Yes. You're going to be 20AMPs low on available power. You'll only be able to use one A/C at a time, not both. A 50amp system splits the two 120V legs off to two different sections (sort to speak) to enable you to power each of the A/Cs on separate 120V legs. The 30amp power only has one leg, not two. Some of the 120 systems won't have power I believe. If both do have power, you're still under powered for two A/Cs.

Talk to your dealer when you do your PDI. Pick their brain as much as possible and write it down for future reference. (Oh, you'll need a 30amp to 50amp adapter/dog bone)
Thank you!! Very good to know there. I have a nice cache of adaptors going right now. Haven't picked up the 50 amp surge protector yet....looks like i'll need to hit the lottery to afford that one!! haha