Originally Posted by sgrol View Post
Look in to this:

https://www.microair.net/collections...nt=30176048267

Then you can run a 2000 or 2200 for your AC. I use my Honda 2000 on idle mode to start and run my 15 k unit with the Micro air and it hasn't "blown up" yet.
I actually have a micro air 364... The soft start module is a very good idea, but you must absolutely have or a true 30 amp power supply available, when you program it...

Keep in mind that the Soft-Start module does not change the running amperage/wattage consumption of your air conditioning system... It only eliminates the heavy Spike on Startup that is required to lock the rotor on the compressor...

It takes what would normally be about a 48 to 52 amp Spike and drops it to something tolerable so that you can run not only your air conditioner, but other accessories on the same generator...