09-07-2022, 03:47 PM
|
#1
|
Senior Member
Join Date: Dec 2021
Location: Richmond
Posts: 339
|
RV Park Power Issues
I'm currently at an RV park that has poor power. I have a 30 amp hookup. My EMS shows 118 VAC until I load it with with 15 amps and then it shows 108 VAC. If I load any more amps the EMS drops the power connection. I mentioned this to the park admin and they say I need to turn off items in my RV. They don't get it, they need to supply 30 amps and 120 VAC. My neighbor at the RV park is now running her generator so that she can run her air conditioner. I've had this problem before at this park and they need to get the power company out here to investigate, but it will probably cost them. Others here are having power issues but they have dumb surge protectors and can't see what's going on and think they're running too much load. I'm paying for "full hookups" and would like for all of them to work.
__________________
Lee
2019 Keystone Passport GT Ultra Lite 2520RL, 7000lb GVW,
2015 F150 5.0, XLT/FX4, 3.55 Tow, 7000lb GVWR, 1829lb payload, 36 gal tank,
|
|
|
09-07-2022, 04:52 PM
|
#2
|
Senior Member
Join Date: Aug 2012
Location: Waco, Tx
Posts: 5,457
|
Quote:
Originally Posted by hlh1
I'm currently at an RV park that has poor power. I have a 30 amp hookup. My EMS shows 118 VAC until I load it with with 15 amps and then it shows 108 VAC. If I load any more amps the EMS drops the power connection. I mentioned this to the park admin and they say I need to turn off items in my RV. They don't get it, they need to supply 30 amps and 120 VAC. My neighbor at the RV park is now running her generator so that she can run her air conditioner. I've had this problem before at this park and they need to get the power company out here to investigate, but it will probably cost them. Others here are having power issues but they have dumb surge protectors and can't see what's going on and think they're running too much load. I'm paying for "full hookups" and would like for all of them to work.
|
There must be a reason that you stay, maybe they're a lot cheaper than the place down the road with 50amp services.
|
|
|
09-07-2022, 05:09 PM
|
#3
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 17,669
|
Your park is the cause of the problem I'm relatively sure. They have told you they don't care and you need to deal with it basically, now it's on you to live with it or get another park. Lots of those places out there; I'd would have been gone first go round.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
|
|
|
09-07-2022, 05:20 PM
|
#4
|
Senior Member
Join Date: May 2016
Location: South Jordan, Utah
Posts: 2,222
|
Too many people running hi amp appliances at the same time. It's hot, everybody wants to run the A/C. The park likely does not have sufficient service from the utility company to supply all the camp spaces with full power. Entire cities out west are experiencing the same problem with the current heat wave. I'm nosey, I'd wander around and see just what kind of service is coming in from the street to the park.
Right after I cranked up the generator and got the air working
__________________
2017 Cougar 279RKSWE
2007.5 Dodge Ram 2500 6.7 Cummins
Retirement Training Completed
I think the little voices in my head have started a chat group.
|
|
|
09-07-2022, 06:04 PM
|
#5
|
Senior Member
Join Date: Jul 2017
Location: Monroeville
Posts: 1,549
|
That's a terrible experience, I would definitely be looking for another park as soon as I could.
__________________
2014 Bullet Premier 29bh in Charocal
2019 Ram 2500 HD 4x4, CC, 6.4L
2011 Passport 2510RB (Sold)
|
|
|
09-07-2022, 06:32 PM
|
#6
|
Senior Member
Join Date: Dec 2021
Location: Richmond
Posts: 339
|
Quote:
Originally Posted by Canonman
Too many people running hi amp appliances at the same time. It's hot, everybody wants to run the A/C. The park likely does not have sufficient service from the utility company to supply all the camp spaces with full power. Entire cities out west are experiencing the same problem with the current heat wave. I'm nosey, I'd wander around and see just what kind of service is coming in from the street to the park.
Right after I cranked up the generator and got the air working
|
I was thinking this was the case but after Labor Day the crowds left and the problem persists. We would go somewhere else but the place is really nice otherwise. We really like the location.
|
|
|
09-07-2022, 06:36 PM
|
#7
|
Senior Member
Join Date: Dec 2021
Location: Richmond
Posts: 339
|
Maybe I should just request a 50 amp service for my 30 amp travel trailer. Maybe that would solve the problem.
__________________
Lee
2019 Keystone Passport GT Ultra Lite 2520RL, 7000lb GVW,
2015 F150 5.0, XLT/FX4, 3.55 Tow, 7000lb GVWR, 1829lb payload, 36 gal tank,
|
|
|
09-07-2022, 07:13 PM
|
#8
|
Senior Member
Join Date: Nov 2017
Location: Mico, TX
Posts: 7,447
|
Quote:
Originally Posted by hlh1
Maybe I should just request a 50 amp service for my 30 amp travel trailer. Maybe that would solve the problem.
|
Not sure where you are camping but check campgroundreviews.com and MOVE to another park. That kind of treatment wouldn't earn my continued stay or business. Write up a review for campgroundreviews.com so others don't fall into the same situation.
__________________
wiredgeorge Mico TX
2006 F350 CC 4WD 6.0L
2002 Keystone Cougar 278
2006 GL1800 Roadsmith Trike
|
|
|
09-07-2022, 07:29 PM
|
#9
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 17,669
|
Your EMS is shutting you down to low voltage on the one leg of AC. Going to a 50A gives you 2 legs of AC but if they are below the cutoff threshold of the EMS, which they probably will be, you gained nothing other than moving. The issue should be pressed with the park or move IMO. If you didn't have an EMS, as I'm some of the poor souls don't, they will be slowly killing their appliances as they endure this.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
|
|
|
09-07-2022, 09:19 PM
|
#10
|
Senior Member
Join Date: Apr 2012
Location: Portland, OR
Posts: 4,218
|
Quote:
Originally Posted by sourdough
Your EMS is shutting you down to low voltage on the one leg of AC. Going to a 50A gives you 2 legs of AC but if they are below the cutoff threshold of the EMS, which they probably will be, you gained nothing other than moving. The issue should be pressed with the park or move IMO. If you didn't have an EMS, as I'm some of the poor souls don't, they will be slowly killing their appliances as they endure this.
|
The OP has a 30 amp rig, if he connects today 50 amp outlet, the 50 to 30 amp dog bone will only deliver power from one leg of the 50 amp. The advantage is that the wire to the pedestal should be at least 6 gauge instead of 10 gauge for 30 amp, so less voltage drop if only drawing 30 amps.
__________________
Russ & Paula and Belle the Beagle.
2016 Ram Laramie 3500 DRW 14,000# GVWR (New TV)
2005 Copper Canyon 293 FWSLS 32’ GVWR 12,360
Visit and enjoy Oregon State Parks
|
|
|
09-08-2022, 04:15 AM
|
#11
|
Senior Member
Join Date: Dec 2021
Location: Richmond
Posts: 339
|
Your excellent responses are why I posted this. I knew the knowledgeable members of this board would give me good advice. Because of this forum I bought the EMS that's probably saving my AC/Fridge, etc. Right now I'm getting by with staying below 15 amps.
I'm new to RV'ing and I'm not sure what to expect, power wise, from these RV camps. I can see how it's possible to go over 30 amps with my TT if I have everything running. We were at a State Park two weeks ago that showed 127 VAC and I was running 35 amps with no issues.
I will try to talk with the camp admin again today and explain. Or I may just send them an email with details of what I'm seeing. We want to stay here in the future, even with the bad power, so I don't want them to black ball me. And yes, I do need to write up a review.
__________________
Lee
2019 Keystone Passport GT Ultra Lite 2520RL, 7000lb GVW,
2015 F150 5.0, XLT/FX4, 3.55 Tow, 7000lb GVWR, 1829lb payload, 36 gal tank,
|
|
|
09-08-2022, 05:26 AM
|
#12
|
Senior Member
Join Date: Jun 2022
Location: Floresville
Posts: 106
|
You are paying for a Full 30Amps. Would you pay full price for a new truck that has no engine or transmission? Walk away from this deal.
__________________
2019 Laredo 325RL
2017 Ford F350 DRW
USAF Retired, (20 years, Firefighter)
|
|
|
09-08-2022, 05:43 AM
|
#13
|
Senior Member
Join Date: Jan 2013
Location: Indiana
Posts: 2,705
|
I don't understand how you can be running 35 amps on a 30 amp camper. Once you exceed 30 amps (even if the shore power supply can exceed this), the main breaker in your camper should trip. If it's not tripping, then you got another problem going on.
Now, if you are running a second extension cord from the same power pole (for example, your normal 30 amp RV power cord and then a 15/20 amp extension or utility cord) and running another appliance, then I can understand how you could exceed 30 amps from one shore power source.
Power management, regardless if 30 or 50 amp availability is always something you have to be aware of in any camper, otherwise breakers trip. BUT low voltage is not something that you should have to deal with.
__________________
2019 Montana High Country 375FL
2014 Chevy Duramax HD 6.6 - 3500 Diesel Dully Long bed Crew Cab
|
|
|
09-08-2022, 06:21 AM
|
#14
|
Senior Member
Join Date: Dec 2021
Location: Richmond
Posts: 339
|
Quote:
Originally Posted by dutchmensport
I don't understand how you can be running 35 amps on a 30 amp camper. Once you exceed 30 amps (even if the shore power supply can exceed this), the main breaker in your camper should trip. If it's not tripping, then you got another problem going on.
Now, if you are running a second extension cord from the same power pole (for example, your normal 30 amp RV power cord and then a 15/20 amp extension or utility cord) and running another appliance, then I can understand how you could exceed 30 amps from one shore power source.
Power management, regardless if 30 or 50 amp availability is always something you have to be aware of in any camper, otherwise breakers trip. BUT low voltage is not something that you should have to deal with.
|
I was kind of surprised to see 35 amps on the EMS.
|
|
|
09-08-2022, 06:38 AM
|
#15
|
Senior Member
Join Date: Jan 2013
Location: Indiana
Posts: 2,705
|
What kind of EMS do you have? Built in or portable, Progressive - Hughes AutoFoamer - SurgeGuard? Maybe there is something failing in the EMS causing false output readings?????
__________________
2019 Montana High Country 375FL
2014 Chevy Duramax HD 6.6 - 3500 Diesel Dully Long bed Crew Cab
|
|
|
09-08-2022, 06:51 AM
|
#16
|
Senior Member
Join Date: Dec 2021
Location: Richmond
Posts: 339
|
Quote:
Originally Posted by dutchmensport
What kind of EMS do you have? Built in or portable, Progressive - Hughes AutoFoamer - SurgeGuard? Maybe there is something failing in the EMS causing false output readings?????
|
I have the progressive ems. I guess I need to check it with a good voltmeter, amp meter.
|
|
|
09-08-2022, 07:03 AM
|
#17
|
Senior Member
Join Date: Jan 2013
Location: Indiana
Posts: 2,705
|
Progressive should be good and reliable. It won't hurt to double check. This way you can eliminate every possible excuse with campground management, and the problem is truly 'on-them."
__________________
2019 Montana High Country 375FL
2014 Chevy Duramax HD 6.6 - 3500 Diesel Dully Long bed Crew Cab
|
|
|
09-08-2022, 08:08 AM
|
#18
|
Site Team
Join Date: Feb 2014
Location: W. Texas
Posts: 17,669
|
Quote:
Originally Posted by rhagfo
The OP has a 30 amp rig, if he connects today 50 amp outlet, the 50 to 30 amp dog bone will only deliver power from one leg of the 50 amp. The advantage is that the wire to the pedestal should be at least 6 gauge instead of 10 gauge for 30 amp, so less voltage drop if only drawing 30 amps.
|
You are correct. I re read post 1 which seemed to leave the amperage of the trailer in doubt, I failed to re read post 7 which stated it was a 30A trailer. Moving to a 50A service with 30A cables and a dogbone would do nothing for the OP.
As far as pulling 35A on a 30A circuit OP needs to look into that with an ammeter. If would seem there could be multiple problems; if the trailer is pulling 35A from inside the 30A breaker inside the trailer should trip. If it didn't the 30A breaker at the ped should trip. If neither is tripping ?? With the apparent poor power service I would suspect the ped breaker but why isn't the trailer tripping? Or is the readout faulty? I would lean toward a faulty reading I believe.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
|
|
|
09-08-2022, 08:38 AM
|
#19
|
Senior Member
Join Date: Apr 2012
Location: Portland, OR
Posts: 4,218
|
Quote:
Originally Posted by sourdough
You are correct. I re read post 1 which seemed to leave the amperage of the trailer in doubt, I failed to re read post 7 which stated it was a 30A trailer. Moving to a 50A service with 30A cables and a dogbone would do nothing for the OP.
As far as pulling 35A on a 30A circuit OP needs to look into that with an ammeter. If would seem there could be multiple problems; if the trailer is pulling 35A from inside the 30A breaker inside the trailer should trip. If it didn't the 30A breaker at the ped should trip. If neither is tripping ?? With the apparent poor power service I would suspect the ped breaker but why isn't the trailer tripping? Or is the readout faulty? I would lean toward a faulty reading I believe.
|
Yes, his 30 amp cable is still the same, BUT the park feed to the 50 amp outlet is 6 gauge wire not the 10 gauge for the 30 amp, thus likely less voltage drop when drawing near 30 amps
__________________
Russ & Paula and Belle the Beagle.
2016 Ram Laramie 3500 DRW 14,000# GVWR (New TV)
2005 Copper Canyon 293 FWSLS 32’ GVWR 12,360
Visit and enjoy Oregon State Parks
|
|
|
09-08-2022, 09:13 AM
|
#20
|
Site Team
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,741
|
Reading thru this thread is a bit confusing. Experiencing a voltage drop during high amperage draws are common. It can be caused by insufficient feeds from the utility company, an overloaded transformer line (unbalanced loading) or a wiring issue anywhere in between the transformer and the trainer's power panel.
If you only have the issue at that park then it points to the issue as the park/utility problem. Either way it's the park responsibility and if they aren't willing to address it then I wouldn't patronize them. If I'm paying for a service then I expect that service to be fully available. I would feel ripped off if I paid full price at a car wash and they didn't was 1/2 of the car.JMO.
As to the accuracy of the EMS voltage reading that's easy to verify with a multimeter or a plug in voltage meter. I keep a voltage meter plugged into an outlet so I can glance at it anytime. It cost <$20. The Amp reading would require an amp clamp portable meter or a permanent mount ammeter to compare and verify. A 35 Amp constant load should trip the 30 Amp main breaker. If that 35 Amp load is a peak load, i.e. short duration like a motor starting, then it shouldn't trip.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
|
|
|
|
|