120v or 240v at 50amp receptacle?

So the tech just left and advised me that my RV plug shouldn't be wired with different phases going into the coach? It doesn't make much sense to me to have a plug with the ability to spread the load out and load it all on one phase at the breaker... enlighten me... I'm a lineman by trade and my way makes sense, but i'm willing to learn
Lateagain is offline   Reply With Quote
Old 07-06-2017, 08:01 AM   #2
Terry W.
Senior Member
 
Terry W.'s Avatar
 
Join Date: Mar 2012
Location: Pickens, SC
Posts: 326
Ok I wired my with 2 120v legs 1 neutral 1 ground and all is well. So says the meter and surge protector

Sent from my XT1585 using Tapatalk
__________________
https://www.keystonerv.org/forums/pic...pictureid=1416 Terry & Kathy
2012 Avalanche 330RE
2006 F250 Super Crew Chipped, K&N
2-11 Pound 4 Legged Furry Childern
Pickens, SC
Terry W. is offline   Reply With Quote
Old 07-06-2017, 08:04 AM   #3
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,741
It is a split phase connection. This may help. http://photobucket.com/gallery/user/...MS5qcGc=/?ref=
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 07-06-2017, 08:16 AM   #4
Lateagain
Junior Member
 
Join Date: Jun 2017
Location: St Pete
Posts: 7
Thanks for assuring me I'm not crazy...
__________________
2016 Ram 3500
2017 Impact 361
Lateagain is offline   Reply With Quote
Old 07-06-2017, 08:19 AM   #5
Racebug
Senior Member
 
Join Date: Mar 2017
Location: Petersburg, KY
Posts: 276
I would assume it could also be wired off the same leg still with 2 50 amp breakers?
__________________

2017 Fuzion 417
2018 Ram 3500 Longhorn
Racebug is offline   Reply With Quote
Old 07-06-2017, 09:17 AM   #6
Lateagain
Junior Member
 
Join Date: Jun 2017
Location: St Pete
Posts: 7
Quote:
Originally Posted by Racebug View Post
I would assume it could also be wired off the same leg still with 2 50 amp breakers?
I would think so, his concern was that opposing phases would damage chargers, inverters and electronics... my concern was only chargers and inverters if he was correct.
__________________
2016 Ram 3500
2017 Impact 361
Lateagain is offline   Reply With Quote
Old 07-06-2017, 11:25 AM   #7
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,981
Your electrician isn't "crazy" and neither are you. I'd make a guess that he was talking about wiring for a 30 amp RV plug vs a 30 amp "dryer plug". One is single phase, 120 VAC (RV) and the other is two phase, 240 volt (dryer). Physically the plugs look the same, but severe damage would be done to your RV if you plug the power cord into a "dryer plug"....

ALL 50 amp RV plugs are "two hot lines" a neutral (common) and a ground. Measuring across the two hot leads will read 240 VAC and from either hot lead to neutral or ground will read 120. (that's the same as a 30 amp dryer plug).

An RV plug will read 120 VAC from the hot lead to either the neutral or ground and 0 VAC from the neutral to ground.

So, in all probability he was talking about his experience wiring a 30 amp RV plug and didn't explain the difference between 30 and 50 amp RV plugs......
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 07-07-2017, 04:52 AM   #8
xcntrk
Senior Member
 
xcntrk's Avatar
 
Join Date: Jun 2016
Posts: 252
He's talking about the different types of 240v circuits. Take a welder or even the OLD style dryer plugs. They have only 3-prongs, 2 are 120v hot (high and low side wave) and one is ground. No need for neutral as the appliances on this circuit use both 120v waves (aka a single 240v phase). Now take your modern dryer or RV plug. It's 4-prong with the addition of the neutral. That's because portions of the appliances running on that plug need 120v (requiring the neutral) and portions require the full 240v. This is where you get both 120v and 240v phases simultaneously.

A perfect example is a modern electric dryer. The display, light, and general electronics run on 120v power while the heater & motor run on 240v. All this comes from the same plug and the addition of the neutral allows the 120v side to operate correctly.

To make it more confusing, all of the appliances including the 15k btu AC's, in your 5th wheel are 120v devices. When they're all running (including x2 AC units) the amp demand is greater than a typical 120v circuit can support. Therefore the RV uses the 50-amp 240v circuit to in effect bring into the coach TWO independent 120v circuits in order to meet the load. This is the both phase requirement being mentioned, the high wave phase and the low wave phase, just like a panel box at home.

Or something like that
__________________
2015 F350 LARIET CCSB SRW PSD
2017 KEYSTONE FUZION 325


xcntrk is offline   Reply With Quote
Old 07-07-2017, 05:10 AM   #9
xrated
Senior Member
 
xrated's Avatar
 
Join Date: Oct 2016
Location: "Murvil, TN
Posts: 2,210
50Amp RV Plug supplies......
One 50amp (120volt) line using one of the hot lines to neutral.
One 50amp (120volt) line using the other hot line to neutral

Total wattage available....12,000W
This of course is assuming that everything is wired correctly, in good operation condition, and the power pedestal has the proper size feed to it that supplies the power to the RV receptacle on it.

And you are correct, it is the same type setup that is used in service entrances for your house, a single phase center-tapped transformer providing the power.
__________________
2016 F350 King Ranch Crew Cab Dually Diesel 4x4
2018 Grand Design Momentum 394M
2023 Suzuki GSX-S1000GT+
Excessive payload capacity is a wonderful thing

"If it ain't Fast....It ain't Fun"
xrated is offline   Reply With Quote
Old 07-07-2017, 02:12 PM   #10
Bob Landry
Senior Member
 
Join Date: Jan 2011
Location: Austin, Tx
Posts: 1,910
A common misconception on phase... 240 service is not dual phase. It's still single phase power. When an electrical source is said to be multi-phase, that refers to voltage and current component of the sine wave being out of phase with each other. The voltage is still 60HZ with the two halves of the sine wave being 180 degrees out of phase with each other, but voltage and current remain in phase. Multi phase power is used mostly in commercial equipment to increase starting torque of large electric motors, seldom if ever in residential or recreational equipment.
__________________
2011 Outback 277RL
2013 F250 XLT Crew Cab 6.2L

Bitter Gun Owner
Bitter Clinger
Armed Infidel
Bob Landry is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 09:14 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.