Old 06-27-2017, 03:30 AM   #5
Dave W
Senior Member
 
Join Date: May 2015
Location: Near Saratoga Springs,
Posts: 1,131
The only concern I would have is that the extension was a true 3 x #6 and 1 x #8 awg set of conductors. I say this as some of the after market sellers have been using 4 x# 8 awg which, depending on the wire code may or may not be enough ampacity but is marginal in any case. I've had no problem with our pigtail and extension running 2 a/c units and whatever else at 90 feet.