as a CYA against product liability lawsuits, then perhaps those polices and the reasoning behind them warrant revisiting.
__________________
2011 Outback 277RL
2013 F250 XLT Crew Cab 6.2L

Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Old 04-10-2014, 11:26 AM   #2
SAABDOCTOR
Senior Member
 
SAABDOCTOR's Avatar
 
Join Date: Aug 2011
Location: WESTERN,CT
Posts: 2,095
Well Bob Maybe they think or that you should just shut off the main breaker. but that maybe pushing it. i do agree with you that the wire routing is at best insane they had both a/c units and my hot water heater on one breaker They must put some funny sugar in the company coffee pot!
__________________
BARNEY AND CHRISTINE
2010 MONTANA 3750FL
2005 DODGE 3500 DUALLY TD
2 RESCUE PUPS: SUSITNA AND CRYSTAL. RIP ALYESKA!
SAABDOCTOR is offline   Reply With Quote
Old 04-10-2014, 12:02 PM   #3
Bob Landry
Senior Member
 
Join Date: Jan 2011
Location: Austin, Tx
Posts: 1,910
Quote:
Originally Posted by SAABDOCTOR View Post
Well Bob Maybe they think or that you should just shut off the main breaker. but that maybe pushing it. i do agree with you that the wire routing is at best insane they had both a/c units and my hot water heater on one breaker They must put some funny sugar in the company coffee pot!
That's nuts. Even discounting the safety aspect of it, what happens when an owner stars getting nuisance trips at the breaker panel because the breaker is overloaded and he has no idea what to turn off to get it to stop tripping. It's hard for me to believe that in a tightly controlled(we hope) manufacturing environment, that the workers on the floor would just take it upon themselves to do stuff like this, so you can only hope that someday you will run across something as good as what they are smoking.

In my trailer, they ran #12 wire to the microwave outlet and put it on a 15A breaker, which is OK as far as wire rating goes, it just makes you think they use what ever happens to be in the parts box that day.
__________________
2011 Outback 277RL
2013 F250 XLT Crew Cab 6.2L

Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Old 04-16-2014, 07:59 AM   #4
Jeff_S
Junior Member
 
Jeff_S's Avatar
 
Join Date: Jul 2013
Location: Bend, OR
Posts: 17
Bob,
All the outlets in the living area of our 2014 Montana HC 318RE are on the same breaker! That is crazy to me. With regard to using #12 wire on a 15A breaker...they probably buy #12 in bulk so their install techs don't have to know anything about electricity. BTW, I'm told but can't yet confirm that the second optional A/C unit in the bedroom area is wired to the same leg of the 220 as the living room unit. If that is true, when and if I install the second unit they will be separated forthwith.

Jeff_S
__________________

2014 Montana High Country 318
1999 Ford F250, 7.3L Diesel
Banks Exhaust Brake,Trans Command,Trans Lock
Superchips CORTEX tuner
Jeff_S is offline   Reply With Quote
Old 04-16-2014, 08:07 AM   #5
canesfan
Senior Member
 
canesfan's Avatar
 
Join Date: Jan 2014
Location: Tidewater Area Virginia
Posts: 1,271
Quote:
Originally Posted by Jeff_S View Post
Bob,
All the outlets in the living area of our 2014 Montana HC 318RE are on the same breaker! That is crazy to me. With regard to using #12 wire on a 15A breaker...they probably buy #12 in bulk so their install techs don't have to know anything about electricity. BTW, I'm told but can't yet confirm that the second optional A/C unit in the bedroom area is wired to the same leg of the 220 as the living room unit. If that is true, when and if I install the second unit they will be separated forthwith.

Jeff_S
Is there an easy way for me to check this? I haven't had the chance to determine the need for the second AC, but I'd like to know beforehand what I may have to change.
__________________
2014 Raptor RP300MP w/ Rear Patio Party Deck, Folding Side Ladder, 6 Point Level Up, Carlisle Radial Trail HDs
2004 2500HD D/A CC SB - TTT Mirrors, Prodigy BC, 18K Pullrite Superglide, NEW Fuel Injectors 11/2015 (ouch)
canesfan is offline   Reply With Quote
Old 04-16-2014, 09:36 AM   #6
PARAPTOR
Site Team | Emeritus
 
PARAPTOR's Avatar
 
Join Date: Jan 2014
Location: Western PA
Posts: 2,732
Smile

Quote:
Originally Posted by canesfan View Post
Is there an easy way for me to check this? I haven't had the chance to determine the need for the second AC, but I'd like to know beforehand what I may have to change.
Well lets see, can imagine you smiling already, you can look at our power distribution panel labeling I assume AC1 and AC2. I think we share the same wf-8930/50 power distribution panel with a separate converter. As far as I can tell by the diagram the bus is just split and not alternating therefore breakers left of the 50 AMP main breaker are on one 120VAC side and breakers to the right side of the main on the other side. Ideally you want to try and balance the loads on each side of the 50 AMP service, meaning AC1 on one side and AC2 on the other. As far as checking if they are labeled correctly, well just have to start throwing breakers and checking what goes off for each one For our second pre-wired AC in Bedroom will have to check power in that box next to the opening.

40 degrees and not snowing so good sign
__________________
2013 RAPTOR 300MP w/Rear Patio Deck NO Folding Side Ladder
2013 Silverado 3500HD LTZ CC LB 4X4 DRW
Duramax 6.6L Turbo Diesel; Allison Trans
Reese 20K; Carlisle Radial Trail RH/HD; TPMS (12 Tires)

Veteran


PSU (GO LIONS)
PARAPTOR is offline   Reply With Quote
Old 04-16-2014, 09:58 AM   #7
canesfan
Senior Member
 
canesfan's Avatar
 
Join Date: Jan 2014
Location: Tidewater Area Virginia
Posts: 1,271
Quote:
Originally Posted by PARAPTOR View Post
As far as I can tell by the diagram the bus is just split and not alternating therefore breakers left of the 50 AMP main breaker are on one 120VAC side and breakers to the right side of the main on the other side. Ideally you want to try and balance the loads on each side of the 50 AMP service, meaning AC1 on one side and AC2 on the other.
Ok that makes sense, so it's probably not wired that way. I'll check it out later. It's 54 and sunny here.
__________________
2014 Raptor RP300MP w/ Rear Patio Party Deck, Folding Side Ladder, 6 Point Level Up, Carlisle Radial Trail HDs
2004 2500HD D/A CC SB - TTT Mirrors, Prodigy BC, 18K Pullrite Superglide, NEW Fuel Injectors 11/2015 (ouch)
canesfan is offline   Reply With Quote
Old 04-16-2014, 12:59 PM   #8
Bob Landry
Senior Member
 
Join Date: Jan 2011
Location: Austin, Tx
Posts: 1,910
Quote:
Originally Posted by Jeff_S View Post
Bob,
All the outlets in the living area of our 2014 Montana HC 318RE are on the same breaker! That is crazy to me. With regard to using #12 wire on a 15A breaker...they probably buy #12 in bulk so their install techs don't have to know anything about electricity. BTW, I'm told but can't yet confirm that the second optional A/C unit in the bedroom area is wired to the same leg of the 220 as the living room unit. If that is true, when and if I install the second unit they will be separated forthwith.

Jeff_S
That's not unusual and it's quite common in stick houses. The idea is that you are not going to have something in every outlet running at the same time. Even having the second AC on the same leg is OK as long as they are not on the same breaker, especially with 50A service. Two 15KBTU air conditioners are going to draw around 14A each running, and one of those is likely to be a smaller one. That leaves 22A of available power on that leg, which allows you to run quite a bit along with the two Acs. The idea is to split the loads as evenly as possible across the two legs, so it doesn't matter what is connected to what as long as it's reasonably balanced. That's with 50A. 30A is a different matter and it would be almost impossible to run two ACs on one leg unless everything else is shut off, and that's still iffy. Dual 30A gets a little better. I did that to my trailer, but I don't know of but a couple of other people who have done that. I chose to do it that way because of cost and the fact that my trailer is not set up for a 2nd AC unit
If I were able to add a second AC, then I would have done a 50A conversion.
__________________
2011 Outback 277RL
2013 F250 XLT Crew Cab 6.2L

Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Old 04-20-2014, 03:58 AM   #9
Bill & Deb
Senior Member
 
Join Date: Oct 2013
Location: Toronto
Posts: 120
Quote:
Originally Posted by Jeff_S View Post
Bob,
All the outlets in the living area of our 2014 Montana HC 318RE are on the same breaker! That is crazy to me. With regard to using #12 wire on a 15A breaker...they probably buy #12 in bulk so their install techs don't have to know anything about electricity. BTW, I'm told but can't yet confirm that the second optional A/C unit in the bedroom area is wired to the same leg of the 220 as the living room unit. If that is true, when and if I install the second unit they will be separated forthwith.

Jeff_S
Jeff

I think it's all about the cost of copper ! If they run a large number of the outlets on one breaker then they don't have to run another new feed from the panel therefore using more copper.

Bill
__________________
2014 Keystone Laredo 329RE
Mor/Ryde Pin Box
2002 Ford F250 SD with 7.3 PS
Pullrite Superglide 15K Hitch
Bill & Deb is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 01:12 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.