When I am plugged in to 110 and turn my gen on to run say the coffee pot, does the gen override the 110 power or do I need to always unplug first?
Thanks Jeannie
|
|
|
08-29-2019, 07:27 PM
|
#2
|
Site Team
Join Date: Jul 2014
Location: Modesto
Posts: 20,351
|
Most transfer switches are designed to “default” to the generator. If your plugged into shore power, you shouldn’t need the gen.
__________________
2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.
Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
|
|
|
08-29-2019, 08:16 PM
|
#3
|
Senior Member
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
|
Quote:
Originally Posted by chuckster57
Most transfer switches are designed to “default” to the generator. If your plugged into shore power, you shouldn’t need the gen.
|
That was my question.
Why would you start the generator if you're plugged into shore power? You won't double the amps!
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
|
|
|
08-29-2019, 10:09 PM
|
#4
|
Senior Member
Join Date: Jul 2013
Location: Box Elder
Posts: 2,910
|
If it was possible to feed both the power from a pedestal and a generator at the same time, either the generator or the pedestal power will trip out because, even though both sources would be providing 120 volts, they would be out of sync of the frequency or the actual voltage, and you would be backfeeding power into the utility system which is extremely dangerous which can and has killed utility line workers, one that I worked with years ago.
__________________
Bob & Becky
2012 3402 Montana
2012 Chevy 2500HD D/A CC
|
|
|
08-30-2019, 06:03 AM
|
#5
|
Junior Member
Join Date: Feb 2019
Location: Ontario
Posts: 7
|
Because what I am plugged into is not enough power to run the coffee pot or hair dryer etc. That is why I posted the question. If I need to unplug then that's ok and what I need to know.
If you read the question, I am plugged into 110 not 30 or 50. I would never turn gen on when plugged into 30 or 50.
|
|
|
08-30-2019, 06:42 AM
|
#6
|
Site Team
Join Date: Mar 2011
Location: Gaylord
Posts: 26,997
|
IF (note all caps) you have an automatic transfer switch that automatically disconnects the shore power from the trailer power center when the generator comes online, then NO, you don't have to disconnect the trailer from shore power, the transfer switch does it for you.
IF (again all caps) you do not have an automatic transfer switch (manual switch or no switch at all) then you need to disconnect shore power BEFORE bringing the generator online. If you fail to do that, you'll be feeding 120VAC from shore power AND 120VAC from generator power to the power center "main circuit breakers"... Depending on how they are wired, you'll probably damage the generator (backfeeding power to it) or damage appliances and accessories connected to the circuit breakers inside the trailer. The input "could be wired" a number of ways, potentially providing 240VAC to the main circuit breakers which "could destroy your electrical system, the generator or send unwanted power into the campground electrical grid".
__________________
John
2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
|
|
|
08-30-2019, 06:52 AM
|
#7
|
Senior Member
Join Date: Dec 2017
Location: Lisbon
Posts: 551
|
Quote:
Originally Posted by jbiggers
Because what I am plugged into is not enough power to run the coffee pot or hair dryer etc. That is why I posted the question. If I need to unplug then that's ok and what I need to know.
If you read the question, I am plugged into 110 not 30 or 50. I would never turn gen on when plugged into 30 or 50.
|
What are you plugged in to? Any regular outlet should be more than adequate to run a coffee pot or hair dryer. Are you using a long extension cord?
__________________
2018 Keystone Cougar 22RBS
2020 Ford F-350 XLT SC SRW 6.7l Powerstroke.
|
|
|
08-30-2019, 07:00 AM
|
#8
|
Junior Member
Join Date: Feb 2019
Location: Ontario
Posts: 7
|
Thank you ! That makes sense. I will find out what I have.
|
|
|
08-30-2019, 08:00 AM
|
#9
|
Senior Member
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
|
Quote:
Originally Posted by jbiggers
Because what I am plugged into is not enough power to run the coffee pot or hair dryer etc. That is why I posted the question. If I need to unplug then that's ok and what I need to know.
If you read the question, I am plugged into 110 not 30 or 50. I would never turn gen on when plugged into 30 or 50.
|
Hopefully you're plugged into 110 volt & not 220! If you're plugged into your house or a park pedestal, yes your plugged to 110 volts, depending on your RV it's either 30 or 50 amp service. If your RV is a 30 amp service it's doubtful you could run more than a couple high amp appliances (ac, microwave, coffee pot, hairdryer) at the same time. If at home plugged into a regular plug with an extension cord it could be 15, 20, 30 amps depending on the breaker & won't run but 1 of those items at a time, maybe. Depending on your generator you still may not be able the run them all with it either.
This probably sounds confusing, after reading your post you apparently don't know what you have or anything about electricity so be very careful, probably need some assistance from someone that knows what they're doing.
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
|
|
|
08-30-2019, 06:13 PM
|
#10
|
Junior Member
Join Date: Feb 2019
Location: Ontario
Posts: 7
|
I have a 50 amp trailer and cord. I know on 10 amp service you can only run minimal things 1 at a time and some things like ac, coffee pot, hair dryer etc never. I made the mistake as saying 110 which was incorrect. I needed to be talking in amps instead. I do have a switch and I am fine staying plugged in as my unit will make the switch. Thank you all for your help!!
|
|
|
08-30-2019, 06:22 PM
|
#11
|
Site Team
Join Date: Jul 2014
Location: Modesto
Posts: 20,351
|
Quote:
Originally Posted by jbiggers
I have a 50 amp trailer and cord. I know on 10 amp service you can only run minimal things 1 at a time and some things like ac, coffee pot, hair dryer etc never. I made the mistake as saying 110 which was incorrect. I needed to be talking in amps instead. I do have a switch and I am fine staying plugged in as my unit will make the switch. Thank you all for your help!!
|
Saying 110 wasn’t incorrect, just incomplete. Your plugged into 110, even if your plugged into a 50A source. 50A is a bit misleading as it’s actually 2 “legs” of 50A for a total of 100A of 110VAC. It can get confusing for some, not pointing a finger at you. One of the great things about forums like this one is the ability to gain lots of knowledge for an affordable cost.
__________________
2012 Copper Canyon 273FWRET being towed by a 1994 Ford F350 CC,LB,Dually diesel.
Airlift 5000 bags, Prodigy brake control, 5 gauges on the pillar.Used to tow a '97 Jayco 323RKS.
Now an RVIA registered tech. Retired from Law enforcement in 2008 after 25+ yrs.
|
|
|
08-31-2019, 05:13 AM
|
#12
|
Senior Member
Join Date: Dec 2018
Location: grand rapids
Posts: 596
|
Gee, I was just getting started on what?????
I really never heard of a circuit just being 10 amps. Something isn't normal. It must be an old old system.
As for the coffee pot, take it outside and just run a direct line to the coffee pot from the gen.
|
|
|
09-05-2019, 07:50 AM
|
#13
|
Member
Join Date: Apr 2019
Location: Panama City
Posts: 75
|
Be on the safe side and unplug from shore power! The sync is unbalanced and can cause problems. There is always a chance of back feed to the power grid. With the generator you can generate overhead line voltage which is over 1000 volts and can kill utility workers!!!
|
|
|
09-05-2019, 08:22 AM
|
#14
|
Senior Member
Join Date: Jul 2011
Location: Lehigh Acres
Posts: 176
|
That must be one hell of a coffee pot to use that much juice.
__________________
Rick and Sandy
2017 Toyota Platinum Tundra 4X4
2011 Bullet Premier 19FBPR
|
|
|
09-05-2019, 10:40 AM
|
#15
|
Member
Join Date: Nov 2013
Location: Calgary
Posts: 58
|
15a
Generally speaking, the lowest circuit in North America is 15amps. Every campground will run a dedicated 15A circuit to each campsite. I would be really surprised that you'd have to start your gen to make coffee in the morning while plugged in to shore power.
I would always start by trying it out first on shore power. If doing that trips the breaker to the campsite (no big deal) then you'd know to reduce the load (set fridge to propane, turn off the TV, etc) next time.
In a campground that has power sites, none of your neighbors will appreciate hearing a generator fire up at whatever time in the morning while you make your coffee.
|
|
|
09-05-2019, 11:03 AM
|
#16
|
Junior Member
Join Date: Sep 2019
Location: Lawrence
Posts: 23
|
I've always been a gauge weenie when it comes to power cords, and I've noticed even my fat cords can get hot near the connections. My question is this: Might there be any corrosion starting in an aging cord, or might the connectors be a bit on the skimpy side? This might make a difference, based on the weakest link theory.
Coffee is my essential heart starting fluid, so I pay close attention here!