Most construction open frame type generators have the ground and neutrals tied together (bonded), so the EMS will not cause any issues with that type generator It's the Honda type inverter generators that have the ground and neutral connections separate that will cause an EMS to see the problem and shut off power. The EMS is looking for what is normally found from a utility fed source such as your house or a pedestal at a campground, and those will have the neutral and ground connected at the main panel, usually where the utility meter is located.