Old 07-22-2019, 06:30 AM   #1
Skins44
Member
 
Join Date: Dec 2018
Location: Maryland
Posts: 87
AC Breaker and Power

camping in 100+ heat in Delaware over the weekend. Around 6pm Saturday, things got quiet in the camper (2017 276UBH - 30 amp). AC went out and lights got dim. AC breaker tripped. Pretty sure i know why...2 TV's on and streaming (kids relaxing watching TV after 7 hours on the beach), AC pumping, fridge on, iphone and tablet charging, lights on (so assuming converter was pulling amps) and 2 strands of palm tree lights (not LED) plugged in outside. Add all that up and pretty sure i was well over 30 amps.

reset the AC breaker, unplugged some things and was good. AC was back on.

My question, why did the lights dim if they run off of the battery? Also, checked my battery level on the panel and it was 1 bar (very low). Gradually, lights went back to normal and battery level showed full.

I wont get into the campground power going out at 3am! let's just say i got an early jump on the trip home.
__________________

2017 Outback 276UBH
2010 F150 Lariat
Skins44 is offline   Reply With Quote
Old 07-22-2019, 07:05 AM   #2
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
It sounds to me like you had a brown-out at the camp power pedestal. Do you have an EMS installed in the trailer (or a portable one attached to the pedestal)? If not, you should get one before the results are far less favorable.

Also, if you were plugged in to the shore power when you checked the battery level, what you were actually checking was the voltage coming from the battery charger (on the converter), and not the battery. If taking the trailer off of shore power and your batteries show low, then they are not charging properly. Perhaps they need to be checked as well.

Good luck.
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 07-22-2019, 07:10 AM   #3
Skins44
Member
 
Join Date: Dec 2018
Location: Maryland
Posts: 87
Thanks Mark. I use this at the electrical pedastal:
Camco Heavy Duty Dogbone RV Circuit Analyzer With Power Grip Handles, Integrated Surge Protection and Fault Indication (125V 30M/30F Amp) (55312)

would a brown out trip my AC breaker?
__________________

2017 Outback 276UBH
2010 F150 Lariat
Skins44 is offline   Reply With Quote
Old 07-22-2019, 07:21 AM   #4
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
That's a surge protector and not an EMS. EMSs do far more to protect your RV. You should look into them. There are many threads on this forum which compare the two.

My favorite is the Progressive Industries EMS HW30C (hard-wired unit). It's not that expensive and not that difficult for a DIY'er to install.

As for the breaker, I'm not quite sure. I think when the volts goes down, all kinds of bad things can happen - some quite destructive. Perhaps others will have a better answer for that one.

Good luck.
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 07-22-2019, 07:29 AM   #5
wiredgeorge
Senior Member
 
wiredgeorge's Avatar
 
Join Date: Nov 2017
Location: Mico, TX
Posts: 7,447
I think your Camco gizmo might be good for catching voltage spikes but doesn't seem to be the correct device to protect from low voltage situation at the pole. Many use a Progressive EMS-PT30X which would actually turn off the power if it is low enough to put your electronics in danger and conversely will do the same if it is too high and it has, of course, a surge protect function. THere is also a similar Progressive unit that can be wired inside the camper near the converter and the power cord goes into this unit and then out to the converter. This is a good set up as well especially if you don't trust your neighbors at the camp ground you are staying at as Progressive EMS units tend to be popular items among camping enthusiasts. It is possible to use a bicycle lock or similar on your outdoor unit as it comes with a metal collar for running a cable through for this reason.

Would also like to point out that your breakers can trip is they get too hot. They are sometimes arrayed in your box in such a way as two higher draw breakers are adjacent (dumb but it happens). You can buy replacements to get the high draw way from its neighbor high draw breaker. The heat can also be mitigated by use of an additional fan. I used a 117V computer muffin fan I cobbled into the front panel of my voltage converter and it helps with the heat. It runs all the time when we are on shore power (117V).
__________________
wiredgeorge Mico TX
2006 F350 CC 4WD 6.0L
2002 Keystone Cougar 278
2006 GL1800 Roadsmith Trike
wiredgeorge is offline   Reply With Quote
Old 07-22-2019, 08:22 AM   #6
Jarhead4life
Junior Member
 
Join Date: Feb 2019
Location: Montrose
Posts: 3
Sounds like a couple things to check. Battery conditions? Are they holding a charge?,weak cells, 3 years old or older etc. Also what type of converter do you have? Perhaps its not floating or trickle charging your batteries perhaps its boiling them and over charging them constantly? Good luck.
Jarhead4life is offline   Reply With Quote
Old 07-22-2019, 08:24 AM   #7
Jarhead4life
Junior Member
 
Join Date: Feb 2019
Location: Montrose
Posts: 3
Quote:
Originally Posted by Skins44 View Post
camping in 100+ heat in Delaware over the weekend. Around 6pm Saturday, things got quiet in the camper (2017 276UBH - 30 amp). AC went out and lights got dim. AC breaker tripped. Pretty sure i know why...2 TV's on and streaming (kids relaxing watching TV after 7 hours on the beach), AC pumping, fridge on, iphone and tablet charging, lights on (so assuming converter was pulling amps) and 2 strands of palm tree lights (not LED) plugged in outside. Add all that up and pretty sure i was well over 30 amps.

reset the AC breaker, unplugged some things and was good. AC was back on.

My question, why did the lights dim if they run off of the battery? Also, checked my battery level on the panel and it was 1 bar (very low). Gradually, lights went back to normal and battery level showed full.

I wont get into the campground power going out at 3am! let's just say i got an early jump on the trip home.
Sounds like a couple things to check. Battery conditions? Are they holding a charge?,weak cells, 3 years old or older etc. Also what type of converter do you have? Perhaps its not floating or trickle charging your batteries perhaps its boiling them and over charging them constantly? Good luck
Jarhead4life is offline   Reply With Quote
Old 07-22-2019, 08:27 AM   #8
sourdough
Site Team
 
Join Date: Feb 2014
Location: W. Texas
Posts: 17,669
You said the AC went out (breaker tripped - you didn't say whether ped or main inside) and the lights got "dim". At that point you were running on batteries. The first thing I would ask is what condition are they in? They would be the first thing I would suspect. The trailer is only 3 years old; the converter will probably be fine BUT the batteries may be toast, especially if there has been a lack of maintenance. When you replace them, replace them both to prevent a recurrence of the same situation.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
sourdough is offline   Reply With Quote
Old 07-22-2019, 10:09 AM   #9
Skins44
Member
 
Join Date: Dec 2018
Location: Maryland
Posts: 87
Sourdough - only one battery and it is brand new as of this year (March 2019). The breaker that tripped was not the main. It was the AC.

Jarhead - not sure type of converter

Thanks for the replies
__________________

2017 Outback 276UBH
2010 F150 Lariat
Skins44 is offline   Reply With Quote
Old 07-22-2019, 10:17 AM   #10
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
Don't assume that because the battery is new, that it can't be a problem. Your comment about the battery level indicator showing a low level indicates a problem. Don't ignore it.
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 07-22-2019, 10:18 AM   #11
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,979
Quote:
Originally Posted by Skins44 View Post
Thanks Mark. I use this at the electrical pedastal:
Camco Heavy Duty Dogbone RV Circuit Analyzer With Power Grip Handles, Integrated Surge Protection and Fault Indication (125V 30M/30F Amp) (55312)

would a brown out trip my AC breaker?
That "surge protector" (NOT EMS) won't protect your electrical system from low voltage, high amperage, lost ground, reverse wiring or "brown out" conditions.... It's got lights that will illuminate to warn you of some of the above problems, but it won't disconnect your trailer to protect your equipment.

So, while the light is "burning brightly" your air conditioner can also be "burning brightly" and unless you happen to walk outside and see the red light and turn off power, that CAMCO surge protector" will happily keep supplying power to your trailer until it either catches fire or a circuit breaker (inside on your power center or outside on the campground pole) opens to stop the damage.....

In other words, it'll burn down your camper before it protects it from anything but a power surge.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is offline   Reply With Quote
Old 07-22-2019, 10:28 AM   #12
travelin texans
Senior Member
 
travelin texans's Avatar
 
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
Quote:
Originally Posted by Skins44 View Post
Sourdough - only one battery and it is brand new as of this year (March 2019). The breaker that tripped was not the main. It was the AC.

Jarhead - not sure type of converter

Thanks for the replies
Is the "new" battery a true deep cycle RV battery?
If there are CCA/CA, cranking amps, listed on the top, NO it's not.
The only numbers you'll want posted will be "Ah", the bigger the number the better.
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
travelin texans is offline   Reply With Quote
Old 07-22-2019, 10:42 AM   #13
Skins44
Member
 
Join Date: Dec 2018
Location: Maryland
Posts: 87
understood, but within minutes after the AC going off and light dim, it was showing back at full charge. I will test the battery when i get home this evening.
__________________

2017 Outback 276UBH
2010 F150 Lariat
Skins44 is offline   Reply With Quote
Old 07-22-2019, 10:58 AM   #14
MarkEHansen
Senior Member
 
MarkEHansen's Avatar
 
Join Date: Oct 2018
Location: Sacramento
Posts: 1,005
Quote:
Originally Posted by Skins44 View Post
understood, but within minutes after the AC going off and light dim, it was showing back at full charge. I will test the battery when i get home this evening.
If you were checking while connected to shore power, then you weren't looking at the state of charge on the battery, you were looking at the voltage being applied to the battery from the on-board charger.
__________________
2022 Cedar Creek Champagne 38EL - "Big Bertha"
2019 GMC Sierra 3500 Denali HD 6.6L Duramax TD, CC, 4WD, DRW - "Mr. Beefy"
MarkEHansen is offline   Reply With Quote
Old 07-22-2019, 01:26 PM   #15
wiredgeorge
Senior Member
 
wiredgeorge's Avatar
 
Join Date: Nov 2017
Location: Mico, TX
Posts: 7,447
I think someone who knows more than me tried to figure out if the 30A breaker at the pole box went off or the 20A breaker in your converter for the A/C. Or the 30A main for that matter in the converter. It makes a HUGE difference as far as trouble shooting. I am not saying you should load test your battery but I will say that if you are plugged into shore power, it gets converted in the converter box and if the shore power voltage dips, this may effect the DC voltage supplied to charge your battery. And for the second time, the Camco gizmo offers ZERO protection from power dips at the pole box.
__________________
wiredgeorge Mico TX
2006 F350 CC 4WD 6.0L
2002 Keystone Cougar 278
2006 GL1800 Roadsmith Trike
wiredgeorge is offline   Reply With Quote
Old 07-22-2019, 02:02 PM   #16
sourdough
Site Team
 
Join Date: Feb 2014
Location: W. Texas
Posts: 17,669
Quote:
Originally Posted by Skins44 View Post
Sourdough - only one battery and it is brand new as of this year (March 2019). The breaker that tripped was not the main. It was the AC.

Jarhead - not sure type of converter

Thanks for the replies

Sorry. From the original post it sounded like you had flipped one or the other of your main breakers.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
sourdough is offline   Reply With Quote
Old 07-28-2019, 11:59 AM   #17
BadmanRick
Senior Member
 
BadmanRick's Avatar
 
Join Date: Jul 2011
Location: Lehigh Acres
Posts: 176
We have been camping in Florida and the temperature is in the 90 s when at the campground running on the pedestal 30 amp breaker I have had it trip many times along with the 20 amp onboard A/C breaker trip. I have a 30amp surge guard portable power protector which shuts off as soon as it detect any power fluctuations.
Don’t get the cheap surge protector get a good powerful power protector.
__________________
Rick and Sandy
2017 Toyota Platinum Tundra 4X4
2011 Bullet Premier 19FBPR
BadmanRick is offline   Reply With Quote
Old 07-28-2019, 12:38 PM   #18
larryflew
Senior Member
 
larryflew's Avatar
 
Join Date: Feb 2014
Location: Young America MN
Posts: 372
As your voltage drops your amperage on running items goes up. IE if your A/C draws 20 amps at 120 volts it's nearer to 25 amps at 100 volts. Considering what was running you also were not likely charging the battery as the voltage to the converter also drops, so with your low battery charge when the converter voltage dropped the amperage there also went up causing your lights to dim since they were not getting all of the 12+ volts they need.
__________________
39 foot Forest River Vengeance dragged by GMC 3500.
larryflew is offline   Reply With Quote
Old 07-28-2019, 08:50 PM   #19
bobbecky
Senior Member
 
bobbecky's Avatar
 
Join Date: Jul 2013
Location: Box Elder
Posts: 2,907
Along with what has been stated, when on a 30 amp connection, you should have your water heater and fridge on propane only, as those two appliances draw quite a bit of load, and load management with a 30 amp system is the name of the game. If you do get an EMS protective device, get one with a remote display, and you will know exactly how much load you are drawing, plus all the benefits the EMS provides.
__________________
Bob & Becky
2012 3402 Montana
2012 Chevy 2500HD D/A CC
bobbecky is offline   Reply With Quote
Old 07-29-2019, 07:08 PM   #20
johnlewis
Senior Member
 
Join Date: Oct 2016
Location: Green Valley
Posts: 124
[QUOTE=MarkEHansen;350983]That's a surge protector and not an EMS. EMSs do far more to protect your RV. You should look into them. There are many threads on this forum which compare the two.

My favorite is the Progressive Industries EMS HW30C (hard-wired unit). It's not that expensive and not that difficult for a DIY'er to install.

As for the breaker, I'm not quite sure. I think when the volts goes down, all kinds of bad things can happen - some quite destructive. Perhaps others will have a better answer for that one.

Good luck.[/QUOTE

You are using power {watts}. Watts = volts x amps. When the voltage goes down, the amperage goes up.
johnlewis is offline   Reply With Quote
Reply

Tags
power

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 09:20 AM.