Another Furnace Question

We had the occasion to do a little cold weather camping this past week. We've camped before with temps in the 20's. This time, thanks to a Canadian cold front, we found ourselves dry camping in the single digits for several nights.
So here's the question: We've never really had good air flow to the heat vents in the bathroom and the bedroom (upstairs). Also didn't care a whole lot since we like it a little cooler for sleeping. But, when it got really cold we thought it might be nice to have a little more warm air flowing to the front of the Cougar. Has anyone experienced this same problem and were you able to find a solution??
So far, I've installed "closable" registers in the kitchen and living room in an attempt to force more air forward. Not much help. The ducting to the upstairs registers is visible from the cargo area and looks to be intact with no damage or restrictions. I'm thinking about tearing into it further but thought there might be some tribal knowledge here I could take advantage of. Some of you more experienced pros might know of a test I could do to make sure the furnace is actually putting out the proper CFM to the registers.
Appreciate the help!
Attached Thumbnails
Click image for larger version

Name:	_MGL6797.jpg
Views:	141
Size:	451.5 KB
ID:	24032   Click image for larger version

Name:	_MGL6795.jpg
Views:	126
Size:	342.0 KB
ID:	24033  
__________________
2017 Cougar 279RKSWE
2007.5 Dodge Ram 2500 6.7 Cummins
Retirement Training Completed
I think the little voices in my head have started a chat group.
Canonman is offline   Reply With Quote
Old 10-12-2019, 07:38 PM   #2
busterbrown
Senior Member
 
busterbrown's Avatar
 
Join Date: Feb 2016
Location: SE Michigan
Posts: 1,659
I don't think "proper CFM" and RV's should be used in the same paragraph. There are ways to properly seal up the duct-work in the underbelly to help with air flow to the front of your coach. Accessing it through the coroplast will be your biggest hurdle.

I'm not aware you can do anything to help with airflow at the blower. Maybe the moderators, John or Chuck, can offer some insight.
__________________
2017 Keystone Bullet 308BHS in Saddle.
2017 RAM 2500 Laramie Mega Cab 4x4 Hemi 6.4L
2008 GMC Yukon XL Denali (SOLD)
Hensley SwiftArrow Control Hitch with 1000 lb Spring Bars
Me, DW, (3) little DS's, and 1 rambunctious Boston Terrier

busterbrown is offline   Reply With Quote
Old 10-12-2019, 08:17 PM   #3
chuckster57
Site Team
 
chuckster57's Avatar
 
Join Date: Jul 2014
Location: Modesto
Posts: 20,235
Depending on how the furnace is ducted, you may be losing airflow at the “box”. Often times there are circles cut into the box and the ducting has a flange with a tab. Line up the fitting and it twists into place. I’ve seen them off completely and other times not fully engaged

Some furnaces sit on the floor and blow down into ductwork. There is a fiber gasket between the box and the ducting, I’ve seen that gasket not placed right or broken/missing. Find the return to your furnace and remove that grill. Then have a look, turn on the furnace and feel for air flow loss. There are flow tests but we don’t have the expensive equipment to perform it.
__________________

2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.

Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
chuckster57 is offline   Reply With Quote
Old 10-12-2019, 08:53 PM   #4
hankpage
Site Team
 
hankpage's Avatar
 
Join Date: Jun 2009
Location: Venice
Posts: 5,346
Starting under the steps, I replaced all the flex vent "Slinky" stuff with aluminum 4" vent pipe and it greatly improved the flow to the bedroom vents. It made the pass through a little neater too. Removing the step was not as hard as I thought it would be, only a few screws hidden in the carpet.

__________________
Hank & Lynn
2007 Cougar 290RKS, E-Z Flex, 16" XPS RIBs ( SOLD .. Gonna miss her ... looking for new 5r)
2004.5 Dodge 2500 QC, LB, 5.9HO, WestTach gauges, Ride-Rite
hankpage is offline   Reply With Quote
Old 10-13-2019, 06:50 AM   #5
Canonman
Senior Member
 
Canonman's Avatar
 
Join Date: May 2016
Location: South Jordan, Utah
Posts: 2,221
Quote:
Originally Posted by chuckster57 View Post
Depending on how the furnace is ducted, you may be losing airflow at the “box”. Often times there are circles cut into the box and the ducting has a flange with a tab. Line up the fitting and it twists into place. I’ve seen them off completely and other times not fully engaged

Some furnaces sit on the floor and blow down into ductwork. There is a fiber gasket between the box and the ducting, I’ve seen that gasket not placed right or broken/missing. Find the return to your furnace and remove that grill. Then have a look, turn on the furnace and feel for air flow loss. There are flow tests but we don’t have the expensive equipment to perform it.
Furnace is installed in the horizontal position and is downdraft into the ductwork going to the living area. I'll check the seal around the downdraft connection for any leaks. I've got some regular duct seal aluminum tape that i'll likely put on as long as I have the access open. Next step will be to empty the basement and access the connections where the two flex ducts connect to the living area ductwork to see if there is any loss there. Depending on what I find and the degree of difficulty, I may take Hank's suggestion and replace the flex pipe with 4" ducting.
Thanks guys for the help!
Attached Thumbnails
Click image for larger version

Name:	IMG_5645.jpg
Views:	135
Size:	1.49 MB
ID:	24037  
__________________
2017 Cougar 279RKSWE
2007.5 Dodge Ram 2500 6.7 Cummins
Retirement Training Completed
I think the little voices in my head have started a chat group.
Canonman is offline   Reply With Quote
Old 10-13-2019, 07:21 AM   #6
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,836
One of Keystone's "inherent design features" (yeah, right) is to install "belly heat ducting" that meanders through the underbelly. It's not insulated, 4" aluminized flex duct that comes in 12' lengths. Typically, Keystone installs the entire 12' section, even if the "to and from" connections are only 2 feet apart. They (Keystone) claims that the other 10' "meandering around the holding tanks" will supplement basement heat (2" hot air duct) and is a "design feature" of the Polar Package" or "Arctic Protection Package" ...

I found two "meandering ducts" in my underbelly, one ran from the forward part of the main cabin floor system, around the black tank and forward gray tank, then up into the pass-through (behind the water heater) and then coiled once before it was connected to that "passthrough overhead duct" that connects to the bathroom and bedroom heat registers. I straightened up part of the "belly flex duct" and removed the coiled duct behind the water heater. It improved the bedroom hot air flow, but the main area floor and the passthrough are now noticeably colder without that heat loss and air flow loss from the "too long flex duct meandering through the belly"....

It's sort of a "give and take" situation. Give the heat to the tanks/belly and take it from the front two registers (bedroom and bathroom) or take the heat from the tank/belly and they'll be colder.

It's been said many times, that you can only provide a specific BTU output from an RV furnace. Where you "share those BTU's" makes a significant difference in comfort vs system protection. Not everyone needs system protection at the expense of main cabin comfort, some other members need system protection to keep their RV "livable" in sub-arctic conditions"... Keystone tries to "split the difference" or maintain a "happy median" but both main cabin comfort (bedroom airflow) and underbelly protection tend to be compromised to obtain that "happy median"....

Do what you can to improve on the airflow losses, but realize that if you put those BTU's in the main cabin, they won't be heating the belly and your overall protection MIGHT be reduced in extremely cold conditions.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 10-13-2019, 07:30 AM   #7
Roscommon48
Senior Member
 
Join Date: Dec 2018
Location: grand rapids
Posts: 596
this is why we don't camp in the cold...trailers suck at heating.


when cold we just turn on on electric heater...it is quieter anyway.


good luck
Roscommon48 is offline   Reply With Quote
Reply

Tags
furnace

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 05:24 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.