Propane generator problem

I am always suspicious of those 2 tank red/green regulators. It is possible that it will not deliver sufficient flow for the generator. I would check with an authorized Onan service facility (not CW) as to what type of regulator they specify. You may need to have a separate regulator piped in exclusively for the genset and leave the original for the stove/furnace/HWHeater. The genset may actually have an interna regulator to work off of tank pressure directly.

Let us know what you find.
John