Quote:
Originally Posted by Arnold88
thank you.
i will look into the propane. l will look for the circuit breaker tomorrow and see if i can warm it with a heat gun and see if it fails
|
There was a "recent" (about 18 months ago) service repair to remove all the 15 amp 12VDC circuit breakers from the furnace wiring system and replace with a 15 amp "blue" fuse... The reason given was that the circuit breakers "weaken over time" and start to open at lower and lower amperage draw.
All of the 12VDC circuit breakers I've seen are in the furnace slot in the 12 volt power distribution panel.
Another issue you may have, since there seems to be a 6 minute delay from furnace ignition until shutdown, is a blocked warm air ducting issue. There may be pet hair, dust or something else either caught in the squirrel cage fan blower or even a rat's nest or some other restriction in one of the heat duct runs. As the furnace operates, if there is not enough air movement through the heat exchanger, the temps will rise and the "HI LIMIT" safety switch will open to shut down the furnace.
I'd check for any circuit breaker in the main DC fuse panel and then start checking for a possible air restriction in the ducting/air movement system in the trailer.