Old 01-20-2018, 08:26 AM   #1
gordo
Member
 
Join Date: Jan 2018
Location: Caldwell
Posts: 31
No heat in bedroom

New Montana 3130. Still trying to figure out the switches and things.

Here is the issue. The furnace in the living area works as it should. The furnace in the bedroom, not so much. I set the thermostat, the blower comes on, but no fire. Propane full, everything is as it should be, but no heat upstairs.

This is driving me nuts, Granted, it is not a long trip. Any clues????
gordo is offline   Reply With Quote
Old 01-20-2018, 08:47 AM   #2
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,836
I could be wrong about this, but I don't think you have two furnaces in your RV. It's a 35' fifth wheel and the specs I've found on all of the models online indicate that there is a 35,000 BTU furnace and a 30,000 BTU air conditioner system (2 15K units) and the main A/C is a heat pump. The front A/C is "cool only". So, the "control thermostat" in the bedroom may be the same model as the "heat pump thermostat" in the main area of the RV, and the "heat section" just isn't used.

The furnace heat comes through the floor registers and typically the long duct run and the sharp angles in the ducting cause the floor registers to "barely blow warm air". The ceiling ducting for the A/C units is interconnected so with either unit operating, all ceiling ducts deliver air. If the main unit is on, the heat pump will deliver warm air, but if the front unit is on, it can only deliver cool/ambient air since there is no heat pump capability.

That said, you may have a 5100 BTU "heat strip" in the front unit. Typically that type "electric heating element" doesn't deliver very much warmth and there is almost no noticeable temperature rise when using the "heat strip". On some models that are equipped with a heat strip, the trailer leaves the factory with the heat strip unplugged from the A/C unit. You might find that to be the situation "IF" you have a heat strip.

However, back to your question, it's likely your thermostat in the bedroom doesn't control any heating function and you only have one furnace, located beside the water heater on the road side of your basement area.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 01-20-2018, 09:17 AM   #3
gordo
Member
 
Join Date: Jan 2018
Location: Caldwell
Posts: 31
thanks john

I'll go look for that plug. I guess I was understanding that the thermostat controlled heat up there.
I thought the kid that did the walk through with us said it did.
gordo is offline   Reply With Quote
Old 01-20-2018, 09:20 AM   #4
gordo
Member
 
Join Date: Jan 2018
Location: Caldwell
Posts: 31
Hold on, could it be I need the heat pump on down below to get heat up top....Im sooooo confused
gordo is offline   Reply With Quote
Old 01-20-2018, 09:43 AM   #5
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,836
If (and I believe from the literature they are) the two A/C units are tied in "racetrack configuration" so unless the "main heatpump" is on, there is no heat being delivered to the "racetrack" to be propelled through the system. But, there probably is no need to turn on the bedroom unit to get air delivered from the main unit. Either unit should deliver air through all of the vents. Keep in mind that you can only get "warm air" if the heat pump is operating.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 12-01-2018, 05:34 PM   #6
Jonnyjuno
Junior Member
 
Join Date: Aug 2018
Location: Whittier
Posts: 17
I just bought a 2019 3700lk same issue except no fan or anything main ac has heat pump main thermostat controls furnace. upstairs bedroom thermostat only controls ac in bedroom although it has furnace option it does not operate the furnace. Which happens to suck a lot because it’s cold in the main living area heat pump set to 66 and the bedroom is at around 70°
Jonnyjuno is offline   Reply With Quote
Old 12-02-2018, 07:33 AM   #7
ctbruce
Site Team | Emeritus
 
ctbruce's Avatar
 
Join Date: Dec 2015
Location: Kansas City
Posts: 3,878
Quote:
Originally Posted by Jonnyjuno View Post
I just bought a 2019 3700lk same issue except no fan or anything main ac has heat pump main thermostat controls furnace. upstairs bedroom thermostat only controls ac in bedroom although it has furnace option it does not operate the furnace. Which happens to suck a lot because it’s cold in the main living area heat pump set to 66 and the bedroom is at around 70°
Do you have the electric heating element in your unit? You'll have to take the cover off and look. It will have fins and be towards the front of the unit. Usually they are not plugged in and don't work. The plug on mine was on the right side of the unit.
__________________

Chip Bruce, RPh
Kansas City, MO
2016 Impact 312
2017 Silverado 3500HD SRW
ctbruce is offline   Reply With Quote
Old 12-02-2018, 09:53 AM   #8
Jonnyjuno
Junior Member
 
Join Date: Aug 2018
Location: Whittier
Posts: 17
Quote:
Originally Posted by ctbruce View Post
Do you have the electric heating element in your unit? You'll have to take the cover off and look. It will have fins and be towards the front of the unit. Usually they are not plugged in and don't work. The plug on mine was on the right side of the unit.
I am going to have to look now I have the whisper quiet which is not actually THAT quiet in the bedroom trying to sleep haha but it is noticeably quieter
Jonnyjuno is offline   Reply With Quote
Old 01-20-2018, 12:00 PM   #9
travelin texans
Senior Member
 
travelin texans's Avatar
 
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
If your talking furnace, warm air from floor vents, you should only have one. On mine the bedroom furnace duct work had came loose from register & had to remove basement wall to reattach.
If talking heat pump, warm air from ceiling vents, then if it's 40 degrees or less outside it will blow cold air not warm. If you have your thermostat set to "elec" it should run the heat pump until ambient temperature inside falls to 3-5 degrees below set temperature then gas furnace will start up. Also if thermostat is on "elec" when you turn it on if you set t stat more than 3-5 degrees above what the temp shows inside the furnace will start til it warms to t stat setting then the heat pump will take over.
I hope you can make sense of this, it's not as complicated as it sounds.
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
travelin texans is offline   Reply With Quote
Old 01-20-2018, 02:14 PM   #10
gordo
Member
 
Join Date: Jan 2018
Location: Caldwell
Posts: 31
Well,
The dealer called, and said that the bedroom thermostat on provides a/c to the bedroom. The heat is supplied by the living room thermostat. That being said, it would make sense that very little warm air makes it to the bedroom heat ducts.

Sounds like B/S to me, but I'm willing to make a few tests. If I block one of the living area ducts, more air will go to the bedroom....We will see...
gordo is offline   Reply With Quote
Old 01-20-2018, 02:32 PM   #11
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,836
What the dealer told you isn't BS. It's what I attempted to explain above and the way every trailer with two roof units, one of which is a heat pump and one that is a conventional A/C works. They all do the same.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 01-20-2018, 03:02 PM   #12
Pull Toy
Senior Member
 
Pull Toy's Avatar
 
Join Date: Mar 2015
Location: Southeastern Connectiut
Posts: 1,305
For what it's worth... our heat pump is useless below 40deg +/-. You need the furnace and or fireplace heater, and/or heat strips, (if equipped) when it's cold. Heat pump or heat strip will deliver warmth from the ceiling, The furnace is in the floor vents.

If your furnace is providing warm air downstairs, but not upstairs, your problem is probably the ducting to the upstairs floor registers. I would check my duct connections, and also check for kinks. Zip tie, or preferably duct tape, or clamp all register connections to keep them in place.

When it's really chilly, we throw down towels or area rugs over the floor vents where we "are not" forcing/directing thewarm air to where "we are".



Good Luck,
__________________

Pull Toy

Steve & Jan, Ava & Emma (Mini Schnauzers):
2016 F350 Lariat 4X4 Powerstroke CC/SB "PULLTOY V"
2013 Alpine 3535RE "MAGIC CARPET IV"
Proud Navy Vet!
Pull Toy is offline   Reply With Quote
Old 01-20-2018, 03:11 PM   #13
gordo
Member
 
Join Date: Jan 2018
Location: Caldwell
Posts: 31
Quote:
Originally Posted by JRTJH View Post
What the dealer told you isn't BS. It's what I attempted to explain above and the way every trailer with two roof units, one of which is a heat pump and one that is a conventional A/C works. They all do the same.
Now that I have re-read what you posted, and you are right. I just get frustrated with dealing with them.

I will go take a look at the duct work too. It could be disconnected somewhere.

Thanks to all for the good advise. Now I just need to get my truck, get it set up for the tow, so we can go.
gordo is offline   Reply With Quote
Old 01-20-2018, 06:30 PM   #14
IRV2
Senior Member
 
Join Date: Oct 2017
Location: Acton
Posts: 127
Yes check the ducting

Sometimes this can happen. We wondered why we weren't getting warm air from this register. Our brand new 5er.
Attached Thumbnails
Click image for larger version

Name:	IMG_0300.JPG
Views:	550
Size:	36.2 KB
ID:	15127  
__________________


2018 Keystone Laredo 298RL
2003 Keystone Laredo 27RL
2019 Ram 3500 Laramie DRW
IRV2 is offline   Reply With Quote
Old 02-13-2018, 07:02 PM   #15
Johnko
Junior Member
 
Join Date: Jan 2018
Location: Leesburg
Posts: 10
You say that blower comes on but no fire. I'm assuming you mean that that propane furnace burner does not come on. A wasp had built a nest in the furnace exhaust on my Montana. I had to remove the cover and clean it out. There is a sensor in the exhaust and intake to make sure you have air flow to the furnace before the burner will light.
Johnko is offline   Reply With Quote
Old 02-16-2018, 06:08 AM   #16
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,714
Quote:
Originally Posted by gordo View Post
Now that I have re-read what you posted, and you are right. I just get frustrated with dealing with them.

I will go take a look at the duct work too. It could be disconnected somewhere.

Thanks to all for the good advise. Now I just need to get my truck, get it set up for the tow, so we can go.
Hang in there gordo it will get better. As much as I dislike dealers you can't get frustrated with them because you don't understand what they are telling you. This is a common issue with the industry as things in a camper don't work the same way as in a stick and brick house. The industry compounds the issue by poorly integrating systems that don't play well together or are not intuitive to operate, referring to OE instructions that may read like a 1980's Chinese toy assembly book. This forum is an excellent resource as the members here are not only willing to help but have most likely "been there done that" with the issue that you are facing and can save you much time and frustration. Enjoy your new fiver and travel safe.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is online now   Reply With Quote
Old 01-22-2018, 06:00 AM   #17
rhagfo
Senior Member
 
rhagfo's Avatar
 
Join Date: Apr 2012
Location: Portland, OR
Posts: 4,176
Quote:
Originally Posted by gordo View Post
Well,
The dealer called, and said that the bedroom thermostat on provides a/c to the bedroom. The heat is supplied by the living room thermostat. That being said, it would make sense that very little warm air makes it to the bedroom heat ducts.

Sounds like B/S to me, but I'm willing to make a few tests. If I block one of the living area ducts, more air will go to the bedroom....We will see...
Not sure how your ducts work, if all is run through a rigid floor duct or the flexible type like IRV2 has.
At this point is is time to remove registers and if rigid, use a mirror to check for obstructions. The other thing to look for is poor connections.
Our bedroom is on a rigid duct connected to the under floor duct, that connection leaked so much we had very poor circulation to the bedroom.
Get a roll of good quality foil duct tape, and seal every leak.
__________________
Russ & Paula and Belle the Beagle.
2016 Ram Laramie 3500 DRW 14,000# GVWR (New TV)
2005 Copper Canyon 293 FWSLS 32’ GVWR 12,360
Visit and enjoy Oregon State Parks
rhagfo is offline   Reply With Quote
Old 01-21-2018, 04:43 AM   #18
Tinner12002
Senior Member
 
Tinner12002's Avatar
 
Join Date: Aug 2017
Location: Lafayette
Posts: 1,068
If the thermostat is anything like mine, which will take some time getting used to, when you go to heat, it will show elec or gas. If you go the elec route then yes as others have mentioned you should have warm air from ceiling vents. If you select gas then your furnace will run supplying warmer air from the floor vents which you should have possibly a couple of in your bedroom, upper units don't run when you use the gas or furnace option.
__________________
2015 Ram,3500,Dually,B&W,4.10s,Aisin,Limited,Silver
2018 Raptor,428SP w/full body paint
2012 Harley, Ultra Limited
Tinner12002 is offline   Reply With Quote
Old 02-13-2018, 08:19 PM   #19
travelin texans
Senior Member
 
travelin texans's Avatar
 
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
You will only have 1 furnace regardless of how many thermostats you have. If more than 1 has a "heat" setting then it's either a heat pump, has heat strips or just a universal thermostat that does absolutely nothing for heat.
Agree the furnace ONLY blows from floor vents, heat pumps/heat strips/ac ONLY from ceiling vents.
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
travelin texans is offline   Reply With Quote
Old 02-14-2018, 03:35 AM   #20
jimhardenbrook
Junior Member
 
Join Date: Nov 2017
Location: Box Elder
Posts: 2
Mine had little heat from. Bedroom floor vent.

Round silver type air hose had slipped off furnace. Removed drawers and re-attached silver duct and fixed. SIMPLE


Sent from my iPhone using Tapatalk
jimhardenbrook is offline   Reply With Quote
Reply

Tags
bed, bedroom, heat

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 05:51 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.