Old 01-07-2019, 07:44 AM   #1
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
Adding a 120v power outlet to a slide wall?

We have a 2019 Cougar half-ton 26RBSWE. The trailer has a single slide which includes both the dinette and theater seating areas.

The problem is that there is no 120v outlet anywhere near the dinette. I would really like to have one along the inside of the outer wall, just below the table level (or above, really) - to plug in things like laptops, phone charges, etc.

Is this a difficult thing to do, given it's a slide wall? I'm not sure I want to tackle this myself (without some coaching, anyway), so is this something I can get a service/repair place to do for me? What can I expect it to cost?

Thanks,
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 01-07-2019, 08:40 AM   #2
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,739
Start by extending the slide and crawl under it and take a look. If you have a cable installed for the slide motor and or side clearance light then you may be able to attach your wire to it. If not, then you will have to engineer that. I would use a surface mount box and not disturb the slide out wall. This is the type cable I'd use https://www.automationdirect.com/adc...jeoow-14-3bk-1
Next challenge would be getting the wire to the electrical panel. A 15 amp breaker should be easy to source. I have no idea on cost to do it by a tech but given their hourly rate prepare for $300 - $400 in my thinking. I'm sure others will chime in.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 01-07-2019, 08:46 AM   #3
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
By attaching to the existing slide cable, I assume you mean just for routing purposes, not electrical connection, right? Just want to make sure we're on the same page.


I guess to get access to the breaker panel, I'm going to have to go up under the coro-plast bottom cover and look for other wires going up in the same general area? I've not looked under there yet...
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 01-07-2019, 09:12 AM   #4
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,974
The coroplast only covers the area between the frame rails. The 15" (or so) on the outer sides of the bottom are not covered. Rather than pull the coroplast, it would be easier to run the new romex from the breaker panel to the edge of the trailer above the floor, through the back of cabinets (if possible) and then drill a small hole in the floor so the romex comes out under the trailer side "outside the frame rails". You won't have the coroplast to deal with and the romex will be closer to the actual area where you'll want it.

DON'T USE ROMEX on any moving parts, using the slide will eventually fatigue the copper single strand wires and cause failure. Install a junction box to the underside of the floor directly under the hole you drilled and wire a multistrand flexible wire (think 12 gauge extension cord) from there to a hole in the floor of your slide. MAKE SURE IT WON'T BE PINCHED OR CUT WHEN THE SLIDE MOVES IN !!!!! Determine how to support the flexible wire during travel such as a spring to keep it tight or a slide wiring guide to fold when the slide moves in. Then, mount a wire guide on the inside wall of the slide from that hole to the point where you want the outlet and install a "shallow outlet box" on the wall, wire your outlet and you're ready to plug in.

You can peek under almost any RV slide to see how the wire guides are used to manage keeping the wire "folded/extended" to prevent damage during travel.

I would NOT recommend trying to run wires through the slide walls. Most are vacuum formed sandwich construction and it is very difficult to drill through them and run romex. Think about drilling through an aluminum tube frame member, the sharp edges you will make with the drill and the insulation on the romex vibrating against those sharp edges.... There's no way to install rubber hole protectors inside the wall to protect the romex from being damaged.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 01-07-2019, 09:21 AM   #5
Steveo57
Senior Member
 
Join Date: Dec 2017
Location: Lisbon
Posts: 551
Instead of going back to the panel and adding a breaker I would look at existing outlets and see if it would be easier to tie into one nearby.

Instead of adding a new outlet in my slide I just got a power strip with a long cord on it and position it where I need it. I only use it for small things like charging phones etc so I think it's safe and it gives me flexibility to move it around if I need to.
__________________
2018 Keystone Cougar 22RBS
2020 Ford F-350 XLT SC SRW 6.7l Powerstroke.
Steveo57 is offline   Reply With Quote
Old 01-07-2019, 09:24 AM   #6
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
Thanks for the responses. There is an existing outlet in the non-moving wall next to the slide that should be easy to tap into - if I want to go forward with the built-in solution.

Extension cords sound easy, of course, but I hate having the cord on the floor where it can be a tripping hazard. This is what I'm doing today, however
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 01-07-2019, 10:11 AM   #7
Steveo57
Senior Member
 
Join Date: Dec 2017
Location: Lisbon
Posts: 551
The only problem with tieing in to an existing outlet is if they used a self contained outlet. A special tool is used to push the wires in usually. What I did is just cut out the outlet and put an old work box in with a regular outlet.

The other option I've used is to go with some type of wiremold surface mount cable raceway to run wires where it's hard or impossible to run through walls etc.Click image for larger version

Name:	hqdefault.jpeg
Views:	376
Size:	10.7 KB
ID:	19806
__________________
2018 Keystone Cougar 22RBS
2020 Ford F-350 XLT SC SRW 6.7l Powerstroke.
Steveo57 is offline   Reply With Quote
Old 01-07-2019, 11:27 AM   #8
travelin texans
Senior Member
 
travelin texans's Avatar
 
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
Quote:
Originally Posted by MarkEHansen View Post
By attaching to the existing slide cable, I assume you mean just for routing purposes, not electrical connection, right? ...
Hopefully so, both of those items are 12 volt so won't be much help to what you want to do.
There's plastic wire channel sold at most home improvement stores that sticks on the wall that you could tie into an existing plug & run the wires in this plastic channel to hide it. The most difficult part would be revamping the existing box.

Name:   086698003790md.jpg
Views: 2419
Size:  24.7 KB
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
travelin texans is offline   Reply With Quote
Old 01-07-2019, 12:11 PM   #9
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,739
Quote:
Originally Posted by MarkEHansen View Post
By attaching to the existing slide cable, I assume you mean just for routing purposes, not electrical connection, right? Just want to make sure we're on the same page.


I guess to get access to the breaker panel, I'm going to have to go up under the coro-plast bottom cover and look for other wires going up in the same general area? I've not looked under there yet...
Yes, for routing purposes only. I thought that was self explanatory with "connecting at the panel". The other advice on not drilling into the slide wall and using wiremold, a surface mounting system for wire and outlet are also the same advice as my original response. I'm not familiare with where your electrical panel is so I can't advise on the need to remove the coroplast or not. Whichever route, make certain the wire is well secured.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 01-07-2019, 12:37 PM   #10
retiredusps69
Member
 
Join Date: Jun 2018
Location: Hewitt
Posts: 73
Outlet

We had almost the same problem on another brand of trailer. I mounted a box and outlet under our counter on the kitchen slide.Then ran the wires to a covered 110 male recepiticle. We then use a 110 power cord to the camp ground breaker box. Wife uses for slow cooker, coffee pot,Etc. We always were tripping the breaker when running the Air cond and water heater at the same time.
retiredusps69 is offline   Reply With Quote
Old 01-07-2019, 12:58 PM   #11
wiredgeorge
Senior Member
 
wiredgeorge's Avatar
 
Join Date: Nov 2017
Location: Mico, TX
Posts: 7,444
The slide represents some challenges if you want a 117V outlet. My slide has one built onto the bottom (not convenient) of the dinette booth. It is there an I use an extension cord. You very well may not have AC current in your slide but in mine, the two lights over the dinette and sofa are 117V AC with odd bulbs. Take a look at all the lights in your slide and if one is AC, pull power from there and go outside using channel to a place where a surface mount outlet could be installed in the slide.
__________________
wiredgeorge Mico TX
2006 F350 CC 4WD 6.0L
2002 Keystone Cougar 278
2006 GL1800 Roadsmith Trike
wiredgeorge is offline   Reply With Quote
Old 01-07-2019, 02:48 PM   #12
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
We do have lights in the slide, but all 12V.
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 01-07-2019, 03:29 PM   #13
wiredgeorge
Senior Member
 
wiredgeorge's Avatar
 
Join Date: Nov 2017
Location: Mico, TX
Posts: 7,444
Some of the lights; that is, the wall sconces in my slide are 12V but the overheads are 117V. Couldn't figure that out. The bulbs in the 12V fixtures, like the rest of my old trailer, are incandescent but look like car taillight bulbs; 1156 type but the prongs stick out straight rather than offset like a car bulb. They can be had at autoparts stores and I can't recall their number but I bought an extra.
__________________
wiredgeorge Mico TX
2006 F350 CC 4WD 6.0L
2002 Keystone Cougar 278
2006 GL1800 Roadsmith Trike
wiredgeorge is offline   Reply With Quote
Old 01-13-2019, 08:52 AM   #14
PKONolan
Junior Member
 
PKONolan's Avatar
 
Join Date: May 2014
Location: Colorado
Posts: 14
Try Stationary Wall Next to Slide

I am going to install one in our 24 foot bunk house in the stationary wall immediately next to the slide which is close enough for computer and tablet chargers but avoids the problems with a moving outlet. It looks like there is one in the wall immediately under the refer on your type of unit so that may not be close enough for your purposes. Ours will allow me to avoid stringing the cord into the bathroom (shockingly the closest outlet to that side of the table). The other benefit for doing it that way is that this wall encloses the electrical panel which will make wiring very easy.
PKONolan is offline   Reply With Quote
Old 01-13-2019, 10:26 AM   #15
apachewolf
Senior Member
 
Join Date: Aug 2015
Location: Tucson
Posts: 117
Quote:
Originally Posted by MarkEHansen View Post
We have a 2019 Cougar half-ton 26RBSWE. The trailer has a single slide which includes both the dinette and theater seating areas.

The problem is that there is no 120v outlet anywhere near the dinette. I would really like to have one along the inside of the outer wall, just below the table level (or above, really) - to plug in things like laptops, phone charges, etc.

Is this a difficult thing to do, given it's a slide wall? I'm not sure I want to tackle this myself (without some coaching, anyway), so is this something I can get a service/repair place to do for me? What can I expect it to cost?

Thanks,
Installing a 120VAC outlet in the slide is a bit of work. I ran flat plastic conduit along the wall and at each end I installed an surface mount box with the outlet. At the first box I attached a short pigtail with a plug that is plugged into a short extension cord tucked in between the carpet and the wall. That cord is plugged into the outlet by the bed side. That cord stay in place all the time. The pigtail is only attached to the cord AFTER the slide has been extended. This works like a charm and the setup cost me around $20.00. So I am running off one of the 15A outlets and therefore protected and as long as you remember to unplug the pigtail before retracting the slide you are OK.
Attached Thumbnails
Click image for larger version

Name:	DSCN7499.jpg
Views:	319
Size:	252.2 KB
ID:	19874   Click image for larger version

Name:	DSCN7502.jpg
Views:	313
Size:	293.3 KB
ID:	19875  
apachewolf is offline   Reply With Quote
Old 01-13-2019, 10:33 AM   #16
cbmfire
Junior Member
 
Join Date: Sep 2018
Location: Durham
Posts: 10
We have the exact same camper. I was thinking of just running a drop cord behind recliners to a strip Velcroed to the wall or dinette back. Wife mainly plugs in a make up mirror while sitting there putting on makeup. Keep us posted on what you end up doing.
cbmfire is offline   Reply With Quote
Old 01-13-2019, 10:35 AM   #17
hankpage
Site Team
 
hankpage's Avatar
 
Join Date: Jun 2009
Location: Venice
Posts: 5,346

Wire-Mold products will allow you to mount an outlet where you want it. If you are drilling holes in the carpeted floor be sure to cut an X in the carpet before drilling or the drill will pull a strand from the carpet very quickly. (Don't ask me how I know this)
In my case the power was there but you can get a general idea of how it looks and they are paint-able.
__________________
Hank & Lynn
2007 Cougar 290RKS, E-Z Flex, 16" XPS RIBs ( SOLD .. Gonna miss her ... looking for new 5r)
2004.5 Dodge 2500 QC, LB, 5.9HO, WestTach gauges, Ride-Rite
hankpage is offline   Reply With Quote
Old 01-13-2019, 01:43 PM   #18
larryflew
Senior Member
 
larryflew's Avatar
 
Join Date: Feb 2014
Location: Young America MN
Posts: 372
No matter where you get your power from a 14/3 SO or SOW cord for the part that is moving will last forever. We build a sliding gate that moves 10 times a day that so far is at the 10 year mark.
larryflew is offline   Reply With Quote
Old 01-13-2019, 05:04 PM   #19
Cracker727
Junior Member
 
Join Date: Jun 2018
Location: Damascus
Posts: 6
2019 Cougar 25RES Slide Outlet Location

On our Cougar, we have a 120 outlet in our slide under the forward seat cushion of our dinette. It has proven to be very useful even though you do have to get on your hands and knees to plug a cord into it. My wife who “quilts” uses it for her sewing machine power. (2018 Cougar not 2019, sorry)
Cracker727 is offline   Reply With Quote
Reply

Tags
power, slide

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 08:48 AM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.