generators

can anyboby tell me what size portable generator i would need to run my 50 amp fifth wheel. one 15000btu and 1 13500btu ac
brent is offline   Reply With Quote
Old 08-02-2011, 08:39 AM   #2
jq1031
Senior Member
 
Join Date: Dec 2010
Location: Venice, FL
Posts: 484
Quote:
Originally Posted by brent View Post
can anyboby tell me what size portable generator i would need to run my 50 amp fifth wheel. one 15000btu and 1 13500btu ac
My former motor home had that set up & the generator was 7500 Watts
__________________
Joe & Carolyn, Venice, FL.
2011 Laredo TT 297RL
2011 GMC Sierra Denali 2500 HD 4X4, Duramax Diesel/Allison Transmission, 3.73 Gears, Reese WD with two sway bars. Dometic 3000KW Generator.
jq1031 is offline   Reply With Quote
Old 08-02-2011, 08:46 AM   #3
brent
Junior Member
 
Join Date: Aug 2011
Location: louisiana
Posts: 7
thank you can you tell me if the 120/240 straight plug in on the generator only puts out 120 volts to the camper using the camper cord. i have a outback sydney 5th
brent is offline   Reply With Quote
Old 08-02-2011, 05:23 PM   #4
Houndie Dog
Member
 
Houndie Dog's Avatar
 
Join Date: Sep 2010
Location: Saint Louis, MO
Posts: 78
Brent,
this is the setup I use...This is only 30A because anything I have found that is 50A is very big and very heavy. I can run both A/C's on this, but you have to be aware of your power usage and keep things to a minimum.
***No I do not run the generator in the cargo bay & No, there is no fuel in the tank......I have ramps that I roll the generator in and out on. Just thought I would show you my setup, it weighs about 170lb without fuel.

http://i809.photobucket.com/albums/z...IMGP0825-1.jpg
http://i809.photobucket.com/albums/z...o/IMGP0827.jpg
__________________
Grant & Melisa
2014 Montana 3625RE Big Sky
2011 GMC 3500 Duramax
Hensly TS3 trailer-saver hitch
KVH TracVision R4SL
3 Basset Hounds "Lucy, Ethel, & Fred"
https://i809.photobucket.com/albums/z...vado/coach.jpg
Houndie Dog is offline   Reply With Quote
Old 08-02-2011, 07:14 PM   #5
CampDestinations.com
Guest
 
Posts: n/a
When hooked up at a campground, a "wired" 50-Amp service will provide about 6,000 watts of power to your camper.
  Reply With Quote
Old 11-15-2011, 08:44 AM   #6
SAABDOCTOR
Senior Member
 
SAABDOCTOR's Avatar
 
Join Date: Aug 2011
Location: WESTERN,CT
Posts: 2,095
THERE ARE AS MANY ANSWERS AS PEOPLE ON THE THREAD! WATTS... VOLTAGE TIMES AMPS = WATTS 120 VOLTS X 50 AMPS IS 6000 WATTS. THAT WILL BE A FAIRLY BIG UNIT AND LOUD! PLUS YOU WOULD NEED THIS MUCH IF YOU WANT TO START EVERTHING AT ONCE..(NOT) BE GOOD ABOUT WHAT YOU TURN ON ONE A/C AT A TIME CAREFULL WITH THE MICRO WAVE LEAVE THE HOT WATER OFF ELECTRIC WHEN NOT NEEDED AND YOU CAN GET BUY WITH UNDER 3000 WATTS! BEFORE YOU ALL JUMP DOWN MY THROUGHT I HAVE DONE IT I AM CAREFUL HOW I USE THE POWER. BUT MINE IS BACKUP POWER IN AN EMERGANCY. I WOULD THINK 4KW SHOULD BE FINE FOR YOU. QUICK AND EASY, LOOK AT YOUR BREAKERS THE A/C IS ON A 30 AMP BREAKER THAT IS 3600 WATTS BUT THAT WOULD BE SURGE POWER RUNING IS ABOUT 1500 MAX SO 4 K WILL COVER YOU LOTS OF CAMPERSS USE 2 HONDA EU2000i IN PARALELL HONDA HAS A CABLE FOR THAT. THEN YOU HAVE A CHOISE. 4000 OR 2000 WATTS. PLUS THEY ARE QUIET AND VERY STINGY ON FUEL. PLUS PLUS THEY ARE LIGHT SO THE DW CAN LIFT THEM OUT OF THE STORAGE CABINET. ONLY IF YOU ASK NICELY HA HA.
__________________
BARNEY AND CHRISTINE
2010 MONTANA 3750FL
2005 DODGE 3500 DUALLY TD
2 RESCUE PUPS: SUSITNA AND CRYSTAL. RIP ALYESKA!
SAABDOCTOR is offline   Reply With Quote
Old 11-15-2011, 05:03 PM   #7
cumminsdad08
Senior Member
 
cumminsdad08's Avatar
 
Join Date: Mar 2011
Location: West Lebanon PA
Posts: 350
X 2 on the honda inverters. they are very nice, we use them at work, and often take them in the larger buildings and keep them in our areial lifts while we work (i know, i know, not the smartest idea, but we get the job done). they perform flawlessly for us day after day, even when you run over them with a dually,( don't ask).

how do you like the generac? does it put out what it says it will? we tried a few of them, and they didn't run anywhere near what they said they would. the price was right for them, but just didn't hold out for what we needed. were several hundred less then the hondas.
__________________
2006 Springdale 295bh TT
2004.5 Dodge Ram 2500 Diesel TV(Babe, the Blue Ox), tuned, cold air, high ram, open pipes, 6 spd., 3 inch lift, running on 35's and lovin' it
Me-26, Wife-26, Boy-4, Girl-2
Dogs
Buddy-beagle hound mix
Emily-beagle hound mix
Sadie-boarder collie (my amish one)
cumminsdad08 is offline   Reply With Quote
Old 11-15-2011, 07:40 PM   #8
chain_dogg
Senior Member
 
chain_dogg's Avatar
 
Join Date: Jun 2011
Location: Anaheim California
Posts: 186
Quote:
Originally Posted by brent View Post
can anyboby tell me what size portable generator i would need to run my 50 amp fifth wheel. one 15000btu and 1 13500btu ac
Best Portable Generator a man could own.......

http://www.hondapowerequipment.com/p...lid=EU3000ISAN


chain_dogg is offline   Reply With Quote
Old 11-15-2011, 09:20 PM   #9
Ron
Senior Member
 
Ron's Avatar
 
Join Date: Mar 2011
Location: Washington State
Posts: 859
What do you all think about the Yamaha 4500ise, What I like about this unit is the remote start.



I know someone that has one and it is super quite like the Honda
__________________
Ron
99 Freightliner FL70 Western Hauler CC 300 HP Cat/Chipped/ Allison Auto
12 Montana 3800RE/Level-Up Auto Leveling/Slide Toppers/MorRyde Hitch/VuQube 2000
01 F350 7.3 PSD Crew Cab DRW 4X4 6 Speed/Chipped


Ron is offline   Reply With Quote
Old 11-15-2011, 10:02 PM   #10
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,974
The Honda 3000 generator is rated at 3000 watts surge and 2800 watts continuous. That means it will run continuously at 23.3 Amps (Half of what you need if you're wanting to run at 50 Amps). Dometic recommends a minimum of 3500 watts for one AC and 5000 watts for two. That recommendation is for either 13.5K or 15K BTU AC's. That means that the manufacturer recommends a generator rated 700 watts higher than the Honda 3000 is capable of producing continuously and 500 watts higher than it can rate for "momentary" use. What that means is that the Honda should not be used to power more than 2800 watts for greater than 20 minutes. One 13.5K BTU AC requires 13.9 Amps to run (more to start the compressor) which means that one AC requires 1668 watts to run.

While it's true that some people, under ideal conditions can use a Honda 3000 generator to power a 30 Amp RV electrical system while conserving power by not using the HWH, microwave, etc, it won't power a 50 Amp RV if you expect to use both AC's, even with conservative management. ALL the motorhome manufacturers install a minimum of 4500 watts (usually at least 5500 watts) in their motorhomes with 2 rooftop AC units. With the onboard 4500 watt generators, those motorhomes require a special circuit which alternates between front and rear AC. Both AC's don't operate at the same time.

I'd recommend you do a search on this forum for generators and read the extensive discussions regarding recommendations for which are minimally acceptable in 30 Amp RV's and in 50 Amp RV's.

As for the 4500 watt Yamaha generator, it is rated at 4000 watts (33 Amps)continuous and 4500 watts surge. It is hardly portable as it weighs 194 lbs empty, by the time you put 4.5 gallons of gas (about 30 lbs) you're going to be lifting over 200 pounds in and out of your truck. The electric start may be nice, especially when you pull your back muscles lifting that heavy thing and can't pull a starter rope...
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 11-17-2011, 02:38 PM   #11
christopherglenn
Senior Member
 
Join Date: Jul 2011
Location: 1 hour from Yosemite
Posts: 165
Actualy a 50 amp service is 50 amp 240 volt. There are 2 120 volt 50 amp legs in the same cable. That is 12,000 watts (12kw).
My trailer has a 5.5KW Onan, and it runs both AC's and the microwave at the same time.
__________________
2007 Chevrolet 3500 CC/LB Duramax/Dually 4X4 Mine r4tech, Reese Signature Series 18k +slider, duratrac, titan 62 gallon, diamond eye, Cheetah 64, EFI Live
2008 Chevrolet 2500 CC/SB Duramax 4X4 Hers r4tech, duratrac
2011 Keystone Fusion 405 TrailAir & Triglide, Centerpoint, gen-turi, 3 PVX-840T, XANTREX FREEDOM SW3012, G614
2013 Yamaha 242LS
2010 GMC Yukon The Bus
2005 Chevrolet 2500 CC/SB Duramax 4X4 Hers (sold)
2006 Jayco Jay Flight 31BHS (sold)
christopherglenn is offline   Reply With Quote
Old 11-17-2011, 04:07 PM   #12
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,974
A 5.5KW (5500 Watt) generator will do fine running two air conditioners and the microwave. The only potential problem would be if both AC's tried to start at the same time and the microwave was running. That's a very unlikely situation. As for the wattage on a 50 Amp trailer. I think you'll find that it's 2 legs of 30 amps each at 120 VAC, not 2 lines of 50 amps...

You know, it puzzles me how (or why) so many people "preach" truck limitations, expressing an 80% rule for towing, etc, stress tire inflation safety, load limits for truck and trailer, yet when it comes to generators, (something that can kill you easily if safety is ignored) many of them will load a Honda 2000 Watt generator up to the max and then ask it to power something else as well... A Honda 2000 generator is really a 1600 watt generator and when you do the wattage requirements for a 13.5 BTU AC, it ocmes out to 1668 watts required to run and even more to start. I guess it seems that when it comes to the "sacred" truck, protection and conservative operation is warranted, but when it comes to a generator, all bets are off, just plug stuff in until it pops the circuit breaker, then complain that "something" must be wrong with it because the "neighbor's" generator didn't do that..... Hmmmmm
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 11-17-2011, 04:23 PM   #13
SteveC7010
Senior Member
 
SteveC7010's Avatar
 
Join Date: Sep 2011
Location: Northville NY in the Adirondacks
Posts: 2,128
Quote:
Originally Posted by JRTJH View Post
You know, it puzzles me how (or why) so many people "preach" truck limitations, expressing an 80% rule for towing, etc, stress tire inflation safety, load limits for truck and trailer, yet when it comes to generators, (something that can kill you easily if safety is ignored) many of them will load a Honda 2000 Watt generator up to the max and then ask it to power something else as well... A Honda 2000 generator is really a 1600 watt generator and when you do the wattage requirements for a 13.5 BTU AC, it comes out to 1668 watts required to run and even more to start. I guess it seems that when it comes to the "sacred" truck, protection and conservative operation is warranted, but when it comes to a generator, all bets are off, just plug stuff in until it pops the circuit breaker, then complain that "something" must be wrong with it because the "neighbor's" generator didn't do that..... Hmmmmm
That's one of the reasons I've never included the A/C in my generator usage for the trailers as it it way too much draw for the eu2000i. Even Mama's hair dryer and the microwave running at the same time can be problematic if both are set for full load and kick in at more or less the same time. The 1000 and 2000 series Hondas (and others) are great for keeping batteries up and running smaller 110vac appliances, but people have to understand their limitations and stay within them.
__________________

'11 Cougar 326MKS loaded with mods
'12 Ford F250 SuperCab 6.7 PowerStroke Diesel
Amateur Radio: KD2IAT (146.520) GMRS: WQPG808 (462.675 TPL 141.3)
SteveC7010 is offline   Reply With Quote
Old 11-17-2011, 04:35 PM   #14
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,974
Steve, My "fear" is that people who don't really understand electricity and get complacent with its use get out in "the middle of nowhere" and plug in a small generator, overload it, and when it starts "balking" on them and won't run what they have plugged in, they start poking at things on the generator. That's the same as poking at an outlet at home, only problem is the one at home is grounded and you're somewhat protected against shock, at least if your house is wired properly. But, that "little thingie" we all ignore, the grounding lug on the generator, is the only thing that could make it "close to a household circuit" and we never run a 4 guage wire from the generator to a copper ground driven into the ground at the proper depth. Add to that "damp grass" and you're inviting disaster if someone starts resetting circuit breakers, tapping on the generator windings with a small hammer, a screwdriver poked into the back of the distribution box, etc. I've seen it happen time and time again. Those "things" aren't magic boxes to make us comfortable, they are tools that need to be properly used just like any power saw, welder, or pick up truck. All of them have a great potential to cause harm or to kill, yet we often times forget and just keep on "plugging away" at the generator...
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 11-17-2011, 05:04 PM   #15
mhs4771
Senior Member
 
mhs4771's Avatar
 
Join Date: Jan 2011
Location: Central Florida
Posts: 478
[QUOTE=JRTJH;23565] As for the wattage on a 50 Amp trailer. I think you'll find that it's 2 legs of 30 amps each at 120 VAC, not 2 lines of 50 amps...


Nope, newer rigs run on 240V/50 Amps just like a mini stick house system. Two 120V legs of 50 Amps each. That is provided you're plugged into a real 50 Amp Service. Some CGs advertise 50 Amp Service, but it's just a Single Phase, 120V/50Amp
__________________
2011 Chevy Silverado 3500HD Ext Cab LT DRW Duramax/Allison pulling a 2012 SOB (still Thor, but not a Keystone), Dual ACs, 4 Door Fridge, Fireplace, Sleep Number Bed, Level-Up Auto Levelers, Disc Brakes, Winegard DirecTV SlimLine Auto Dish, Onan 5.5K, Splendide Combo Washer/Dryer, GY G114s on HiSpec 17.5 wheels, TrailAir Tri-Glide Pin Box, Mor/ryde IS.

Michelle & Ann Sullivan and 4 American Shorthairs
mhs4771 is offline   Reply With Quote
Old 11-17-2011, 09:13 PM   #16
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,974
The largest somewhat portable generator I could find with an "RV plug function" that could be adapted to use a 50 Amp RV plug is the Honda EU6500. It is rated at 30 Amps for each leg, 60 Amps total. On my Champion 4000Watt, when used on the 240V function, each leg is 15 Amps for a total of 30 Amps if connected to a 50 amp RV adapter plug. As you mentioned, many campgrounds use 50A single phase power and "call it 50 Amp Service" I'd think that with many parks, the upgrade included adding a 50 Amp plug/breaker to the service post at the campsite, but did not include upgrading the underground wiring to handle the extra demand. That may well be the reason for a lot of the low voltage power problems in many campgrounds. Just a guess, I don't have any specifics to say what any particular campground may have done during their upgrade.

Actually, I believe (correct me if I'm wrong) that in order to use all the circuits in a 50 Amp RV, you need both legs of the 240V power. Each leg is connected to separate circuit breakers which power different functions in the RV, some on one leg of 120V and some on the other leg of 120V. So, if all the circuits are to be used at full capacity, then both phases need to be connected. In that scenario, you're right, the total input wattage would be 12,000 watts. Am I missing something?
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 11-18-2011, 04:03 PM   #17
christopherglenn
Senior Member
 
Join Date: Jul 2011
Location: 1 hour from Yosemite
Posts: 165
2 AC's = 3kw
microwave 1kw
tv / satellite / converter 1kw
water heater 1.5kw?
hair drier 1.5kw
washer / drier 2kw
total 10kw
I doubt (shooting high) you could max out a 50 amp service without actually trying to max it out.
__________________
2007 Chevrolet 3500 CC/LB Duramax/Dually 4X4 Mine r4tech, Reese Signature Series 18k +slider, duratrac, titan 62 gallon, diamond eye, Cheetah 64, EFI Live
2008 Chevrolet 2500 CC/SB Duramax 4X4 Hers r4tech, duratrac
2011 Keystone Fusion 405 TrailAir & Triglide, Centerpoint, gen-turi, 3 PVX-840T, XANTREX FREEDOM SW3012, G614
2013 Yamaha 242LS
2010 GMC Yukon The Bus
2005 Chevrolet 2500 CC/SB Duramax 4X4 Hers (sold)
2006 Jayco Jay Flight 31BHS (sold)
christopherglenn is offline   Reply With Quote
Old 11-18-2011, 05:02 PM   #18
hankpage
Site Team
 
hankpage's Avatar
 
Join Date: Jun 2009
Location: Venice
Posts: 5,346
I have found in the past that this site is very helpful when it comes to RV electric questions. Hank
__________________
Hank & Lynn
2007 Cougar 290RKS, E-Z Flex, 16" XPS RIBs ( SOLD .. Gonna miss her ... looking for new 5r)
2004.5 Dodge 2500 QC, LB, 5.9HO, WestTach gauges, Ride-Rite
hankpage is offline   Reply With Quote
Old 12-11-2011, 07:30 AM   #19
whitebb
Junior Member
 
whitebb's Avatar
 
Join Date: Nov 2011
Location: Full Timing
Posts: 4
Looks like a good setup. The only thing both of my storage area are full as i full time. Had mine mounted in the front compartment of my RL 3700. 5.5 Onan propane. Had a 5.5 on my last motor home and carried my load great. We were in North Carolina working camping this year and lost power a lot. Enjoy & be safe
__________________
Ben & Karen
We are long time camping in all kinds of setups

2012 F-350 Ford Dually
2012 Montana RL 3700


whitebb is offline   Reply With Quote
Old 12-11-2011, 08:40 AM   #20
jje1960
Senior Member
 
Join Date: Nov 2010
Posts: 692
Small generator

Felt completely stupid last September at the Richmond Race.... Didn't need the big generator, was nice out, so we were using the 1K Mitsubishi. After a couple of minutes it just died, pop'd it's breaker... Immediately accused my poor wife of turning a toaster on or something..... ran around the trailer for like 15mins checking every possible plug for something that was over-drawing.... Almost gave up... it was definitely something over-drawing, the generator was working fine until plugged in..... Finally hit me.... Mr. Stupid forgot that when we left the house the aircon was on.....
__________________
2011 F350 DRW 4X4
"The Beast"
2011 Cougar 325 SRX
jje1960 is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 05:33 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.