Old 06-11-2017, 05:23 PM   #1
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
possible grounding issue?

While out walking around our TH in bare feet this evening, I noticed that while touching the metal hinge on the rear door, there was a faint voltage present (I actually could feel a very slight electrical current flowing through me to ground) This was very slight and felt like only a few volts at low amperage.
Just wondering if this was normal and if anyone else has ever noticed this?
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-11-2017, 05:44 PM   #2
ctbruce
Site Team | Emeritus
 
ctbruce's Avatar
 
Join Date: Dec 2015
Location: Kansas City
Posts: 3,878
That would not be normal. Are you plugged in to shore power?

Sent from my SAMSUNG-SM-N910A using Tapatalk
__________________

Chip Bruce, RPh
Kansas City, MO
2016 Impact 312
2017 Silverado 3500HD SRW
ctbruce is offline   Reply With Quote
Old 06-11-2017, 05:48 PM   #3
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
Yes...plugged into 15amp house plug via adaptors.
Unit is currently in our yard at home.
I will try unplugging and see if it's still an issue.
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-11-2017, 05:59 PM   #4
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
Update....just went out and checked, and I could not replicate the situation. I will have to investigate further.
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-11-2017, 06:05 PM   #5
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,841
It sounds like your physical ground (the bare copper wire) is not connected "somewhere"... Possibly it vibrated loose in the trailer or you could have a loose connection "almost anywhere"... I'd be very cautious until you find the cause. My guess is the 15 amp circuit/plug at the house, but it could be anywhere in the entire circuit.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is online now   Reply With Quote
Old 06-20-2017, 06:03 PM   #6
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
Quote:
Originally Posted by JRTJH View Post
It sounds like your physical ground (the bare copper wire) is not connected "somewhere"... Possibly it vibrated loose in the trailer or you could have a loose connection "almost anywhere"... I'd be very cautious until you find the cause. My guess is the 15 amp circuit/plug at the house, but it could be anywhere in the entire circuit.
Thanks for the reply.
It got me thinking though.
How is a "physical ground" established if you happen to be dry camping and running off the Genny? I never thought about having to connect a ground rod of some sort.
This is not my current case (no pun intended ) but it just got me wondering.
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-20-2017, 06:51 PM   #7
JRTJH
Site Team
 
JRTJH's Avatar
 
Join Date: Mar 2011
Location: Gaylord
Posts: 26,841
From what I understand, RVIA and most electrical codes stipulate that there can only be "one neutral/ground tie" in an electrical circuit. Hopefully there's an electrician that's more familiar with the codes that can expand on that.

Anyway, In trailers and generators, the physical ground and the neutral are not together. In homes they are tied together. Your trailer "can't be tied" because as soon as you plug it into the house or a campground pedestal, it would be "double tied" which is a violation of code. It's the same "theory" that is used with "double insulated" power tools (plastic case and separate connections for the neutral) which is why they no longer have a 3-prong power cord.

If your physical ground in the trailer is loose, corroded or otherwise not secure, you're relying only on your neutral to provide a return path for the 120 VAC wiring. If anything happens to interrupt the neutral half of the system, there's no "backup" to protect you against shock. When using a generator, if you have a "circuit protection device" on your trailer power cord, it will not allow power to pass to the trailer unless you use a "neutral/ground tie" at the generator. That "neutral/ground tie" physically connects the generator ground to the neutral bus. By doing that, you "create the same environment" as in your home wiring.

There's a lot of information about the differences in wiring and how they interact with each other in RV power. Some internet searching will provide you with more information than you'll ever want to read.

Suffice to say, there was "something" not working correctly if you got a "tingle" when touching the trailer while standing in damp grass.... Next time, it may be raining, you standing in wet sand with the trailer connected to a 50 amp campground power pedestal. That's not a good way to start (or end) a weekend camping trip.
__________________
John



2015 F250 6.7l 4x4
2014 Cougar X Lite 27RKS
JRTJH is online now   Reply With Quote
Old 06-20-2017, 07:57 PM   #8
Outback 325BH
Gone Traveling
 
Join Date: May 2016
Location: Highland, IL
Posts: 512
Quote:
Originally Posted by JRTJH View Post
From what I understand, RVIA and most electrical codes stipulate that there can only be "one neutral/ground tie" in an electrical circuit. Hopefully there's an electrician that's more familiar with the codes that can expand on that.



The bonding of neutral and ground are allowed only once in a system because if there was a second (or more) bonding of the neutral and ground downstream, two things would result:
A parallel path would be created that would allow current to flow on the ground wire. In normal operations (no faults), no current flows on the ground. If more than one bond existed, the ground between the bondings would essentially be a second neutral and have current flowing on it. This is a safety problem and renders the purpose of the ground useless.
In addition, with current flowing on both the ground and neutral, it is possible to overload the ground wire since the ground does not have to be the same size as the neutral over a certain size. Current doesn't split across the two based on conductor size.

This is why it is critical to NOT bond in a house sub panel.

The main panel in your camper is just like a sub panel in your home (if you have one). All neutral and ground wires are isolated; the neutral/ground bonding occurs upstream-- probably in the pedestal.

If you look inside your main panel in your home, the neutral and ground are bonded there. That is why the neutrals and grounds are scattered and connected to the same buss... it doesn't matter. (Sometimes bonding is done in the meter and the main panel is kept not bonded. Less common though.)

The most technically correct way to use a generator would be to bond the neutral and ground in the genny, then ground the genny to a ground rod. Since that almost never happens, I think it is more acceptable to have the neutral and ground not bonded since the generator is not grounded. Of course we all know the floating ground issue with the EMS.



Sent from my iPhone using Tapatalk
Outback 325BH is offline   Reply With Quote
Old 06-21-2017, 02:06 AM   #9
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
Yes Thanks for both of your replies. It does seem the InterWeb is full of theories and conflicts as far as the "right" way to do it.
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-21-2017, 03:07 AM   #10
ctbruce
Site Team | Emeritus
 
ctbruce's Avatar
 
Join Date: Dec 2015
Location: Kansas City
Posts: 3,878
Quote:
Originally Posted by Harleydodge View Post
Yes Thanks for both of your replies. It does seem the InterWeb is full of theories and conflicts as far as the "right" way to do it.
Like all things on the internet, I'd take some of them with a grain of salt and verify the resource. Due diligence is the battle cry.

Sent from my SAMSUNG-SM-N910A using Tapatalk
__________________

Chip Bruce, RPh
Kansas City, MO
2016 Impact 312
2017 Silverado 3500HD SRW
ctbruce is offline   Reply With Quote
Old 06-29-2017, 06:23 PM   #11
Harleydodge
Senior Member
 
Join Date: Jun 2017
Location: Kingston
Posts: 295
This issue has been resolved.
It was due to a disconnected ground wire in the receptacle I was plugged into in the Garage.

Thanks all for your input.
__________________

2013 Raptor 310ts Toy Hauler
2017 Dodge Ram 6.7l CTD DRW Laramie Longhorn
2008 FLHTC Harley.

Harleydodge is offline   Reply With Quote
Old 06-30-2017, 07:12 AM   #12
sourdough
Site Team
 
Join Date: Feb 2014
Location: W. Texas
Posts: 17,600
Quote:
Originally Posted by Harleydodge View Post
Yes Thanks for both of your replies. It does seem the InterWeb is full of theories and conflicts as far as the "right" way to do it.
I know the issue is resolved but just wanted to comment on the post above.

There really aren't any "theories" or conflicts any longer, as far as I know, on how electricity flows and the proper way to wire the various elements. There are established practices for them and not theories. There are many "arm chair" electricians that have their own ideas about stuff but not rooted in established practice. All of that to simply say to beware of random comments from folks on the internet. When dealing with electricity it could be a life or death choice. If in question, find the appropriate electrical code and go from there.....or get an electrician
sourdough is online now   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by the Keystone RV Company or any of its affiliates in any way. Keystone RV® is a registered trademark of the Keystone RV Company.


All times are GMT -8. The time now is 01:40 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2024, vBulletin Solutions, Inc.