Quote:
Originally Posted by jsb5717 View Post
Without the correct testing equipment it's difficult to diagnose the regulator. We had the same problem and eventually just replaced our regulator which solved our problem. It is possible to have the furnace falter while the other gas appliances work just fine. That's because the furnace's demand for propane requires that the regulator operate at it's maximum flow setting. The other appliances don't require the same propane pressure and can still work fine. If your regulator is weakening then that could be the case.

I'm not confirming that your regulator is the problem...but it is a possibility.
Thanks, I will keep it in mind. Going to check the thermocouple today and if it is getting power I will move to the regulator. Just can't seem to make it make sense that it functions fine in the day but at night acts up (temps anywhere from 15-30.)