Ok I am not a electrician. So this is why I am asking. A lot of treads have been saying that my 5th wheel should be hooked to a expensive surge protector. My question is why. The camp grounds that I have been to all have a breaker in their box that I hook my shore line to and I also have a main breaker in my 5th wheel. So I see that I am double protected. How am I wrong. Please explain . That is what the breakers do is protect the wiring.

Thanks to all who respond. Just trying to figure this out.
__________________
Beavercreek Ohio
2020 Cougar Half Ton 27 SGS
2009 Silverado 2500 HD
Ext cab short bed
6 liter gas..3:73
Travler is offline   Reply With Quote
Old 06-25-2018, 01:57 PM   #2
Frank G
Senior Member
 
Frank G's Avatar
 
Join Date: Feb 2017
Location: Dade City
Posts: 1,039
You will get a lot of answers and explanations here, some from well educated sources and some not so qualified. Might I suggest you do some research on line from reliable sources such as the manufactures of the devices and pay attention to the features of the devices they manufacture. Progressive Industries is a good start. Short answer to your question, the park pedestal and the circuit breakers in your unit give very limited protection mostly over current protection.
__________________
2021 Surveyor Legend 19rble
2017 Laredo 325RL
Travelers Rest Resort
www.travelersrestresort.com
Frank G is offline   Reply With Quote
Old 06-25-2018, 02:06 PM   #3
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
Breakers WILL NOT protect you from a power surge. They are there to protect you from something WITHIN your RV from drawing too much amperage and causing a fire or other damage.
A power surge from an outside source is an "over voltage" situation, as opposed to Amperage, and can result in major damage to anything connected to it.
A surge protector will (help) guard against this and that is why it is recommended.
A complete EMS, or electrical management system will do that, as well as tell you if the power supply you are connected to is properly wired and grounded and if the supplied voltage is within proper specification. All things that a common circuit breaker cannot and will not do.
Hope that helps.


Added: I will also say that instead of considering a good EMS system an "expensive" addition to your RV, you should consider it as being a really cheap insurance policy on all of your on-board electrical systems and appliances that you need to only pay for once.
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-25-2018, 02:21 PM   #4
sourdough
Site Team
 
Join Date: Feb 2014
Location: W. Texas
Posts: 17,600
"Breakers" perform a very minimal task. Example: you have breakers in your trailer. If you plug a toaster and some other high draw components on that circuit and pull more than that allocated breaker (say 15A) it will trip. At the ped you will have a 30 or 50A plug. If all the appliances you have on do not throw a breaker in the trailer BUT all of it combined is over the rating of the breaker in the ped it will blow. They are protecting you from pulling too much current and burning something up.....end of the breaker story. They do nothing for a power surge.

A cheap "surge protector" for the trailer, either at the ped or inline, will protect you from a power surge....so, if you have one of those and the breakers your breakers will trip when the draw is too high and the EMS will trip if you have a sudden surge - that's it.

The EMS does many other things. It provides the protections of both of the above along with reverse polarity, low voltage, high voltage, loss of ground etc.

The things that generally get a trailer, or the owner, isn't the surge or pulling too much "juice". It's the reversed polarity, lack of ground, brown outs etc. We just had one poster that fried their ped connection due to too small of an extension cord....the breaker didn't take care of it but the EMS would have.

The EMS is worth far more than you pay for it. One event when it works can save you thousands of dollars, or, your life. It analyzes the power you are getting (many rv parks have really shoddy power distribution) and won't let your trailer get hurt. The list goes on and on. It has saved my bacon several times and there are others on here that will attest to the same. I believe it is the general consensus that they are a must have for the reasons above.
__________________
Danny and Susan, wife of 56 years
2019 Ram 3500 Laramie CC SWB SB 6.4 4x4 4.10
2020 Montana High Country 331RL
sourdough is offline   Reply With Quote
Old 06-25-2018, 02:30 PM   #5
Javi
Senior Member
 
Join Date: Aug 2012
Location: Waco, Tx
Posts: 5,456
Quote:
Originally Posted by sourdough View Post
"Breakers" perform a very minimal task. Example: you have breakers in your trailer. If you plug a toaster and some other high draw components on that circuit and pull more than that allocated breaker (say 15A) it will trip. At the ped you will have a 30 or 50A plug. If all the appliances you have on do not throw a breaker in the trailer BUT all of it combined is over the rating of the breaker in the ped it will blow. They are protecting you from pulling too much current and burning something up.....end of the breaker story. They do nothing for a power surge.

A cheap "surge protector" for the trailer, either at the ped or inline, will protect you from a power surge....so, if you have one of those and the breakers your breakers will trip when the draw is too high and the EMS will trip if you have a sudden surge - that's it.

The EMS does many other things. It provides the protections of both of the above along with reverse polarity, low voltage, high voltage, loss of ground etc.

The things that generally get a trailer, or the owner, isn't the surge or pulling too much "juice". It's the reversed polarity, lack of ground, brown outs etc. We just had one poster that fried their ped connection due to too small of an extension cord....the breaker didn't take care of it but the EMS would have.

The EMS is worth far more than you pay for it. One event when it works can save you thousands of dollars, or, your life. It analyzes the power you are getting (many rv parks have really shoddy power distribution) and won't let your trailer get hurt. The list goes on and on. It has saved my bacon several times and there are others on here that will attest to the same. I believe it is the general consensus that they are a must have for the reasons above.
Yep... EMS, Slide Awnings and Auto Level are must haves..
__________________
2015 Ford F350 DRW 6.7 Diesel XL
2020 Avalanche 313 RS
Javi is online now   Reply With Quote
Old 06-25-2018, 02:44 PM   #6
SummitPond
Senior Member
 
SummitPond's Avatar
 
Join Date: Jan 2015
Location: Northeast Florida/Southeast Maine
Posts: 784
Quote:
Originally Posted by sourdough View Post
... It has saved my bacon several times ...
We've had ours (Progressive Industry hardwired) a little over a year; already it has saved us from a reverse polarity and several undervoltage situations.

Like said above ... cheap insurance.
__________________

Now: 2019 Winnebago 2500FL w/e2 WDH;Sold: 2015 Bullet Premier 19FBPR (shown)
2012 Ford F-250 Lariat Super Duty Crew Cab (gas 6.2 L, 3.73 gear ratio 2WD, 172" WB)
SummitPond is offline   Reply With Quote
Old 06-25-2018, 02:57 PM   #7
Laredo Tugger
Senior Member
 
Join Date: Apr 2018
Location: South US
Posts: 712
Javi's quote: Yep... EMS, Slide Awnings and Auto Level are must haves.
I would mark that "true" on the test.
I do not understand why all the major RV manufactures do not include EMS systems in the build. Slide covers (not sure here,might be aftermarket only) and auto level yes, but EMS no?
I don't think the $400 price is going to make the difference in a sale. And much easier installed at the factory.
Just my thoughts.
RMc
Laredo Tugger is offline   Reply With Quote
Old 06-25-2018, 03:18 PM   #8
travelin texans
Senior Member
 
travelin texans's Avatar
 
Join Date: Nov 2017
Location: Picacho, Az
Posts: 6,809
Most rv parks/campgrounds utilities are showing their age, add to that most are maintained by folks that aren't or never were electricians & rvs are getting more & more high tech with lots of electronic equipment, so the surge protector/ems is very cheap insurance compared to a fridge, several tv's, water heater, as well as what you've pulled into the outlets.
I agree the surge protector/EMS should be mandatory equipment installed at the factory, but it would be like most items they add, the cheapest crap on the market, so maybe best we add our own.
Also mine has saved us more than once & on one occasion fried the protector.
Simple answer, if you don't have one, get one asap!
__________________
Full-timed 10+ years
Sold '13 Redwood FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
travelin texans is offline   Reply With Quote
Old 06-25-2018, 03:50 PM   #9
cynnich
Junior Member
 
Join Date: Apr 2018
Location: Vernon
Posts: 20
We have the
Progressive Industries EMS-PT50X Portable RV Surge Protector - 50 Amp. Purchased from Amazon.
cynnich is offline   Reply With Quote
Old 06-25-2018, 04:10 PM   #10
Plumbtrician
Member
 
Join Date: May 2018
Location: SC
Posts: 34
I’ve seen first hand what “dirty voltage” can do to appliances, tv’s, components, etc. in homes. Not to mention the safety aspect.

Like most have already said above, the loss of a ground (among other things) at your shore power pedestal could be very hazardous, even life threatening. An EMS will shut you down if this, or any other “bad thing” happens at the ped.

A cheaper surge protector will give you a nice pretty light indicating a problem, but if you see it, then it’s too late. Damage may have already been caused.

I installed a hardwired unit inside the trailer to eliminate the possibility of theft. It was one of the first mods I did. Also has a lifetime warranty (Progressive Industries)

I’d rather have it and not need it, than need it and not have it.
Plumbtrician is offline   Reply With Quote
Old 06-25-2018, 05:14 PM   #11
Hookoil
Junior Member
 
Join Date: May 2018
Location: Bethlehem
Posts: 18
I have been looking for one and just ordered the 50 amp hardwired progressive industries from amazon. My 30 amp on the travel trailer saved me twice from pedistals mis wired
__________________
2016 GMC Denali 3500 duramax
2018 Cougar 369BHS
Hookoil is offline   Reply With Quote
Old 06-28-2018, 02:34 AM   #12
anuccite
Member
 
Join Date: Jan 2018
Location: Richlands
Posts: 44
In Nashville a couple weeks ago... During a lightning storm, DW actually complained when the TV shut off twice when my Progressive Hard wire noticed the over voltage and shut everything off....


When I explained that she will be glad when the TV actually comes back on.... She still complained.... But that's why i love her....
__________________
2018 Premier 26RBPR being towed by a 2015 Ram 1500 LongHorn CC, Eco-diesel.

anuccite is offline   Reply With Quote
Old 06-28-2018, 06:43 AM   #13
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,714
An EMS (electrical management system) does far more than just surge protection. It will disconnect the power source for various faults as mentioned including over or under voltage, improper wiring, missing neutral and ground. One very important aspect not mentioned yet is the time delay. Have you ever seen the "lights flicker" during a wind storm or lightning event? Typically it's caused by the power company overvoltage protection. When that happens it can burn up the air conditioner compressor and wipe out sensitive electronics such as refrigerator control boards. The EMS will have a time delay built in so when the power is interrupted it will take 30 seconds to a minute before the EMS will reset and allow the power back on saving these appliances.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 06-28-2018, 06:55 AM   #14
Triple GGG
Senior Member
 
Join Date: May 2018
Location: Lenoir City
Posts: 108
I have the Progressive portable EMS 50amp. The campground at the lake where we have a permanent setup has constant low voltage issues (106 to 107) sometimes to where we can't run one ac let alone both. I just got the Hughes Autoformer RV220-50SP. My question is can I run the Progressive after the Autoformer or is it necessary since I have the Autoformer. Have used progressive for years but have heard good thing s about the Autoformer as well.
__________________
Greg, Gina and Ginger the rescue dog
2014 Keystone Sprinter 302RLS
Triple GGG is offline   Reply With Quote
Old 06-28-2018, 07:12 AM   #15
LFord
Member
 
Join Date: Mar 2017
Location: Warne
Posts: 61
Quote:
Originally Posted by Harleydodge View Post
Breakers WILL NOT protect you from a power surge.

***

A surge protector will (help) guard against this and that is why it is recommended.
***

Added: I will also say that instead of considering a good EMS system an "expensive" addition to your RV, you should consider it as being a really cheap insurance policy on all of your on-board electrical systems and appliances that you need to only pay for once.

I agree, and "bit the bullet" on buying the "expensive," full EMS system from Progressive (30 amp PTC model), which I figured was much cheaper than replacing all the electronic control boards in the TT's applicances. Plus, it let's me know if there's something "funky" with the RV park's AC supply BEFORE I plug the TT into it! Some of the older RV parks especially can have wildly fluctuating voltages from what I have read, and having spent many years in the Amateur Radio hobby, I know that can be "quick death" to sensitive electronics.
__________________
Larry J Ford (SWNC)
2016 Passport Ultra Lite Express 199ML
2013 Ford F-150 XLT Supercab, 3.5L V6 ecoBoost (turbo), 3.15 RAR, 8600 lbs. Tow Capacity, Equalizer WDH
LFord is offline   Reply With Quote
Old 06-28-2018, 08:56 AM   #16
HANGAR
Member
 
HANGAR's Avatar
 
Join Date: Oct 2015
Location: So Cal
Posts: 50
Quote:
Originally Posted by Triple GGG View Post
I have the Progressive portable EMS 50amp. The campground at the lake where we have a permanent setup has constant low voltage issues (106 to 107) sometimes to where we can't run one ac let alone both. I just got the Hughes Autoformer RV220-50SP. My question is can I run the Progressive after the Autoformer or is it necessary since I have the Autoformer. Have used progressive for years but have heard good thing s about the Autoformer as well.
The Hughes unit has 4,800 Joules of protection. The Progressive portable units vary, but they're around 3,600 Joules. It wouldn't hurt anything to use the Progressive unit after the autoformer, but it may not be necessary.
__________________
2006 Raptor 3612DS
2007 Ford F350 (Diesel, SRW, FX4, Crew Cab, 8' bed)
Super Stroke / Power Duty
HANGAR is offline   Reply With Quote
Old 06-28-2018, 12:23 PM   #17
flybouy
Site Team
 
Join Date: Oct 2011
Location: Joppa, MD
Posts: 11,714
Triple GGG I have an older 30 amp Autoformer that I use upstream of my EMS with no issues. Have been using in that form for years.
__________________
Marshall
2012 Laredo 303 TG
2010 F250 LT Super Cab, long bed, 4X4, 6.4 Turbo Diesel
flybouy is offline   Reply With Quote
Old 06-28-2018, 02:36 PM   #18
Triple GGG
Senior Member
 
Join Date: May 2018
Location: Lenoir City
Posts: 108
Thanks for the input. I ran up and setup the Autoformer with the Progressive EMS downstream. Everything worked fantastic. I had 107 volts and after installing both ACs ran just fine. I even fired up the microwave while they were running. I'm very happy. With all these storms rolling through the Knoxville area I may need 4 surge protectors. Lol.
__________________
Greg, Gina and Ginger the rescue dog
2014 Keystone Sprinter 302RLS
Triple GGG is offline   Reply With Quote
Old 07-01-2018, 11:09 AM   #19
sdetweil
Member
 
Join Date: Sep 2013
Location: Pflugerville
Posts: 65
Quote:
Originally Posted by Plumbtrician View Post
...

I installed a hardwired unit inside the trailer to eliminate the possibility of theft. It was one of the first mods I did. Also has a lifetime warranty (Progressive Industries)

I’d rather have it and not need it, than need it and not have it.
i added a generator (and transfer switch) to my 5th wheel and added the hardwired progressive EMS 50amp unit at the same time. didn't like the price, but have seen the results of not having one.
__________________
2018 Ford F350 DRW Longbed King Ranch
2013 Alpine 3720FB
sdetweil is offline   Reply With Quote
Old 07-01-2018, 11:27 AM   #20
bradufault
Junior Member
 
bradufault's Avatar
 
Join Date: Oct 2014
Location: Nipomo
Posts: 9
We were camping in a Florida and I did not think I need to put mine on. That night we had thunder and lighting storm. To top it off the was also a power surge,
Long story short, did about $1800 damages to my 5th and nothing really work that well afterwards.
I now put my on no matter what.
bradufault is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 06:03 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.