Quote:
Originally Posted by Patrick007
My solar GFCI tripped and will not reset leaving half of my outlets in my rig unusable. I took the outlet out of the wall and the copper ground wire was severed so I reconnected it. GFCI still will not reset. I tested the Load side of the outlet and there was not any power. I tested the Line side and there was power on the outlet. Not sure what to do next?
|
On the line side check voltage from black wire (Line) to white wire (Nuetral) and from Line to bare wire (Ground) . You should read ~120 VAC on both tests. If you don't have it on both then there is a break in the wire or a disconnected wire in the panel. If you have voltage testing from the Line to the Nuetral AND to the ground and the GFI will not reset then the GFI is defective and needs to be replaced.