Quote:
Originally Posted by sgpa4boys
Unit was just cleaned inside and on top. Air flow is good and always runs on high with all vents open. Guess I will just keep operating until she gives out. Thanks
|
Guessing they did not actually clean the evaporator coil which is the problem most of the time. 27 years fixing these and everyone says they cleaned it all but usually did not get the evap clean.
Not a freon leak.
Possible air short circuiting to return air as mentioned. How close was the amp draw to the RA on compressor tag?