Quote:
Originally Posted by bjstager View Post
We plugged into 50amp. Within 5 minutes the shore power breaker tripped. After that 50amp would always trip. We plugged into 30amp and found after that the trailer metal shocked you? Any ideas? We can not find the issue. Everything was running fine inside, but all the metal outside was “hot”.

Also we then plugged into our generator and the charge moved to the generator instead of trailer metal.
10/22/2019 Update: Issue has been found! They found the electrical cable was pinched in the frame from incorrect install at factory. So, all is being covered for all the repairs that need to be done. Since we traveled 2700 miles over 5 day with the pinch it finally broke through the line and caused the issue. This could have been much worse than the 120v shock, the line in the picture I was provided is messed up, thankfully no fires happened. Thanks for all the help!