Before putting my trailer into storage everything was working. I bought it new only last September/October. Now when I plug the trailer into a household GFCI breaker it trips. Typically this is the heating element in the water heater. But it's good. If the breaker in the trailer which is labeled CONV/GEN is "ON", the GFCI trips. This is regardless of other breakers, execpt of course the MAIN. We have swapped out the converter but it has no effect. At this point the dealer is stumped and so am I. Any suggestions?
|
|
|
02-23-2012, 08:14 AM
|
#2
|
Senior Member
Join Date: Sep 2011
Location: Northville NY in the Adirondacks
Posts: 2,128
|
Somewhere in the trailer there is a ground fault of some kind on the 110vac wiring.
Try this:
- Shut off all the breakers in the trailer and then plug the shoreline back into the house GFCI.
- If the GFCI trips right away, you know that the ground fault is in either the shore line or the trailer wiring from the shoreline to the electric panel.
- If it doesn't trip, then one at a time, turn a breaker on.
- If it does not trip the GFCI, shut it off and go to the next.
- By the time you have tested the last breaker, you should know which circuit is causing the ground fault.
If you can figure out which circuit is the culprit, and the dealer still can't fix the problem, get a real electrician to check it out.
__________________
'11 Cougar 326MKS loaded with mods
'12 Ford F250 SuperCab 6.7 PowerStroke Diesel
Amateur Radio: KD2IAT (146.520) GMRS: WQPG808 (462.675 TPL 141.3)
|
|
|
02-23-2012, 12:45 PM
|
#3
|
Junior Member
Join Date: Feb 2012
Location: Grand Junction, CO
Posts: 2
|
Gfci
Thanks for the reply. As it turns out the breakers in the trailer were deceiving. The problem ended up being the typical water heater element burnout. Only the power is switched by the breakers. Neutral is not. So the current imbalance was caused by leakage from the heater neutral to something wired to the Converter breaker power. Replacing the electrical heating element fixed the problem. The dealer tells me that virtually all GFI problem are the related to the water heater element.
|
|
|
02-25-2012, 07:36 PM
|
#4
|
Senior Member
Join Date: May 2011
Location: SW Florida
Posts: 196
|
Quote:
Originally Posted by Montegj
Thanks for the reply. As it turns out the breakers in the trailer were deceiving. The problem ended up being the typical water heater element burnout. Only the power is switched by the breakers. Neutral is not. So the current imbalance was caused by leakage from the heater neutral to something wired to the Converter breaker power. Replacing the electrical heating element fixed the problem. The dealer tells me that virtually all GFI problem are the related to the water heater element.
|
That is good information to know.
|
|
|
02-26-2012, 09:28 AM
|
#5
|
Senior Member
Join Date: Jan 2012
Location: N. Illinois
Posts: 167
|
Good info to know for sure. However, why did the heating element go bad so fast on a new trailer?
__________________
Andy & Iacie G.
2017 Impact 361
2017 F350 4x4 6.7 Powerstroke
---------------------
|
|
|
02-26-2012, 10:39 AM
|
#6
|
Senior Member
Join Date: Sep 2011
Location: Northville NY in the Adirondacks
Posts: 2,128
|
Quote:
Originally Posted by 86GT2r
Good info to know for sure. However, why did the heating element go bad so fast on a new trailer?
|
All it takes is a few seconds of power to the heating element in a dry water heater tank, and it's shot.
Since our camping has been mostly in NYS parks that don't have hookups, I shut off the breaker for the heater and taped it so it can not be accidentally turned back on. But with the new Cougar, our outings will be different and we'll likely use the 110vac more often. Not sure how I am going to protect the element.
__________________
'11 Cougar 326MKS loaded with mods
'12 Ford F250 SuperCab 6.7 PowerStroke Diesel
Amateur Radio: KD2IAT (146.520) GMRS: WQPG808 (462.675 TPL 141.3)
|
|
|
02-26-2012, 02:25 PM
|
#7
|
Site Team
Join Date: Mar 2009
Location: Fraser Valley BC Canada
Posts: 7,015
|
Steve:
Some Keystones have a small, "safety" cotter pin located in the bottom LH corner of the exterior service door the heater (Suburban). The pin, when inserted into the rocker switch, prevents accidental turning on of the HW tank. Your tank may not have this feature.
__________________
2008 Cougar 5th Wheel 27RKS
2005 2500 GMC Duramax
|
|
|
02-26-2012, 03:03 PM
|
#8
|
Senior Member
Join Date: Sep 2011
Location: Northville NY in the Adirondacks
Posts: 2,128
|
Quote:
Originally Posted by Festus2
Steve:
Some Keystones have a small, "safety" cotter pin located in the bottom LH corner of the exterior service door the heater (Suburban). The pin, when inserted into the rocker switch, prevents accidental turning on of the HW tank. Your tank may not have this feature.
|
Good to know. Trailer is still in storage until mid-April so I can't dash out and look to see if ours has that. Thanks!
__________________